What are the differents between Breaker & Contactor?
Answer Posted / iamdon
Basic difference between circuit breaker and contractor is
that
A circuit breaker can make,break and carry current in all
conditions i.e normal,overload and short circuit where as a
contractor can make,break and carry only in normal and
overloaded condition not in short circuit condition.
Also, Contractor are always backup by HRC fuse where as
there is no need of any backup in circuit breaker.
The frequency of operation of contractor is more than the
Circuit breaker
Is This Answer Correct ? | 77 Yes | 12 No |
Post New Answer View All Answers
TRANSFORMERS WITH DC SUPPLY
What is the settings of distance protection relay in 400 kv line
What is FM200 Gas??Applications........
what are the application of over current relay?
What is superposition theorem?
difine electrical ballast in HPSVL
what are the major & minor faults that occur in an inverter and in UPS ? And how to repair and resolve them ?
What are the functions of different probes used in cro?
i need project topics along with circuit diagram in the electrical and electronics engg and also some websites regarding projets.
i installed 100kva ups. what KVA genset they should provid in input side? plz any update formula or ans with reason.
What do you mean by pull of electromagnet?
what is is the potential diffrence between two phase ?
What is difference is of VSD,VFD,VSDS, are they the same as the direct current to control dc using above mention
how give earthing conection to household equipment?
which cable is used for 15 Hp monoblock pump 3phase and service wire Distance is 210 feet please tell me cable size Armaured