Answer / zahid ali
Vk is knee point of CT it mean when 10% increase in voltage
varies the current 50% at that point we determine the knee
point voltage. In othe words excitation test of CTs,
connect a single phase variable power supply leads to the
CT seccondary leads k & l or s1, s2 along with ampere meter
& voltage meter & than apply voltage start from zero &
raise incremental simultaneously draw a graph on each
increments by plotting current on X-axis & voltage on Y-
axis.
Magnetizing current is those which is used in core & tank
of transformer due to leakage flux, which is furthur
devided into hysteris losses & eddy current losses.
We can find magnetizing current by open circuit test.
5P10 means: 5 for composite errors in percentage, P for
protection & 10 mean overlaod factor by multiply 10 times
in others words CT will not saturate by passing 10 times
higher current.
Is This Answer Correct ? | 84 Yes | 9 No |
Answer / v .selvakumar
knee point means at which the core tends towards
saturation .magnetising current means to produce flux in
the core it will take some current it is called magnetising
current.before knee point the graph between Vk and Imag
will be linear,at which point linear curve getting
disturbed .
Is This Answer Correct ? | 31 Yes | 9 No |
Answer / ugrasen
Dear friend,
Knee Point voltage is nothing but a point at which the CT
saturates. Thatsy its always better to design the CTs which
can operate without saturation even at a voltage appears in
the CT during fault condition. Pls find below the following
formula for calculating the Knee point voltage.
The formula for Knee Point Voltage is:
Vkp = K * If/CTR * (RCT + RL + RR)
in which,
K = Constant, conventionally taken as 2.0
Vkp = The minimum Knee Point Voltage
If = Maximum Fault Current at the location, in Amperes
CTR = CT Ratio
RCT = CT Secondary Winding Resistnace, in Ohms
RL = 2-way Lead Resistance, in Ohms
RR = Relay Burden, in Ohms
ugrasen.vishawakrma@gmail.com
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / gunasekaran
if it is 5P20 we can calculate from following formula
1.2*VA*ALF/rated secondary current.
magnetizing current it will be mA it may be .5 or .7 of current
Is This Answer Correct ? | 13 Yes | 3 No |
Answer / savanth
Formula for vk is as follows
vk=if(rct+2*rl)
where if is fault current
rct is ct secondary resistance rl is lead resistance
Is This Answer Correct ? | 12 Yes | 3 No |
Answer / yogesh
How to consider or calculate valu of Rct at the time of detail engineering???
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pradeep maurya
Dear friend,
Knee Point voltage is nothing but a point at which the CT
saturates. Thatsy its always better to design the CTs which
can operate without saturation even at a voltage appears in
the CT during fault condition. Pls find below the following
formula for calculating the Knee point voltage.
The formula for Knee Point Voltage is:
Vkp = K * If/CTR * (RCT + RL + RR)
in which,
K = Constant, conventionally taken as 2.0
Vkp = The minimum Knee Point Voltage
If = Maximum Fault Current at the location, in Amperes
CTR = CT Ratio
RCT = CT Secondary Winding Resistnace, in Ohms
RL = 2-way Lead Resistance, in Ohms
RR = Relay Burden, in Ohms
pkmauryain@gmail.com
Is This Answer Correct ? | 0 Yes | 1 No |
What is the theoretical reason for the size of a zig zag grounding transformer to be 1.732 times less than that of a wye-delta grounding transformer used for the same application?
what will happen if the secondary of current transformer kept open....
why the 4 terminal are named as main, line, common, voltage (M, L, C, v) of a wattmeter?? why not its nameed as A,B,C,D??
how did the testing of protection relays done through current injection
What is a differential amplifier? Also, explain cmrr.
What work have you done on full chip Clock and Power distribution? What process technology and budgets were used?
0 Answers Divis Laboratories, Intel, Sainor Labs,
formula for cable size calculation for current?
10 Answers KL Power, ONGC, RL Clean Power Pvt Ltd RLCPPL, SAS, Sobha Developers,
What happens instead of using 3 phase, if we give loop of single phase to all three phases ??
A synchronous motor is operating at a leading power factor .if the applied voltage is decreases ,(the excitation remains constant ) ,the motor current a)increases b) decreases c)remains same d) none of these
Why the voltage n frequency of the incoming generator is kept slightly higher than d grid voltage n frequency while synchronization ?
For an 100kw generator, only 50kw of load is connected. will the generator generate only 50kw or 100kw. if it generate 100kw what happens to rest of the 50kw. what happens if we connect more than 100kw of load?
why 3 phase is converted into 2 phase using electronics circuit why not 2 phases are diresctly putted from the 3 phase transformer??