Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is the SCAN time of a DCS/PLC? What is the typical
value for scan time of DCS and PLC?

Answers were Sorted based on User's Feedback



What is the SCAN time of a DCS/PLC? What is the typical value for scan time of DCS and PLC?..

Answer / vicki

scan time is the time taken by DCS/PLC to read inputs,
execute program and as per input/logic update outputs
accordingly. PLC scan time depends on no. of inputs,
outputs and program size(total memory used, heap size). so
it may be different for different program(PLC). less scan
time means faster PLC action. scan time is mostly in mili
seconds, from 2ms onwords.

Is This Answer Correct ?    78 Yes 3 No

What is the SCAN time of a DCS/PLC? What is the typical value for scan time of DCS and PLC?..

Answer / mohamed yousuf

scan time means the time required to read the
inputs,execute the program and generate the output this is
called scan time the scan time is usually in milli seconds
to nano seconds

Is This Answer Correct ?    38 Yes 3 No

What is the SCAN time of a DCS/PLC? What is the typical value for scan time of DCS and PLC?..

Answer / amit patel

SCAN time of DCS /PLC defines as execution of one cycle of
program (reads the inputs, executed whole program and
writes output)

Normaly DCS scan time are 200msec ,500msec,1 sec
PLC scan time are less than 100msec.

Is This Answer Correct ?    21 Yes 6 No

What is the SCAN time of a DCS/PLC? What is the typical value for scan time of DCS and PLC?..

Answer / purushotham

scan time , name it self indicates time required to scan the process of operation.
time taken to finish operation (reading inputs,logic(process) and execution (output) of results).

Is This Answer Correct ?    11 Yes 2 No

What is the SCAN time of a DCS/PLC? What is the typical value for scan time of DCS and PLC?..

Answer / hiteshhp

Scan time is the time required to scan the inputs,program written and display the output accordingly.

As scan time of PLC is smaller than that of DCS,we use PLCs for faster operations in Industries.
Normally,PLC are used for Safety Purpose,the switches in interlocks for tripping,etc

Is This Answer Correct ?    4 Yes 0 No

What is the SCAN time of a DCS/PLC? What is the typical value for scan time of DCS and PLC?..

Answer / sivabalan

PLC/DCS

Scan time is scan input and update input table, then perform logic and update logic table and finally update physical output devices. Taking time to execute above process is called.

Process

Scan input, Perform logic, Update output and finally perform house keeping task such as update the display.

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

which is type of thermocouple is used to measure 1000deg?

9 Answers  


Can all intrinsic safe transmitters are provided with inbuilt zener barriers? why

2 Answers  


What is the formula to know the error of weighfeeder after having drop test.

3 Answers  


In turbine what does term CDP, NI, NH, HSSOC means.

0 Answers   ADMA OPCO,


If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc signal. The transmitter is placed across an orifice plate which is sized to create 2500 mmH2o differential at 5000m3/Hr a) what is the flow rate when the transmitter signal is 13.0mA DC? b) what is the signal output of the transmitter when flow rate is 2500 m3/Hr ?

5 Answers  


How to calibrate and check thermal mass flow meter of Make thermal instrument company inc model 60?

1 Answers   Wood Group,


what is remote mount with MTA option? (In case of Dual Sensor Vortex Flowmeter,rosemount has written in its catalog drawings).

2 Answers  


wht is mean by dpt(differential pressure transmitter)

1 Answers  


What is meant by cold float of compressor shaft.

1 Answers   Sabic,


How to Calibrate Temperature Switch in field

0 Answers  


if i change range of flow transmitter in th field then does it need to change range in dcs?

3 Answers  


what are the use of belew gear in general ??

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)