how to adjust relay in smart positioner ?
Answer / ralu
Steam Service (Filling the water legs)
1. Ensure that the steam line is depressurized with no steam.
2. Check the transmitter for a dry zero of 4 mA with no water loss.
3. Attach hose connection valve to high side vent DVH. See Figure 3-3.
4. Attach a water supply to the hose connection. The water supply
should have a maximum psi of 100.
5. Open the high and low manifold valves MH and ML and equalizer
valve ME (MEH and MEL for 5-Valve Manifolds).
6. Ensure low side vent DVL is closed.
7. Open the hose connect valve for a minimum of 30 seconds.
Water will flow through both the high and low chambers and
into the pipe.
8. Close the high side manifold valve MH for 30 seconds to force water
to the ML side.
9. Re-open the MH valve.
10. Open low side vent DVL until no air is observed.
11. Close the low-side vent DVL.
12. Close the hose connect valve and remove hose.
13. Close both manifold high side valve MH and manifold low side valve
ML.
14. Check the transmitter zero by noting the output. If the signal reads
outside of the range 3.98 mA to 4.02 mA, air is probably still in the
system; repeat this procedure from step 2, and trim sensor if
necessary.
15. Open the manifold high side valve MH.
16. Close equalizer valve ME (for 5-Valve Manifolds first close valve
MEL, then close valve MEH).
17. Open the manifold low side valve ML. The system is now operational.
| Is This Answer Correct ? | 0 Yes | 3 No |
how many types of spped sensors n vibration sensors?their basic principle n connection?
ON RADAR INTERFACE LEVEL TRANSMITTER IF DI-ELECRIC IS WRONG WITH CONTINIUS PROCESS THAN HOW CAN INDENTIFY OR HOW CAN I PUT NEW DI-ELECTRIC VALUE?(ROSEMOUNT-TDR-3300-COXIAL PROBE TYPE)
What different types of problems do occur while doing the loop checking? and please explain in detail or mail me at kadam.aniket143@gmail.com
1 Answers Operational Energy Group, Process Control Technologies,
how to draw a flowchart for swapping two numbers using bit wise operators?
DCS marshilling Cabinet Power supply can be replace during plant running time?
what is the different between deflection type measurement and null type measurement in RTD?
Dear All can any one told me that VFD Make ABB Model ACS800-01 used for dual Source like 1.DC Source applied at terminal UDC+,UDC- 2. 3 phase 400AC,50Hz
Why rtd out put is ohm how create the ohm
WHAT IS SELF CLEAN ELCTRODE IN MAGNETIC FLOWMETER?? WHAT DO YOU MEAN BY THIS TERM??
if tx. dp increase or decrese what happend in the reading
i have one temperature TX in my loop check time once i was remove elament temp gose maximum then i am conect corectly but still now temp showing maximum what can i do this problem?
DEAR SIR/MADAM MY NAME IS ARKAPROVA BHATTACHARYYA.I AM A FRESHER INSTRUMENTATION ENGINEER.CAN YOU PLEASE SEND SOME QUESTION PAPERS OF GRADUATE ENGINEER TRAINEE EXAM OF DVC(DAMODAR VALLY CORPORATION).MY EMAIL IDs ARE arka_aec@rediffmail.com.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)