why C T secondary are rating 5A generaly .
Answers were Sorted based on User's Feedback
Answer / n arunkumar
CT secondary is 5A in Low voltage systems because we need
more graduation in measurement of current.Moreover measuring
range is small in LT system. but in High voltage system, the
measuring range is more.we need more accuracy. so we prefer
1A secondary in HT system.
| Is This Answer Correct ? | 24 Yes | 2 No |
Earlier they were using electromagnetic relays and
meters.Hence for accuracy and workability higher current
was required. Now a days CTs of 1 A secondaries are
used ,as electronic meters and relays have replaced them
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / nagarjuna
most of the relays work at lower rating generally 5 amps.we
get more accuracy with small rating.so that relays r
generally 5 amps
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sobhuza, za
5A CTs are used beacuse they are cheaper than 1A Cts for
the same primary rating.I mean 600/1A CT is more expensive
than 600/5A CTs as more turns are in the former. 5A CTs
also imply that under full load conditions, 5A is flowing
between the CTs and the relays. Therefore there will be a
large volt-drop if the CTs are far away from the relays.
This is the reason why it 5A CTs are used for indoor
switchgear. Recall that the indoor switchgear houses the
relays as well so the CTs and the relays are closer to one
another. Therefore you will note that 5A CTs are not used
for outdoor CTs.
| Is This Answer Correct ? | 2 Yes | 5 No |
How do you select a cable size(Cu&Al) for a particular load
10 Answers Adhunik, BPCL Bharat Petroleum, Hiecon, TATA,
For single phase(phase to neutral) having potential difference 230.in three phase(phase to phase)we have 440V HOW...?
what is the voltage rating of chiller unit sensors
What is the difference between KW & KVA ?
How many percent of power are not being registered if we bypass one side of the meter base terminal using #8 cu wire on 1-phase kwhr meter.
If any cable burnt how can we identify it burnt by high current of high voltage?
How to calculate the sag on transmission Lines.
what is the impedence
How to calculate the cable size in sq. mm. when the load is given in KW?
I have a 600VA UPS for computer only. It holds for 20minutes only. 1. Can it be upgraded for longer period.? 2. Can it be used for one ceiling fan and a tube light? If yes, how to upgrade?
what are the components of a start and stop motor control?
what is the requirement regarding earthing of Single conductor with AWA
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)