Whether the over frequency protection is turbine or alternator
and why?
Answer / k.prakashchandra
Over frequency relay is for gen and over speed relay is for
turbine.They are normally set at +/- 3 % and 15 % respectively.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is unit of inductance
12 Answers Bhel, Bosch, OSML, Vijai Electricals, Voltage,
why are the likely reasons for bochholz & pressure relays oprate due to a internal fault but not differential relay ?
What is the differance between transformer neutral solidly earthed and transformer neutral earthed through resistor?
In a transformer ,when voltage decreases current increases. but this is a violation of oms law.why?
How to choose size of the cable w.r.to current carrying capacity ...
1.25 kg of hydrogen are burnt with stiochiometric air, the mass of air in kg required is
In a Dyn11 transformer, how are the 3 windings of the delta connected? Assume that R1-R2, Y1-Y2, B1-B2 are the 3 windings on the HV side.
if the load is 80 amp for main fuse and 100 amp for breaker so how can we calculate the cable size (cooper ) .
how to calculate the breaking capacity of different breakers.
why transformers are put with supply for 24 hours before giving supplying to a locality?
Load transfer in 11kv double busbar switchgear - operation.
I had applied for JE in PSEB, Can you pls send me the Question bank for related to my field
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)