Answer / ajay kumar das
Transformers are rated in KVA . because it works in various PF.The P.F is vital for KW as power is V.I.PF.So as we dont know the load PF transformers are rated in KVA.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rrk
Copper loss & iron loss ,Cu Loss its depends upon current (A),Iron loss depends upon Voltage (V) ,Thats y trafo rating in KVA
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / coolclikker
because on the load end there is a real & reactive load both
are connected. Due to reactive load power factor is lagging
so due to low power factor actual capacity of the
transformer becomes less and losses increases. So that's why
capacity is always given in Apparent power(KVA). KVA is
actually the capacity that how much power a transformer can
supply to load
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / iffi
very simple the power factor of the load is unknown to manufacturer of the TRAFO. for which it is going to be used
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / karthick
The transformer will transfer both real and reactive power . That is the apparent power in KVA . That'y it is rated in KVA ,
| Is This Answer Correct ? | 0 Yes | 1 No |
Why breakers not synchronized when the synchroscope is going in the anticlockwise direction?
If 100 KAV USP dedicated earth got disconnect / Cut. What will happen at load.
what is reactive power?, why its measured in VA ? is it transient behavior of system?
What it the purpose of parallel phasing transfomers??
HOW THE OLTC TRANSFORMER SAVE ENERGY IN COMPARISON TO OFF LINE TRANSFORMER AND IS IT ECONOMICAL TO REPLACE THE OFF LINE TRANSFORMER TO OLTC TRANSFORMER
If the 11 KV supply is fail. what will happened with it's breaker if it is supplay to the 11KV motor?
I've descovered that when the earth wire in a domestic electrical installation is not connected back to the board (ground) a voltage of between 9-24v is is found to be present in the earth wire. When connected at the board there is no voltage - is this normal and why does it happen?
What is the function of an exciter in a generator?
how to measure earth resistance of a substation
what is the AC Plant and how can do the work with parts and picture tell us 150 Tr
what's burden resistor, why it's used?
What is the full form of PSD & CSD ?
6 Answers NIFT, PNG Power, PSD,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)