Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to adjust relay in smart positioner ?



how to adjust relay in smart positioner ?..

Answer / ralu

Steam Service (Filling the water legs)
1. Ensure that the steam line is depressurized with no steam.
2. Check the transmitter for a dry zero of 4 mA with no water loss.
3. Attach hose connection valve to high side vent DVH. See Figure 3-3.
4. Attach a water supply to the hose connection. The water supply
should have a maximum psi of 100.
5. Open the high and low manifold valves MH and ML and equalizer
valve ME (MEH and MEL for 5-Valve Manifolds).
6. Ensure low side vent DVL is closed.
7. Open the hose connect valve for a minimum of 30 seconds.
Water will flow through both the high and low chambers and
into the pipe.
8. Close the high side manifold valve MH for 30 seconds to force water
to the ML side.
9. Re-open the MH valve.
10. Open low side vent DVL until no air is observed.
11. Close the low-side vent DVL.
12. Close the hose connect valve and remove hose.
13. Close both manifold high side valve MH and manifold low side valve
ML.
14. Check the transmitter zero by noting the output. If the signal reads
outside of the range 3.98 mA to 4.02 mA, air is probably still in the
system; repeat this procedure from step 2, and trim sensor if
necessary.
15. Open the manifold high side valve MH.
16. Close equalizer valve ME (for 5-Valve Manifolds first close valve
MEL, then close valve MEH).
17. Open the manifold low side valve ML. The system is now operational.

Is This Answer Correct ?    0 Yes 3 No

Post New Answer

More Instrumentation Interview Questions

I am manjunath having exp in maintenance of chemical plants,know i want to do a design course INTOOLS,after doing design course can we get jobs in design field.sinve i dont have design exp..

0 Answers  


How to calibrate a temperature transmitter & how a Cold junction Compensation will be carried out?

2 Answers   QAFCO,


Why MUX JB's are using only Temperature Element in Fundation field bus?

0 Answers   Reliance Industries,


What is NAMUR standard and why its allways reletad with Sollenoid

2 Answers  


What is the use of keyphasor in turbine.

7 Answers   Hindustan Zinc, R&D,


What is the difference between pneumatic and electro pnematic positioner?

3 Answers   TCS,


How we are deciding while programming in pid controller , What we are using heating or cooling.

1 Answers  


HOW WE ARE DECIDING WHILE PROGRAMMING IN PID CONTROLLER THAT WE ARE USING HEATING OR COOLING???????

1 Answers   Eskom,


1.what is the effect of vapour presuure in orifice plate flow measurement 2.which is more effective 2 pressure sensors or one single differential pressure sensor in orifice plate measurement 3.how to design a v/i converter and i/v converter 4.how many type of thermocouple are there 5.how many leads are there in thermocouple measurement 6.how pressure sensors are connected in level measurement in differential pressure method 7.what is the output of capacitive pressure sensor (ac or dc),how its o/p is signal charactarized 8.what is the physical meaning of discharge coeeficient,why it is calculated,orifice plate what is its value,why it is less than 1,Q at upstream is equal to or not equal to Q at downstream of orifice plate why?what is vena contracta in orifice plate 9.why rotameter is called variable area flowmeter,it can measure flow even if area is not varying,why it is made tapered 10.design a 10 bit counter ,which counter you will prefer 11.how to remove self heating error in RTD 12.which is more sensitive pt100 or pt50 13.why thermocouple are connected in parallel 14.what is lead contact error in RTD,how to avoid 15.what is P,PI,PID,PD controller,why there is no ID controller 16.what is override,split range,sequential,ratio,feedforward,cascade controller 17.why we moved from SR to JK and then JK to master slave JK flipflop,give correct reason 18.how to measure level of a closed container which contains vapour and liquid,remember no vapour gas should be leaked,so ultrasonic and capacitive is not an option,design another method 19.how to design horse race counter including sensors and signal conditioning element 20.what is bevelling

0 Answers   BARC,


how can i calibrate a smart temperature transmitter used by druck 720 process calibrator?

0 Answers   Texas,


How can we calibrate the level interface for Fisher® FIELDVUE® DLC3000?if use water to calibrate and our liquid SG are 0.75 and 1 ,Displacer height=14" and How much should be set SG in trasmitter during calibrate,for URV and LRV how shold be set

1 Answers  


what is the diffrence between mmwc and kg/cm2 for pressure measurment when we are using mmwc and when kg/cm2 and why????? ?? what is the reason

19 Answers   Ecoboard, Jindal, Sepco,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)