i have one transformer 1000kva, 11/.433kv. we are using
200/5 amp. ct unit for measuring purpose, & one 800 amp.
V.C.B Unit for the same t/f operate, i wants to known the primary
current of T/F is only 53 amp. why we used 800 amp.
V.C.B ? & 200/5 amp. CT Unit.
Answers were Sorted based on User's Feedback
Answer / vinit patil
You are right, you should fight with your electricity board
regarding the HT Metering CT ratio. You should actually
required 100/5 ratio.
But while deasigning VCB it is always prfarable to go on
higher side because it can sustain the heavy short circuit
current. One thing should be noticed that the protection
CTs should be as per the Primary current of the ransformer.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / a k kataria
Well given the rating of transformer as 1000 kva, CT ratio
should have been 100/5. As far as VCB current rating is
concernd,these are generally made for universal
applications and are generally 630 Amps onwards 'cause in
the eventuility of fault ,heavy currents are to be taken
care of.More over increase in the rated current capacity of
breaker adds little to the cost compared to other
components of the breaker.There fore capacity of VCB is OK.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / krishna chaitanya
first u must know that transformer transforms with
no change in power. As its 11 kv on primary side as
per funda you can calculate primary current 53 amps.
P = vi cos fi. A 100/5 ratio ct is enough to measure.
But its always advisable to select equipments with
larger than required ratings. Sometimes u'l see a
300/5 ratio ct.
and vcb, 800 amp vcb is for load. There'l be another
breaker at secondary of transformer with larger than
this amp rating. 800 vcb is provided for a particular
load control.
checkchaitu@yahoo.com
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / b2
Transformar steap down the voltage so current grow up high
so we are use 200/5 amp. ct & 800 amp.V.C.B
| Is This Answer Correct ? | 1 Yes | 8 No |
For RCD (Residual current device) Icu is defined. How i can find Ics for them?
what is dc voltage?
what are the differant std sizes of cable trenches?
What is earth fault?
ANY ONE TELL ME ABOUT generator synchronization panel panel to synchronise 3 gen of 250kva both automatic and manual. 2 gen output vol 415 3ph, 1 gen output vol 400 3ph SEND THE DETAILS DIAGRAM ON THIS EMAIL ADDRESS ayazleo@hotmail.com as soon as possilble best ragrds electrical engineer ayaz mahmood SAUDI TECH
A 1F capacitor is charged to 100V initially. A 1H inductor is connected accros the capacitor througha a switch. The current in the circiut when the switch is closed is____
3 Core x 35 Sqmm Cable (How we measure 35Sqmm)
4 Answers Alpha Star, Brother,
What are the properties of a resistor?
how to synchronize 4 nos. of diesel generator sets of different capacity (kva)?
what is cro
what is spadar bar .why I use in DC generator.
wat is d diffr btw shunt coil and trip coil in VCB?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)