Why CT secondary should not left open??????????
Answers were Sorted based on User's Feedback
Answer / iamdon
The CT secondary should not be left opened secondary due to
following reasons:
1)Zero current in secondary leads zero back emf.So primary
current becomes very high.Large heat generated may burn the
winding and core.If the transformer sustain this heat, even
then its operation becomes improper as explained below.
2)CT is bascially a step up transformer.So high voltage
induced in secondary may saturate the core (core becomes
permanently damaged).So the operating point advances in non
linear region,which makes the transformer operation improper
(secomdary current will not replicate the primary according
to the turn ratio).
3)High voltage induced in secondary side may endanger the
life of personnel working on the side.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 16 Yes | 2 No |
Answer / bhautik patel
due to the absence of the counter ampere-turns of the secondary, the unopposed primary mmf will set up high flux in the core which will produce excessive core loss with subsequent heating & high voltage across the secondary terminals.
| Is This Answer Correct ? | 3 Yes | 0 No |
what is Distance protection & how did it work
iii) A shunt motor runs at 70 rad/sec from a 460V supply and takes in an armature current of 100A. Resistors of 2.52 ohms and 1.64 ohms are connected in series with the armature and in parallel with the armature respectively. The field excitation remains direct from the 460V supply but the generated torque is halved. Determine the new running speed. Neglect brush voltage drop. The armature resistance is 0.4 ohms. [15]
i want to learn control schedule for 11kv panel? can any one send the detailed control schedule?
What is the harm if we install primary side 11 KV VCB at a distance of one Km from the 11/3.3KV 12.5 MVA transformer through 11 KV cable.
Will The Rated Capacity of 20 MVA ,220/6.6 KV, ONAN cooling Power Tranformer be increased up to 25 MVA with respect to its %Impedence by ONAF cooling with same rating..?
What is the previous name of Cox's Bazar
how can we Increase the Value Of Frequency in electric circuits
NGR? What is NGR?
what is back trip and re-trip in protection schemes? why these two? define me the exact function of these two?
What are the temperature elements?
Either It Possible a dc Motor to Run On Ac Drive [ Ex : ACS 800 , Yaskawa F7 ] If it is Possible How Pls Inform Me dinesh_elect_eng@yahoo.com
Diagram and details of polarity test for Current Transformer 11kv 400/200/100/1A
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)