Answer / nithi
We can design the machines only for rated voltage(insulation
arrangement) & rated current(cooling arrangement,winding
thickness).
we can't predict the power factor while designing the
machine.Because,it is depending upon the load .
This is reason for why transformers & alternators
are rated in KVA.
| Is This Answer Correct ? | 100 Yes | 6 No |
Answer / iamdon
Rating of an alternator or any electrical machine/apparatus
reflects its load carrying capability without
overheating.Temperature rise (major threat to insulation)
arises due to internal loss within the machine.
These internal losses include
1)Copper loss and
2)Core or Fe loss(hysterisis and eddy)
Both losses are independent of power factor.
Copper loss is directly proportionl to I*I
Core loss is function of voltage applied/genetated.
Both loss must be taken into account for rating
purpose.Which is only possible with taking VA which has
nothing to do with power factor.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 45 Yes | 12 No |
Answer / shariff
Transformers or alternators are rated in kvA not in kw/MW
bcoz its losses like hystersis or eddy current or copper
losses are depend upon the frequency or current non of them
on the pf. There is no consideration of pf for this machines
hence they are rated in kvA's.
| Is This Answer Correct ? | 46 Yes | 20 No |
Answer / sohag kumar saha
Cu loss depends on current & iron loss depends on voltage.
Hence total Transformer/Alterntor loss depends on
volt-ampere(VA) and not on phase angle between voltage &
current i.e., it is independent of load power factor.That is
why, rating of transformers is in kVA & not in kW.
| Is This Answer Correct ? | 18 Yes | 1 No |
Answer / goud
the corelosses depend on voltage and copper losses dependon
current .so the rating of alternator or transformer are
mentioned in kva
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / nitin k
generally while designing an alternator we must consider 2 circuits:. i.e. electrical ckt.& magnetic ckt. Electrical ckt.is designed by considering current & magnetic circuit by volt. thats why rating is in kva.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / padmaja.s.
in transformers and alternators we have 2 types or
losses..those are eddy current and hysterious losses.eddy
current losses are depends on current..trese are variable
losses.and hysterious losses depends on voltage.so these
two losses are depends on current and voltage...so the
ratings of transformer and alternaters are rated in
voltampers(VA)Or KVA
| Is This Answer Correct ? | 9 Yes | 6 No |
Answer / oni
cu loss of transformer/alternator depends on current and iron loss on voltage.Hence total loss depends on volt-ampere(VA) and not phase angle between voltage and current that means it is independent of load power factor. That is why rating of transformer/ alternator is in KVA and not in KW.
| Is This Answer Correct ? | 2 Yes | 0 No |
What is the diffrence between ofline ups and online ups?
The initial current is very large at the time of starting for almost all DC motors. SO WE USE STARTER FOR A SAFE STARTING but at our homes we don’t see any starters in our coolers, motors.WHY DON’T WE NEED STARTERS FOR THESE APPLIANCES?
What is the difference between electric and electronic circuits?
we are small scale industry in production of rice & rice bran. Pls let me know how to take contract demand for our industry.. (for information we have total 600.hp)
We have three 33kv substations. All of them energised by same source.When i am checking the phase sequence between one substation to other substation (like R Phase to R Phase) by multimeter i am getting some voltage.Near to LT panels UPS panels are there. Can u explain whether any possible to happen like that. In Phase SEquencemeter is showing correctly in both substations. How is it happen. Explain me.Explain me communication signal will produce Phase difference on this case.
What happen when neutral point connected to core balance current transformer? (Neutral point of an alternator of a 180KVA DG. Neutral point connected to CBCT means enter to the CBCT)
1 Answers Great Eastern Energy Corporation Ltd,
What is ht lt switchgear.
3 Answers Bhel, HBL Power Systems,
can i use the six sigma method which is used in management area, in state estimation of power systems?
1.how many types of relays? 2.difference between ATS& STS?
I Want randstand placement papers
Whis machine is having higher efficiency Transformer or Generator
Can we connect more than one NGR at a time of different rating of generators. what is advantage or disadvantage.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)