Cube tests of concrete are failed at 7 days and 28
days.What is your next action?
Answers were Sorted based on User's Feedback
Answer / vaibhav jadhav
Any is code not give the clause regarding demolishing of
structure if cube fails in 28 days. but IS 456 & 516 give
the clause if strength of cube is less than FCK then
proceed for NDT Test i.e Rebound hammer if fail then go for
Ultrasonic test after all the NDT fail then proceed for
Core cutter also if U found result less then FCK then go
for Retrofitting with suggestion of consultant.
| Is This Answer Correct ? | 33 Yes | 2 No |
Answer / abhijit
ensist contractor to hold skilled man power with quallity
material. note the result in daily work progress and mark
on structure which is not as per specification. finally go
for NDT if also structure fails then we have to demolish &
reconstruct the same
| Is This Answer Correct ? | 37 Yes | 10 No |
Answer / nravindran
Go for NDTest, if it is not satisfied go for Core test that
is also failed go for concrete strengthing process As per
structural consultant comments
| Is This Answer Correct ? | 19 Yes | 4 No |
Answer / vimalsekar
Well. When Concrete cube test result fails at 28th day then
go for concrete core cutting and check the compressive
strength in it. Number of cores shall be as per the
engineer incharge's decision but should not be less than 3
nos. IS:456 says if the core test fails then go for load
test. IS : 456 also says that NDT can be done . But with
rebound hammer test only surface hardness will be known and
hence this test result is not reliable and hardly anyone
suggests for this test.
| Is This Answer Correct ? | 18 Yes | 3 No |
Answer / shafqat
Use concrete tester rebound hammer for strength after
calibration.
Perform test as per standard,if results is more than 100 %
of requirement by calibration graph of hammer continue the
structure.
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / kishorecivil
NDT testing has to be done and if it fails then go for
recto method that is strengthing of concrete and concern is
not demolish it's time taken and it will effect time and
finacial.
| Is This Answer Correct ? | 8 Yes | 7 No |
Answer / prabhakara rao.b
Go for NDT If it is not satisfied go for Core test that
is also failed go for there possibale demolisan that coloum
it is not possible we go for Restrengthing.
| Is This Answer Correct ? | 4 Yes | 3 No |
How many times one TMT bars bents & straight upto not broken the bar.
What are the types of slump?
what are the advantages and disadvantages of using bentonite slurry in bored cast in situ piles, both in terms of design and execution point of view.
How we can calculate cement and sand for a wall 25ft x 28ft.Thickness of wall is 9inches.
How to calculate the Qty of Mortar in 1 m3 Brick work? Detailed Calculation Required?
what are the differences between Tie beam, Ground beam and strap beam. thanks
while doing floring in a room,from where one can start laying tiles.
what is the proportion of stones and concrete inplum concrete??
what is a civil enggineer ?
What is mean by Engineers ?
Materials datas like cement sand steel brick 20&40mm aggregate required per sqft of building?
what would be the rqmnt. of cement and sand (1:6)for building brick wall and also 20mm thick plaster on the wall by same ratio?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)