What are the differents between Breaker & Contactor?
Answers were Sorted based on User's Feedback
Answer / iamdon
Basic difference between circuit breaker and contractor is
that
A circuit breaker can make,break and carry current in all
conditions i.e normal,overload and short circuit where as a
contractor can make,break and carry only in normal and
overloaded condition not in short circuit condition.
Also, Contractor are always backup by HRC fuse where as
there is no need of any backup in circuit breaker.
The frequency of operation of contractor is more than the
Circuit breaker
| Is This Answer Correct ? | 77 Yes | 12 No |
Answer / nishad
Above answer is almost ok. How ever I just add a little
with that.
Basic difference between circuit breaker and contractor is
That, A circuit breaker can make, break and carry current
in all conditions i.e normal, overload and short circuit.
It will protect the system from over load, Earth fault &
unbalance as well as it has different load & trip setting
and it don’t want any fuse back up. That was not inbuilt in
contactor. A contractor can make, break and carry only in
normal and overloaded condition not in short circuit
condition. Also, Contractor are always backup by HRC fuse
where as there is no need of any backup in circuit breaker.
For frequent operation, contractor is more efficient than
the Circuit breaker.
| Is This Answer Correct ? | 24 Yes | 4 No |
Answer / jinal kania d
A Circuit breaker is a simple switch,it can make,break and carry current in normal,overload and short circuit condition.,while Contactor has two types:Auxilary and Power contactor,it can make,break and carry only in overload and normal condition.It has back up protection compulsary by HRC fuses.,While there is no need of back up for circuit breaker.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / vipin singh
1.Circuit Breaker is used to protect the circuit and connected devices whereas contractor is used for controlling purpose.Thus, C.B. is a protective device whereas Contactor is a controlling device.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / rajesh ku sahu
Basic difference between circuit breaker and contractor is
That, A circuit breaker can make, break and carry current
in all conditions i.e normal, overload and short circuit.
It will protect the system from over load, Earth fault &
unbalance as well as it has different load & trip setting
and it don’t want any fuse back up. That was not inbuilt in
contactor. A contractor can make, break and carry only in
normal and overloaded condition not in short circuit
condition. Also, Contractor are always backup by HRC fuse
where as there is no need of any backup in circuit breaker.
For frequent operation, contractor is more efficient than
the Circuit breaker.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / salim
Contactor is prefered selection for smaller motor feeder as they are smaller in size compared with circuit breaker for the same rating , contactor is design for more frequent operation.contactor is sentitive to voltage variation compared to circuit breaker
| Is This Answer Correct ? | 0 Yes | 0 No |
circuit breaker is normally used as main incomer in mcc panel or outgoing feeder in power transfer feeder (PCC)
it can operate fully auto or mannualy it has property of tripping at over load
contector is normaly used as motor starter or control switchgear .
| Is This Answer Correct ? | 8 Yes | 27 No |
Answer / chander pal
circuit breaker used for higher rating as contactor used for
low rating equipment.. both operates in auto mode command
given by relay or manually.
| Is This Answer Correct ? | 8 Yes | 41 No |
what is the use of commutator in dc motor if we supply ac ? commutator is used to convert ac to dc.and it is used to arrange the flux in unidirectional in case of dc supply. if we give ac as supply to dc motor what is the use of commutator?
how electricity is generated an supplied till consumer
What is T’Q and X’Q and X’D ? and what is saturated as well as unsaturated ?
How will you Physically differentiate A.C and D.C motor?
For having nonavailablity of 10 Amps fuse, a lineman replace the same with 5Amps two strand, Do he correct ?
why AC signals are represented by sinusoidal waveform?WHY other waveforms not used for representation
Tan delta point in transformer to be earth or not?
How to determine the Power factor is Leading,Lagging & Unity ?.I don'thave any Meters.
Why water bubbles when D.C. Current is passed through it? Why not when A.C. Current is passed?
l&t switch FN 63 handle position can we change
why we are using star connection and delta connection? difference?
0.5,1,1.5,2.5,4.0.6.0,10,16 square mm electrical wires how much take maximum current in 50htz
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)