Why alternators are rated in KVA?
Answers were Sorted based on User's Feedback
Answer / nithi
We can design the machines only for rated voltage(insulation
arrangement) & rated current(cooling arrangement,winding
thickness).
we can't predict the power factor while designing the
machine.Because,it is depending upon the load .
This is reason for why transformers & alternators
are rated in KVA.
| Is This Answer Correct ? | 100 Yes | 6 No |
Answer / iamdon
Rating of an alternator or any electrical machine/apparatus
reflects its load carrying capability without
overheating.Temperature rise (major threat to insulation)
arises due to internal loss within the machine.
These internal losses include
1)Copper loss and
2)Core or Fe loss(hysterisis and eddy)
Both losses are independent of power factor.
Copper loss is directly proportionl to I*I
Core loss is function of voltage applied/genetated.
Both loss must be taken into account for rating
purpose.Which is only possible with taking VA which has
nothing to do with power factor.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 45 Yes | 12 No |
Answer / shariff
Transformers or alternators are rated in kvA not in kw/MW
bcoz its losses like hystersis or eddy current or copper
losses are depend upon the frequency or current non of them
on the pf. There is no consideration of pf for this machines
hence they are rated in kvA's.
| Is This Answer Correct ? | 46 Yes | 20 No |
Answer / sohag kumar saha
Cu loss depends on current & iron loss depends on voltage.
Hence total Transformer/Alterntor loss depends on
volt-ampere(VA) and not on phase angle between voltage &
current i.e., it is independent of load power factor.That is
why, rating of transformers is in kVA & not in kW.
| Is This Answer Correct ? | 18 Yes | 1 No |
Answer / goud
the corelosses depend on voltage and copper losses dependon
current .so the rating of alternator or transformer are
mentioned in kva
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / nitin k
generally while designing an alternator we must consider 2 circuits:. i.e. electrical ckt.& magnetic ckt. Electrical ckt.is designed by considering current & magnetic circuit by volt. thats why rating is in kva.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / padmaja.s.
in transformers and alternators we have 2 types or
losses..those are eddy current and hysterious losses.eddy
current losses are depends on current..trese are variable
losses.and hysterious losses depends on voltage.so these
two losses are depends on current and voltage...so the
ratings of transformer and alternaters are rated in
voltampers(VA)Or KVA
| Is This Answer Correct ? | 9 Yes | 6 No |
Answer / oni
cu loss of transformer/alternator depends on current and iron loss on voltage.Hence total loss depends on volt-ampere(VA) and not phase angle between voltage and current that means it is independent of load power factor. That is why rating of transformer/ alternator is in KVA and not in KW.
| Is This Answer Correct ? | 2 Yes | 0 No |
transformer cooling fan kharab ho jaye to 1-off kar dena chahiye 2-load kum kar dena chahiye 3-koi frrk nhi padta 4-sub galat hai. choose right option
2 Answers PGVCL Paschim Gujarat Vij Company Limited,
why induction motor take more current when motor start time and this current take for 1 hours when motor is start.
We are preparing another project which involves Waste heat recovery from a 1 MW GE Engine. The Engine in particular gives out flue gas at 487Deg C with a flow rate of 5650 kg/hour and this can be cooled to 180 Deg C. This gives a thermal output of ~ 594 KW that is available for input to VAM via heat exchanger / boiler. Additionally 581 KW will be available from engine jacket water (temperature profile 80/ 80 Deg C and a flow rate of 50m3/hr) Our estimation is that 300 TR of cooling is possible with a suitable VAM machine(s). Please advise what is the most suitable arrangement with maximum TR and min Capital expenditure. plz reply me as early as possible
How 3 phase invertor works?
how to convert star network in delta or vice versa...?
Lt motor sfu flashing reasons?
what is linear elements
what about electrical pannel.? What is meant by plc pannel.?
why square root 2 is multiplied with line voltage in selection of LA ie 11/sqrtroot3=6.35 kv and it is multiplied with sqrt2 ie 6.35 KV*sqrt2=8.9 kv we will select 9kv.my question is why we are multiplying with sqrt 2?
In the case of petrochemical area AC drive & AC motor is used where the speed variation is required. Why they are not Using DC drive & DC motors in such areas?
Current Capacity of 55sqmm & 80sqmm conductor
How to calculate energy stored in an inductance?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)