Answer / n arunkumar
CT secondary is 5A in Low voltage systems because we need
more graduation in measurement of current.Moreover measuring
range is small in LT system. but in High voltage system, the
measuring range is more.we need more accuracy. so we prefer
1A secondary in HT system.
| Is This Answer Correct ? | 24 Yes | 2 No |
Earlier they were using electromagnetic relays and
meters.Hence for accuracy and workability higher current
was required. Now a days CTs of 1 A secondaries are
used ,as electronic meters and relays have replaced them
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / nagarjuna
most of the relays work at lower rating generally 5 amps.we
get more accuracy with small rating.so that relays r
generally 5 amps
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sobhuza, za
5A CTs are used beacuse they are cheaper than 1A Cts for
the same primary rating.I mean 600/1A CT is more expensive
than 600/5A CTs as more turns are in the former. 5A CTs
also imply that under full load conditions, 5A is flowing
between the CTs and the relays. Therefore there will be a
large volt-drop if the CTs are far away from the relays.
This is the reason why it 5A CTs are used for indoor
switchgear. Recall that the indoor switchgear houses the
relays as well so the CTs and the relays are closer to one
another. Therefore you will note that 5A CTs are not used
for outdoor CTs.
| Is This Answer Correct ? | 2 Yes | 5 No |
how to design coil turns ?
What is difference between PVC cable & XLPE cable?
If i switch on a transformer but with no load connected to the secondary path.Is the transformer will burn?
Fault current shall be part of tech specs of power cable or not?.
compressor compresses air means exactly what happens?
how can a transformer test by megger?
what is mean by tan-delta tap in the potential transformer??
Difference between divercity and power factor
What are the different types of testing in ht cables?
Relay setting for earth fault of reciprocating and centrifugal compressor motor feeder.Setting will be different or same?
what you mean by current? what you mean by voltage? what is difference between star and delta connection in motor side?
Dear Friends, Need your help for connecting APFC panel, Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR) Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)