dear all, in motor operation , motor is of 100 hp and
bimetal relay setting is 130 amp, if relay is getting
tripped on 120 amp balance current what can be the
reason? Relay is newly replaced. I dont know but is
there any frequency effect in thit case? Can frequency
variation affect bimetal relay operation?
Bimetallic relays are not very accurate.Ambient temp also
plays a role for setting as the relay acts at a certain
temp.Hence you have to compensate for ambient
temp.Frequency has no effect on the setting .
| Is This Answer Correct ? | 5 Yes | 0 No |
WHY IN AC DRIVES,INPUT PHASE CURRENT SHOW UNBALANCE?
what is the mho relay
please let me know , we have installed two separate motor for fire fighting system 1) 60 hp and 2) 15 hp the load is 74 AMPS and 20 AMPS then tell me the main power cable in Aluminum will be what thickness , the length is 225 mt from the main utility to fire pump house
What is the maxvoltage drop allowed at any healthy joint at full load ?
Why power factor should not be in leading (capacitive) mode of any load.
what is meant by power and distribution transformer ?
What are insulation classes? Tell examples of each of them.
10rm cable can got load ---- amp? Or Which Size Cable can take the load 100amp capacity SCR; breaker.
1 Answers B-Con Trade Associates,
Why does the rotor rotate?
1 Answers Machino Polymers, OPTCL,
how does high earth to neutral voltage affects electronic circuit?
oil cooled transformer
How do we calculate Blower drive Power (kw) If we have Volume m3 and Pressre (mmWC)
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)