Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why alternators are rated in KVA?

Answers were Sorted based on User's Feedback



Why alternators are rated in KVA?..

Answer / nithi

We can design the machines only for rated voltage(insulation
arrangement) & rated current(cooling arrangement,winding
thickness).
we can't predict the power factor while designing the
machine.Because,it is depending upon the load .

This is reason for why transformers & alternators
are rated in KVA.

Is This Answer Correct ?    100 Yes 6 No

Why alternators are rated in KVA?..

Answer / iamdon

Rating of an alternator or any electrical machine/apparatus
reflects its load carrying capability without
overheating.Temperature rise (major threat to insulation)
arises due to internal loss within the machine.
These internal losses include
1)Copper loss and
2)Core or Fe loss(hysterisis and eddy)
Both losses are independent of power factor.

Copper loss is directly proportionl to I*I
Core loss is function of voltage applied/genetated.

Both loss must be taken into account for rating
purpose.Which is only possible with taking VA which has
nothing to do with power factor.

Author:arbelectbit@yahoo.com

Is This Answer Correct ?    45 Yes 12 No

Why alternators are rated in KVA?..

Answer / shariff

Transformers or alternators are rated in kvA not in kw/MW
bcoz its losses like hystersis or eddy current or copper
losses are depend upon the frequency or current non of them
on the pf. There is no consideration of pf for this machines
hence they are rated in kvA's.

Is This Answer Correct ?    46 Yes 20 No

Why alternators are rated in KVA?..

Answer / sohag kumar saha

Cu loss depends on current & iron loss depends on voltage.
Hence total Transformer/Alterntor loss depends on
volt-ampere(VA) and not on phase angle between voltage &
current i.e., it is independent of load power factor.That is
why, rating of transformers is in kVA & not in kW.

Is This Answer Correct ?    18 Yes 1 No

Why alternators are rated in KVA?..

Answer / iamdon

Very well said by Nithi.

Is This Answer Correct ?    15 Yes 2 No

Why alternators are rated in KVA?..

Answer / goud

the corelosses depend on voltage and copper losses dependon
current .so the rating of alternator or transformer are
mentioned in kva

Is This Answer Correct ?    11 Yes 3 No

Why alternators are rated in KVA?..

Answer / nitin k

generally while designing an alternator we must consider 2 circuits:. i.e. electrical ckt.& magnetic ckt. Electrical ckt.is designed by considering current & magnetic circuit by volt. thats why rating is in kva.

Is This Answer Correct ?    5 Yes 1 No

Why alternators are rated in KVA?..

Answer / padmaja.s.

in transformers and alternators we have 2 types or
losses..those are eddy current and hysterious losses.eddy
current losses are depends on current..trese are variable
losses.and hysterious losses depends on voltage.so these
two losses are depends on current and voltage...so the
ratings of transformer and alternaters are rated in
voltampers(VA)Or KVA

Is This Answer Correct ?    9 Yes 6 No

Why alternators are rated in KVA?..

Answer / arijit

answer no 3 is perfect

Is This Answer Correct ?    5 Yes 2 No

Why alternators are rated in KVA?..

Answer / oni

cu loss of transformer/alternator depends on current and iron loss on voltage.Hence total loss depends on volt-ampere(VA) and not phase angle between voltage and current that means it is independent of load power factor. That is why rating of transformer/ alternator is in KVA and not in KW.

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

WANTCONTACT NUMBER & EMAIL/ WEBSITE TO CONTACT THE SECRETARY,MADHYA PRADESH LICENSING BOARD(ELECTRICAL),K- BLOCK,3RD FLOOR,SATPOODA BHAWAN,BHOPAL

0 Answers  


why one side of tubelight glows after switch off ?

1 Answers  


how can we convert 48V dc into 12 V dc? Any standard device for it??

2 Answers  


11KV electrical line going through the forest in cloudy night ,how can we find the direction of line.

5 Answers   Bhel, Cesco, HZL, Nesco,


can you give me some names of projects which can be used in our daily life & which is having medium cost?

1 Answers  


what is diff. between earthing grid,earthing mess, earting grid?

0 Answers   Century Rayon, Emco, Tailor Solution,


NGR? What is NGR?

14 Answers  


what is the min and max dc voltage for a dc system (110vdc)

1 Answers   ASD Lab,


in three phase with neutral connection, what will happen,if the neutral is in open condition with single phase distribution panel ?

2 Answers  


why in crona effect it give violet colour.

1 Answers  


How will you justify IR value and Charging voltage of any motor,transformer and Cables.......???? . . . . . . . . Plz tell me any body Baljeet Singh, engineer_89@refiff.com

0 Answers  


I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)