What are the differents between Breaker & Contactor?
Answers were Sorted based on User's Feedback
Answer / iamdon
Basic difference between circuit breaker and contractor is
that
A circuit breaker can make,break and carry current in all
conditions i.e normal,overload and short circuit where as a
contractor can make,break and carry only in normal and
overloaded condition not in short circuit condition.
Also, Contractor are always backup by HRC fuse where as
there is no need of any backup in circuit breaker.
The frequency of operation of contractor is more than the
Circuit breaker
Is This Answer Correct ? | 77 Yes | 12 No |
Answer / nishad
Above answer is almost ok. How ever I just add a little
with that.
Basic difference between circuit breaker and contractor is
That, A circuit breaker can make, break and carry current
in all conditions i.e normal, overload and short circuit.
It will protect the system from over load, Earth fault &
unbalance as well as it has different load & trip setting
and it don’t want any fuse back up. That was not inbuilt in
contactor. A contractor can make, break and carry only in
normal and overloaded condition not in short circuit
condition. Also, Contractor are always backup by HRC fuse
where as there is no need of any backup in circuit breaker.
For frequent operation, contractor is more efficient than
the Circuit breaker.
Is This Answer Correct ? | 24 Yes | 4 No |
Answer / jinal kania d
A Circuit breaker is a simple switch,it can make,break and carry current in normal,overload and short circuit condition.,while Contactor has two types:Auxilary and Power contactor,it can make,break and carry only in overload and normal condition.It has back up protection compulsary by HRC fuses.,While there is no need of back up for circuit breaker.
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / vipin singh
1.Circuit Breaker is used to protect the circuit and connected devices whereas contractor is used for controlling purpose.Thus, C.B. is a protective device whereas Contactor is a controlling device.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / rajesh ku sahu
Basic difference between circuit breaker and contractor is
That, A circuit breaker can make, break and carry current
in all conditions i.e normal, overload and short circuit.
It will protect the system from over load, Earth fault &
unbalance as well as it has different load & trip setting
and it don’t want any fuse back up. That was not inbuilt in
contactor. A contractor can make, break and carry only in
normal and overloaded condition not in short circuit
condition. Also, Contractor are always backup by HRC fuse
where as there is no need of any backup in circuit breaker.
For frequent operation, contractor is more efficient than
the Circuit breaker.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / salim
Contactor is prefered selection for smaller motor feeder as they are smaller in size compared with circuit breaker for the same rating , contactor is design for more frequent operation.contactor is sentitive to voltage variation compared to circuit breaker
Is This Answer Correct ? | 0 Yes | 0 No |
circuit breaker is normally used as main incomer in mcc panel or outgoing feeder in power transfer feeder (PCC)
it can operate fully auto or mannualy it has property of tripping at over load
contector is normaly used as motor starter or control switchgear .
Is This Answer Correct ? | 8 Yes | 27 No |
Answer / chander pal
circuit breaker used for higher rating as contactor used for
low rating equipment.. both operates in auto mode command
given by relay or manually.
Is This Answer Correct ? | 8 Yes | 41 No |
What is AVR in Generators and How is it working.
why field winding in synchronous machine connecting in star position?
Initially, when the input is not equal to the output — what type of response is this?
delta motor winding resistance I take normally single winding is 2.5, which value is came delta connection ie RY ?
Which capacitor is used in ceiling fans ?
how power can be saved using VFDs in detail explain
how many joints are allowed in underground HT cable of 1 KM
why ligthing is not available in switch yards?
what is meant by rotating magnetic filed
Piezoelectric materials serve as a source of:- A. Microwaves B. Ultrasonic waves C. Musical waves D. Resonant waves
1.wat is the purpose (or)function of regulator? 2.wat is the purpose of stabiliser?
Atwhat condition reverse power relay will act?