how can check the loopchecking for valves?
Answers were Sorted based on User's Feedback
First I have explain about Loop Check. Loop check means
that we have to check the functionality of Field
Instruments to DCS/PLC.
For Valves,you have to simulate the value from DCS/PLC in
step by step(0%,25%,50%,75% and 100%).Valve actuation to be
confirmed by actuator Scale which is in the Valve.
| Is This Answer Correct ? | 21 Yes | 0 No |
Answer / s.selvakumar
control valve loop check means we have to identify open
loop or closed loop,if its closed loop we have to simulate
from primary instruments upto final control element we need
to check,if its in open loop we can stroke check from
control desk.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / r.g.m
first we must check the connections through the scheme
diagram,then trace out the open and closed limit
switches.verifiy the connections between open and closed
limits...........
| Is This Answer Correct ? | 0 Yes | 2 No |
What is cv of control valve
what is the meaning of potential free contact. difference between dry and wet contact?
How to measure the dust in chimney(spm)?
What is loop1 and loop2 in MTS LT?
if my 6 kva UPS gives 20 min. backup at 100 % load, then at 25% load what is the backup time?
please send the hpcl (instrumentation) model placement papers to my mail....
9 Answers HPCL, Invensys, IOCL, ONGC,
Explain bernoulli’s theorem. State its application.
how to measure low temperature(<100 dec celsisus) with non condact sensor
we callculat main steam flow by D.P. but where is H.P. & L.P. IN Orfics?
what is skin type thermocouple? how it is installed? what is the difference b/w thermocouple & skin type thermocouple? what is gounded & non-grounded thermocoplle? what is the diff b/w these two?
2 Answers KazStroy Engineering, PSU,
Pls.could any one Clarify the following with an example. 1.At What condition Close on Rise and Close on Fall Pressure Switch contacts are used. 2.If Pressure is abnormal as per set pressure,if connecting Terminal of pressure switch breaks,how the voltage extends to Relay base. 3.Are these contacts come under fail safe philasaphy.
our kks tagging is crossing more than 12 character please suggest how to take tags in the DCS
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)