why we take transformer reading in kva
Answers were Sorted based on User's Feedback
Answer / ajay kumar das
Transformers are rated in KVA . because it works in various PF.The P.F is vital for KW as power is V.I.PF.So as we dont know the load PF transformers are rated in KVA.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rrk
Copper loss & iron loss ,Cu Loss its depends upon current (A),Iron loss depends upon Voltage (V) ,Thats y trafo rating in KVA
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / coolclikker
because on the load end there is a real & reactive load both
are connected. Due to reactive load power factor is lagging
so due to low power factor actual capacity of the
transformer becomes less and losses increases. So that's why
capacity is always given in Apparent power(KVA). KVA is
actually the capacity that how much power a transformer can
supply to load
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / iffi
very simple the power factor of the load is unknown to manufacturer of the TRAFO. for which it is going to be used
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / karthick
The transformer will transfer both real and reactive power . That is the apparent power in KVA . That'y it is rated in KVA ,
| Is This Answer Correct ? | 0 Yes | 1 No |
What are the basic properties of signal flow graph?
One B.O.T Unit ??
can anyone send me some sample question regarding power grid corp
what are the standard values for resistances(Megger testing) between L&N, L&E and N&E (L=Live,N=Neutral, E=Earth)?
what's ripple content in rectifier? how it formed?
What is an Antipumping relay ?
what are the types used for alternator earthing,what will happen if more than two alternator is working in parallel with each having own system earthing.is there any possibility for circulating current in between two system.
HOW WE KNOW IN PHYSICALLY THE CONTACT SURFACE OF A VACUUM INTERRUPTER IS GOOD OR GOING TO DAMAGE IN A VCB AFTER ABOVE 500 TIMES OPERATED.
what is ht breaker
what will be the motor terminal box connection arrangement (star or delta). on what basis it decided?
any one guide me to reduce the power factor of diesel Generator from 0.97 Leg to 0.8 Leg.with out any change in my load.
What is the difference between voltage and emf ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)