Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


i have one transformer 1000kva, 11/.433kv. we are using
200/5 amp. ct unit for measuring purpose, & one 800 amp.
V.C.B Unit for the same t/f operate, i wants to known the primary
current of T/F is only 53 amp. why we used 800 amp.
V.C.B ? & 200/5 amp. CT Unit.

Answers were Sorted based on User's Feedback



i have one transformer 1000kva, 11/.433kv. we are using 200/5 amp. ct unit for measuring purpose, ..

Answer / vinit patil

You are right, you should fight with your electricity board
regarding the HT Metering CT ratio. You should actually
required 100/5 ratio.
But while deasigning VCB it is always prfarable to go on
higher side because it can sustain the heavy short circuit
current. One thing should be noticed that the protection
CTs should be as per the Primary current of the ransformer.

Is This Answer Correct ?    5 Yes 2 No

i have one transformer 1000kva, 11/.433kv. we are using 200/5 amp. ct unit for measuring purpose, ..

Answer / a k kataria

Well given the rating of transformer as 1000 kva, CT ratio
should have been 100/5. As far as VCB current rating is
concernd,these are generally made for universal
applications and are generally 630 Amps onwards 'cause in
the eventuility of fault ,heavy currents are to be taken
care of.More over increase in the rated current capacity of
breaker adds little to the cost compared to other
components of the breaker.There fore capacity of VCB is OK.

Is This Answer Correct ?    2 Yes 1 No

i have one transformer 1000kva, 11/.433kv. we are using 200/5 amp. ct unit for measuring purpose, ..

Answer / krishna chaitanya

first u must know that transformer transforms with
no change in power. As its 11 kv on primary side as
per funda you can calculate primary current 53 amps.
P = vi cos fi. A 100/5 ratio ct is enough to measure.
But its always advisable to select equipments with
larger than required ratings. Sometimes u'l see a
300/5 ratio ct.
and vcb, 800 amp vcb is for load. There'l be another
breaker at secondary of transformer with larger than
this amp rating. 800 vcb is provided for a particular
load control.
checkchaitu@yahoo.com

Is This Answer Correct ?    1 Yes 2 No

i have one transformer 1000kva, 11/.433kv. we are using 200/5 amp. ct unit for measuring purpose, ..

Answer / b2

Transformar steap down the voltage so current grow up high
so we are use 200/5 amp. ct & 800 amp.V.C.B

Is This Answer Correct ?    1 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

The CHARGED BATTERY GET DISCHARGED WHEN IT IS NOT IN USE FOR LONG TIME.GIVE REASON.

1 Answers  


Can we use 230VAC, 63A MCB for 120VAC, 63A supplied heaters load?

0 Answers  


What is R/X ratio? I have heard that this ratio is higher in a radial distribution system.Why is it so? I would appreciate a word. Thank you

1 Answers   Power Grid, Vignan University,


if the stetor speed (N S) increase by 20% then the rotor speed will be increased by 20% is it true. ?

4 Answers  


The formular of how to calculate a cross sectional cable to feed an electric motor. Examle: 15KW, 26.1A, 415V. Calculate the cable size in mm2

3 Answers   Sona,


Which motor connection is preferable star-delta or delta-star?

0 Answers   IOCL,


Define Current Transformer? Working & TYpe's Of C.T.

4 Answers  


what is open star connection or open delta.

1 Answers   ACC, Jindal,


If there is 25 hp motor,which type of starters we can us? why?

7 Answers  


why current flow to the opposite direction of flow of electrons???????????

0 Answers   Bhel,


How to increase the specific gravity of DG batteries?

12 Answers   SCS,


wich timer i have prefred for pusher operation fwd & back?

2 Answers   AluChem,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)