why we take transformer reading in kva
Answers were Sorted based on User's Feedback
Answer / ajay kumar das
Transformers are rated in KVA . because it works in various PF.The P.F is vital for KW as power is V.I.PF.So as we dont know the load PF transformers are rated in KVA.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rrk
Copper loss & iron loss ,Cu Loss its depends upon current (A),Iron loss depends upon Voltage (V) ,Thats y trafo rating in KVA
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / coolclikker
because on the load end there is a real & reactive load both
are connected. Due to reactive load power factor is lagging
so due to low power factor actual capacity of the
transformer becomes less and losses increases. So that's why
capacity is always given in Apparent power(KVA). KVA is
actually the capacity that how much power a transformer can
supply to load
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / iffi
very simple the power factor of the load is unknown to manufacturer of the TRAFO. for which it is going to be used
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / karthick
The transformer will transfer both real and reactive power . That is the apparent power in KVA . That'y it is rated in KVA ,
| Is This Answer Correct ? | 0 Yes | 1 No |
Why the frequency of ac in india is 50 hz but in some other countries it is 60 hz.
Tell me in detail about c.t. And p.t. ?
when conductor rotates in varying magnetic field the emf will induced in it and it is sinusoidal in nature ...? Why it is not in square wave and rectangular wave in nature?
Difference Between B Curve & C Curve in MCB.
What should be distance required in between two phase of HT cionductors in open area??????
On which side, taps are provided in tap changing transformers and why?
In which reason, one end of CT secondry get connected with Earthed? Normaly S1 of CT. Why????
is it value of power factor is more than unit. whats effects in the source supply
what is the ground clearance of 400KV transmission line?
9 Answers Power Grid, wbsedcl,
what is the diff. between power transformer & distribution transformer.....
what is the deference between watt and KVA
What is minimum permicible value of leackage current for LT Panle when applying voltage up to 3 KV for 5 Minuits?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)