how to adjust relay in smart positioner ?
Answer / ralu
Steam Service (Filling the water legs)
1. Ensure that the steam line is depressurized with no steam.
2. Check the transmitter for a dry zero of 4 mA with no water loss.
3. Attach hose connection valve to high side vent DVH. See Figure 3-3.
4. Attach a water supply to the hose connection. The water supply
should have a maximum psi of 100.
5. Open the high and low manifold valves MH and ML and equalizer
valve ME (MEH and MEL for 5-Valve Manifolds).
6. Ensure low side vent DVL is closed.
7. Open the hose connect valve for a minimum of 30 seconds.
Water will flow through both the high and low chambers and
into the pipe.
8. Close the high side manifold valve MH for 30 seconds to force water
to the ML side.
9. Re-open the MH valve.
10. Open low side vent DVL until no air is observed.
11. Close the low-side vent DVL.
12. Close the hose connect valve and remove hose.
13. Close both manifold high side valve MH and manifold low side valve
ML.
14. Check the transmitter zero by noting the output. If the signal reads
outside of the range 3.98 mA to 4.02 mA, air is probably still in the
system; repeat this procedure from step 2, and trim sensor if
necessary.
15. Open the manifold high side valve MH.
16. Close equalizer valve ME (for 5-Valve Manifolds first close valve
MEL, then close valve MEH).
17. Open the manifold low side valve ML. The system is now operational.
| Is This Answer Correct ? | 0 Yes | 3 No |
What is cv of control valve
could someone explain for me what is 32-bit Floating Point ? Thanks
What is zero elevation and zero suppression?
why 1 to 5 vdc is used for output measurment
In split range control, we will control 2 outputs with time interval. Eg :(with 4-20 ma signal, for 4-12 ma we are operating one control instrument like valve & for 12-20ma we are operating other control instrumet (other valve). If we get a signal of 15ma to first instrument (Valve 1), what will happened to the first valve, and if we get signal above 20 ma to 2 valve what will happened ?
What are Sinking and Sourcing IO Cards
what is a good line as ic engineer as maintenance ,oc, project, calibration ,validation engineer?
How many interlocks at turbine? Plz explain briefly
0 Answers MRPL Mangalore Refinery and Petrochemicals Limited,
what is DCS?
Area classification, Equipments, Gas groups, temperature classification, Ingress protection, Fire Extinguishers.
How does a strain gauge measure pressure?
Meaning of the following a. IOP- Manimum; b. IOP- Maximu,;
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)