Answer / vikas
Synchronous machine can run on both AC and DC
excitaion...The speed at which the machine will rotate will
depend on the relative frequency of stator and rotor
supply...i.e.if machine is connected to grid of 50 Hz
frequency and rotor is also provided with 50 Hz frequency
source then relative frequency will be 0 and machine will
not rotate because average torque produced will be 0 as
someone has already mentioned, but if rotor frequency is
say 20 Hz then the relative frequency will be 50-20=30 Hz.
so the machine speed will be 120f/p..substitute f= 30
Hz..when the rotor supply is DC then the relative frequency
is 50-0= 50 Hz. so the machine speed is given by
substituting f= 50 Hz in this case...
| Is This Answer Correct ? | 71 Yes | 25 No |
because only dc current can produce the fixed pole i.e. the
poles produced by the dc current does not change with time
as in the case of the poles produced by ac current.
now when the stator of the machine is supplied the ac
current the rotating magnetic current is produced.
the dc excitation is necessary so that the poles produced
by the dc current and ac current both attrect each other
which will be responsible for the production of the torque.
| Is This Answer Correct ? | 46 Yes | 6 No |
Answer / b. b. shukla
In a synchronous motor, a rotating magnetic field is produced in stator by giving 3 phase AC supply.Now as per working principle of syn. motor,rotor must have a magnetic locking with stator field. For this purpose we need permanent magnetic poles in rotor so that rotor pole will form magnetic locking with nearest opposite pole of rotating stator field and rotates with stator field at synchronous speed.
Now to form permanent magnetic poles in rotor, DC excitation is fed to rotor winding of synchronous motor.
| Is This Answer Correct ? | 22 Yes | 0 No |
if AC excitation is given then alternate north and south
pole is created on rotor field
the rotor move half cycle clockwise and half cycle anti
clockwise and finaly stop to rotate
due to this dc current is given to the rotor of the
syncroneous motor
| Is This Answer Correct ? | 38 Yes | 18 No |
Answer / pranav patel
it's all about on ac when we applied 3-p supply to the syn
motor it's indused rotating magnetic field and this
magnetic field rotate in synchronous speed so if u r stator
winding is two pole so ur rotor it's also two pole so when
we given supply same pole creat attrection so rotor rotate
in half round and when polarity change differnt pole ripple
so second time its rotate half round in another direction
so we need
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / rahul
Excitation is provided to rotor. Now dc field which is made
rotating in space produces a rotating magnetic field. AC
exciation can be thought as two separate magnetic fields
rotating in opp. directions. Also both the fields are of
same strength and thus net torque is zero. So we must
provide DC and not ac excitaion to synchr m/c.
| Is This Answer Correct ? | 3 Yes | 9 No |
my question is why do we provide DC excitation????
can we provide AC excitation to the notor???
| Is This Answer Correct ? | 11 Yes | 28 No |
Answer / ashok kumar
In AC synchronous motor its stator coil is not a
permanment magentising property so it is connected with dc
exciter for initial operation purpose.
| Is This Answer Correct ? | 5 Yes | 33 No |
please let me know , we have installed two separate motor for fire fighting system 1) 60 hp and 2) 15 hp the load is 74 AMPS and 20 AMPS then tell me the main power cable in Aluminum will be what thickness , the length is 225 mt from the main utility to fire pump house
i completed my DEEE. and i want to electrical c license. how to get it..?
What should be the Sandwitch type Al. bus bar capacity for 2 M.W.Gen. set, having continuous full load current- 3463 Amps,ambient temp.- 50 Deg. C., Required temp. raise-20 deg.C., it will run 24 hrs, 365 days on full load, required highly reliable.
What will happen if mains neutral and generator neutral shorted?
how to calculate the size of the HT cable
How can identify meter AC or DC without use of symbel?
why choke is provided in the centre of the tube light?
what iz second and fifth hormonics please explain
If we impress a dc voltage of 230 V on an unloaded 230 V, 50 Hz transformer it wi A give high secondary voltage B burn out C give secondary voltage as per K D none of these
What is Surge arrest? How it work?
We have two APFC panels in same station. I need how to connect CT in two APFC panels.can we take one CT in series connection or two separate CTs.
What are the different types of transformers present in the Transmission and Distribution system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)