how to adjust relay in smart positioner ?
Answer / ralu
Steam Service (Filling the water legs)
1. Ensure that the steam line is depressurized with no steam.
2. Check the transmitter for a dry zero of 4 mA with no water loss.
3. Attach hose connection valve to high side vent DVH. See Figure 3-3.
4. Attach a water supply to the hose connection. The water supply
should have a maximum psi of 100.
5. Open the high and low manifold valves MH and ML and equalizer
valve ME (MEH and MEL for 5-Valve Manifolds).
6. Ensure low side vent DVL is closed.
7. Open the hose connect valve for a minimum of 30 seconds.
Water will flow through both the high and low chambers and
into the pipe.
8. Close the high side manifold valve MH for 30 seconds to force water
to the ML side.
9. Re-open the MH valve.
10. Open low side vent DVL until no air is observed.
11. Close the low-side vent DVL.
12. Close the hose connect valve and remove hose.
13. Close both manifold high side valve MH and manifold low side valve
ML.
14. Check the transmitter zero by noting the output. If the signal reads
outside of the range 3.98 mA to 4.02 mA, air is probably still in the
system; repeat this procedure from step 2, and trim sensor if
necessary.
15. Open the manifold high side valve MH.
16. Close equalizer valve ME (for 5-Valve Manifolds first close valve
MEL, then close valve MEH).
17. Open the manifold low side valve ML. The system is now operational.
| Is This Answer Correct ? | 0 Yes | 3 No |
what is Micro-switch and where it is used......?
what is the relation between flow and pressure.for example relationship between level and pressure is p = phg like that i want ans for this question.and also how to calculate orifice sizing and flow transmitter. pls some one ans for this questions.
how pressure reduce through pressure control valve? suppose we have to reduce 20 kg pressure to 10 kg pressure , then what we do ? open the valve or close the valve , initially it is 20 % is upon ( for ur knowledge ).
WHAT IS THE Differance b/w on/off & pid control valve?
Why we use the double acting control valve in flow line?
For what reason would you possibly be compelled to make use of a Smith Predictor. Explain the idea behind the operation of this device.
what is dedband in instrumentation ?
what is control valve and how is work
Explain the difference between the types of input variables plc?
On LPG sphere tank we used LIT for level indication.High side port is connected to the bottom of the tank while low side port connected to the top. I would like to know how to fill the glycerin on its low side with two condensing pot installed,one from top and the other one for its drain line.Please I need your expertise...thanks
What is the main difference between Cavitation and Flashing?
We are used ABB 800xa 5.1.please tell me how to instrall this.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)