Pls.could any one Clarify the following with an example.
1.At What condition Close on Rise and Close on Fall
Pressure Switch contacts are used.
2.If Pressure is abnormal as per set pressure,if connecting
Terminal of pressure switch breaks,how the voltage extends
to Relay base.
3.Are these contacts come under fail safe philasaphy.
Answer / carl_ellis
1. At What condition Close on Rise and Close on Fall
Pressure Switch contacts are used.
Close on Rise: the goal is to detect overpressure in normal
operation.
Common to NO is 'made' in the alarm state, logic high state.
Common to NC is open in the alarm state, a logic low state
Common to NC is open in the alarm state, the fail-safe
mode that detects a logic low state.
Close on Fall: the goal is to detect and signal loss of
pressure in normal operation
Common to NO is 'made' in the alarm state.
Common to NC is open in the alarm state
Common to NC is open in the alarm state, the fail-safe
mode that detects a logic low state
2. If Pressure is abnormal as per set pressure, if
connecting Terminal of pressure switch breaks, how the
voltage extends to Relay base.
A pressure switch is wired directly to the wiring terminals
on the microswitch inside the pressure switch. There is no
'relay base' that I'm aware of.
For normal operation (the Common and the NO contact), either
broken wire will leave the electrical circuit in a logic low
state (no voltage).
In normal operation an alarm state is a logic high condition
(the presence of voltage). That means that a broken wire
open circuit can not conduct a voltage, which means that the
circuit will have a logic low state and will fail to detect
an alarm condition.
If the circuit is wired fail-safe (the Common and the NC
contact) a broken wire creates an open circuit that cannot
conduct voltage so the circuit will be in a logic low state
(the absence of voltage) which is the same as an alarm
condition, a logic low state.
3. Are these contacts come under fail safe philasaphy.
Fail Safe is accomplished by
a) wiring to the Normally Open (NO) contacts (Common to NO
is 'made' when there is an absence of pressure) and
b) having the logic solver look for an alarm condition or a
fail condition in the logic low state.
Either the absence of pressure or an alarm state will
produce a logic low, whether the setpoint is set for
close-on-rise or close-on-fall.
Fail-safe pressure switch wiring can not detect failure
conditions like a plugged impulse line or a valve-blocked
impulse line, with the exception of United Electric's ONE
series electronic pressure switch which has plugged port
detection and an I-AM-WORKING signal mode.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS INITILAZIATION PLEASE HELP ME READRING THIS?
In turbine what does term CDP, NI, NH, HSSOC means.
what is modbus,profibus,fieldbus
why? Boiler furnesh pressure transmitter mount in boiler top and it's impulse line is in bottom of the boiler. Aneybody kindly tell me this reason.
what step is taken for ESD ( emergency shut down) in DCS REPLY to hashimka20009@gmail.com
0 Answers Bosch, Eskom, Sabic,
WHICH IS BEST INSTRUMENTATION OR ELECTRICAL ENGG?
plc trouble shootings?
What is the electronic transmitter frequency.
what would be the minimum flow rate that we can measure on rotameter..?
what should be minimum length and size of impulse line for steam flow orifice and feed water orifice? asked by sanjay parihar
How can we calibrate the level interface for Fisher® FIELDVUE® DLC3000?if use water to calibrate and our liquid SG are 0.75 and 1 ,Displacer height=14" and How much should be set SG in trasmitter during calibrate,for URV and LRV how shold be set
What are the cable come out from the paddle type flow sensor.and how is further connections
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)