Why CT secondary should not left open??????????
Answers were Sorted based on User's Feedback
Answer / iamdon
The CT secondary should not be left opened secondary due to
following reasons:
1)Zero current in secondary leads zero back emf.So primary
current becomes very high.Large heat generated may burn the
winding and core.If the transformer sustain this heat, even
then its operation becomes improper as explained below.
2)CT is bascially a step up transformer.So high voltage
induced in secondary may saturate the core (core becomes
permanently damaged).So the operating point advances in non
linear region,which makes the transformer operation improper
(secomdary current will not replicate the primary according
to the turn ratio).
3)High voltage induced in secondary side may endanger the
life of personnel working on the side.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 16 Yes | 2 No |
Answer / bhautik patel
due to the absence of the counter ampere-turns of the secondary, the unopposed primary mmf will set up high flux in the core which will produce excessive core loss with subsequent heating & high voltage across the secondary terminals.
| Is This Answer Correct ? | 3 Yes | 0 No |
what is ground fault in ACB?
if 6 earth pit value is 1.5 ohm then what should be the number of earth pit to make the value .8 ohm
Is it advisable to buy a plot for house construction near High Tension Power lines? If it so how much distance it should be away from power line? Iam residing at Chennai, Tamilnadu, India.
what is the formula of starting current of 3phase and 1 phase motor???
what happen if field of dc shunt motor opens? what is function of putting res. in parallel to one phase of 3 phase IM? the power supplied by 5A source in circuit is given by------Watt.
define the power factor in one word
What is the required value while doing the megering
What is SNMP Card Monitoring in UPS???
PLZ SEND ME SOME UNIQUE PROJECT OF ELECTRICAL ENG (B.TECH)
what determins the amount of voltage produced by a voltaic cell?
If the load of transformer is getting more than its rating,,,than how to overcome this problem? Suppose thee rating of transformer is 315kva and the load is going beyond than the rating say around load: 352kva... Than how can we solve this problem without deducting the load.
What will hapen if we run generator below 47.6hz frequency?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)