Basic difference between circuit breaker and contractor is
that
A circuit breaker can make,break and carry current in all
conditions i.e normal,overload and short circuit where as a
contractor can make,break and carry only in normal and
overloaded condition not in short circuit condition.
Also, Contractor are always backup by HRC fuse where as
there is no need of any backup in circuit breaker.
The frequency of operation of contractor is more than the
Circuit breaker

Is This Answer Correct ?    77 Yes 12 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

TRANSFORMERS WITH DC SUPPLY

1518


What is the settings of distance protection relay in 400 kv line

1184


What is FM200 Gas??Applications........

1914


what are the application of over current relay?

4218


What is superposition theorem?

695






difine electrical ballast in HPSVL

1559


what are the major & minor faults that occur in an inverter and in UPS ? And how to repair and resolve them ?

1825


What are the functions of different probes used in cro?

674


i need project topics along with circuit diagram in the electrical and electronics engg and also some websites regarding projets.

1569


i installed 100kva ups. what KVA genset they should provid in input side? plz any update formula or ans with reason.

1857


What do you mean by pull of electromagnet?

591


what is is the potential diffrence between two phase ?

5358


What is difference is of VSD,VFD,VSDS, are they the same as the direct current to control dc using above mention

990


how give earthing conection to household equipment?

1493


which cable is used for 15 Hp monoblock pump 3phase and service wire Distance is 210 feet please tell me cable size Armaured

1054