To attain a powerfactor more than .95, how much kvr should
we use for 100 HP of current
Answers were Sorted based on User's Feedback
Answer / r. thirumoorthy
I DON'T KNOW EXACTLY, ITS MAY BE CORRECT.
POWER FACTOR=KW/KVAR;
IN THIS CASE WE KNOW KW VALUE INDIRECTLY 1 HP=746 WATTS
SO 100 HP=74600 WATTS
AND POWER FACTOR=0.95
THEREFORE REQUIRED KVAR=74600/0.95=78526.315
IF IT IS WRONG SEND ME CORRECT ANSWER.............
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / s.arul
SOLUTION:
1 HP = 735.5 watts
100 HP = 73550 watts
KVA = KW/PF
KVA = 73.55/0.95
= 77.42 KVA
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / jm
SOLUTION:
1 HP = 735.5 watts
100 HP = 73550 watts
KVA = KW/PF
KVA = 73.55/0.95
= 77.42 KVA
this solution is wrong, this solution indicate the KVAR rating for that specific power factor, for example the power factor of your 100HP is .7, its the KVAR of .7 pf not the .95 becuase you need a KVAR in order to increase its power factor, compute it using power factor correction, and vector diagrams.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / k.prakashchandra
Depends on the present pf, however 30 KVAR is generally
recommended.
| Is This Answer Correct ? | 0 Yes | 2 No |
If carbon brushes spring tension either loose or tight, what happen on Motor performance During Full load Operation?
sir what is the purpose of SF6 in HT breaker and what is the pressure should be maintain in the breaker?
How to Make relay co ordination chart for a Electrical power distribution of a plant
why we use dc motor instead of ac motor?
How Load Factor, Demand Factor, Diversity Factor etc best applied in designing an electrical circuit? Is it allowed to consider these factors in each and every panel in an electrical distribution system? Can any body suggest a good book for reference?
explain all the classes with example
which type of A.C motor is used in the fan (ceiling fan, exhaust fan, padestal fan, bracket fan etc) which are find in the houses ?
25 Answers Airtel, MPPTCL, USSA,
What is Vk and Imag i.e Knee point voltage & Magnetising Current? How to calculate above values? How to define accuracy class 5P10?
7 Answers Deccan Cements, Doosan, Torrent Power, Transco,
1. If we apply dc supply to the primary winding of transformer it will be burnt out. similarly dc supply is given to field winding of syn. motor and armature winding of dc motor, they are safe. (Remember both windings inductive nature) what is the reason behind that?
CORRECT INFORMATION ABOUT TRANSFORMERS,what actually transformer is?
why transformer rating is in KVA?
Is VVVFD reduced the starting current of an induction motor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)