What is Vk and Imag i.e Knee point voltage & Magnetising
Current?
How to calculate above values?
How to define accuracy class 5P10?
Answers were Sorted based on User's Feedback
Answer / zahid ali
Vk is knee point of CT it mean when 10% increase in voltage
varies the current 50% at that point we determine the knee
point voltage. In othe words excitation test of CTs,
connect a single phase variable power supply leads to the
CT seccondary leads k & l or s1, s2 along with ampere meter
& voltage meter & than apply voltage start from zero &
raise incremental simultaneously draw a graph on each
increments by plotting current on X-axis & voltage on Y-
axis.
Magnetizing current is those which is used in core & tank
of transformer due to leakage flux, which is furthur
devided into hysteris losses & eddy current losses.
We can find magnetizing current by open circuit test.
5P10 means: 5 for composite errors in percentage, P for
protection & 10 mean overlaod factor by multiply 10 times
in others words CT will not saturate by passing 10 times
higher current.
| Is This Answer Correct ? | 84 Yes | 9 No |
Answer / v .selvakumar
knee point means at which the core tends towards
saturation .magnetising current means to produce flux in
the core it will take some current it is called magnetising
current.before knee point the graph between Vk and Imag
will be linear,at which point linear curve getting
disturbed .
| Is This Answer Correct ? | 31 Yes | 9 No |
Answer / ugrasen
Dear friend,
Knee Point voltage is nothing but a point at which the CT
saturates. Thatsy its always better to design the CTs which
can operate without saturation even at a voltage appears in
the CT during fault condition. Pls find below the following
formula for calculating the Knee point voltage.
The formula for Knee Point Voltage is:
Vkp = K * If/CTR * (RCT + RL + RR)
in which,
K = Constant, conventionally taken as 2.0
Vkp = The minimum Knee Point Voltage
If = Maximum Fault Current at the location, in Amperes
CTR = CT Ratio
RCT = CT Secondary Winding Resistnace, in Ohms
RL = 2-way Lead Resistance, in Ohms
RR = Relay Burden, in Ohms
ugrasen.vishawakrma@gmail.com
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / gunasekaran
if it is 5P20 we can calculate from following formula
1.2*VA*ALF/rated secondary current.
magnetizing current it will be mA it may be .5 or .7 of current
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / savanth
Formula for vk is as follows
vk=if(rct+2*rl)
where if is fault current
rct is ct secondary resistance rl is lead resistance
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / yogesh
How to consider or calculate valu of Rct at the time of detail engineering???
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pradeep maurya
Dear friend,
Knee Point voltage is nothing but a point at which the CT
saturates. Thatsy its always better to design the CTs which
can operate without saturation even at a voltage appears in
the CT during fault condition. Pls find below the following
formula for calculating the Knee point voltage.
The formula for Knee Point Voltage is:
Vkp = K * If/CTR * (RCT + RL + RR)
in which,
K = Constant, conventionally taken as 2.0
Vkp = The minimum Knee Point Voltage
If = Maximum Fault Current at the location, in Amperes
CTR = CT Ratio
RCT = CT Secondary Winding Resistnace, in Ohms
RL = 2-way Lead Resistance, in Ohms
RR = Relay Burden, in Ohms
pkmauryain@gmail.com
| Is This Answer Correct ? | 0 Yes | 1 No |
how will we calculate the copper wire load..
Why does the radius of armature is less than the radius of pole shoe?
Why LT cables are not sized based on short circuit capacity.
Why should we use jelly filled armoured cables in underground Communication system? What is the use of the Jelly? If we go for unarmoured, then what happens?
1. name the relay for protecting transformer 2. Current Transformer 3. potential Transformer
what is impedence in transformer
what will happens if one phase is missing for 33/11kv power transfomer and why?
A 3PH MOTOR RUNNING IN NORMAL CONDITION AND ITS AMPERE ALSO UNDER ITS FULL LOAD CURRENT,ITS CABLE RATINGS ALSO HIGER THN ITS CAPACITY,BUT ITS CABLE GETTING ABNORMAL HEAT(NOT TOO HOT)WHY ITS GETTING HOT LIK THIS?
Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?
why receiving end voltage increases in a system when capacitive load is added
1.Z transform always lies around ? a) origin b) pole c) zero d) z=1. Multiples Mcqs which is bother me can’t find answers on internet. Some help required with little explanation . Note: this is not homework or related to any test. Thanks
My load is 15 kw,i want to improve power factor from 0.8 to 0.9,how select capacitor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)