Pls.could any one Clarify the following with an example.
1.At What condition Close on Rise and Close on Fall
Pressure Switch contacts are used.
2.If Pressure is abnormal as per set pressure,if connecting
Terminal of pressure switch breaks,how the voltage extends
to Relay base.
3.Are these contacts come under fail safe philasaphy.
Answer / carl_ellis
1. At What condition Close on Rise and Close on Fall
Pressure Switch contacts are used.
Close on Rise: the goal is to detect overpressure in normal
operation.
Common to NO is 'made' in the alarm state, logic high state.
Common to NC is open in the alarm state, a logic low state
Common to NC is open in the alarm state, the fail-safe
mode that detects a logic low state.
Close on Fall: the goal is to detect and signal loss of
pressure in normal operation
Common to NO is 'made' in the alarm state.
Common to NC is open in the alarm state
Common to NC is open in the alarm state, the fail-safe
mode that detects a logic low state
2. If Pressure is abnormal as per set pressure, if
connecting Terminal of pressure switch breaks, how the
voltage extends to Relay base.
A pressure switch is wired directly to the wiring terminals
on the microswitch inside the pressure switch. There is no
'relay base' that I'm aware of.
For normal operation (the Common and the NO contact), either
broken wire will leave the electrical circuit in a logic low
state (no voltage).
In normal operation an alarm state is a logic high condition
(the presence of voltage). That means that a broken wire
open circuit can not conduct a voltage, which means that the
circuit will have a logic low state and will fail to detect
an alarm condition.
If the circuit is wired fail-safe (the Common and the NC
contact) a broken wire creates an open circuit that cannot
conduct voltage so the circuit will be in a logic low state
(the absence of voltage) which is the same as an alarm
condition, a logic low state.
3. Are these contacts come under fail safe philasaphy.
Fail Safe is accomplished by
a) wiring to the Normally Open (NO) contacts (Common to NO
is 'made' when there is an absence of pressure) and
b) having the logic solver look for an alarm condition or a
fail condition in the logic low state.
Either the absence of pressure or an alarm state will
produce a logic low, whether the setpoint is set for
close-on-rise or close-on-fall.
Fail-safe pressure switch wiring can not detect failure
conditions like a plugged impulse line or a valve-blocked
impulse line, with the exception of United Electric's ONE
series electronic pressure switch which has plugged port
detection and an I-AM-WORKING signal mode.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
this site is owned by an nonsense
If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?
8 Answers Bharathi Cement, Titanium,
What is Erosion in a control valve?
How to calibrate radar type level transmitter for interface level? Total liquid(liq.1 and liq.2), level both the liq individually? For. Both the liquid levels how the signal will go from transmitter to dcs? How to calibrate. Single radar 9:26:55 AM for 2 different liquids in a tank?
1 Answers Almeer Technical Services,
Distributed control system
HOW FOREIGN CONTROL SYSTEM CAN BE CONNECTED WITH DCS?
the square root type transmitter r used to which applications
What is the use of valve positioner?
what is RTV function in in process control?
why using negative supply for bentley nevada vibration system ?
what are the different types of communication cables used in automation and what are the difference in the cables
We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)