how we can calculate cable size of 230v,1 hp single phase
motor ? panel to motor distance is 25 meter
Answers were Sorted based on User's Feedback
Answer / vaibhav v t
You can use 3 core x 1.5 sqmm copper cable.Upto 5 hp three
phase or single phase your can use this cable.
| Is This Answer Correct ? | 15 Yes | 6 No |
Answer / abokamal
cable design.
first we have to choose CB.
(I)load=P/(V*PF)......... assume pf=0.8
(I)=746/(230*0.8)=4.1 Ampere
(I)cb=(I)load *s.f (FASETY FACTOR)=4.1*1.25=5.1 Ampere
(I)cable=(I)cb/D.F (DERATING FACTOR)=5.1/0.8=6.33 Ampere
from catalouge you can select the cable according to the
current.
you have to see (volt/ampere/meter) to see the voltage drop
limit which according to +-5%
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / vipin
kamal is right ,after deciding the load current you ll have to consider the starting condition....
as per the IEEE regulations you ll have to consider 3 to 4 times the rated current as the starting current...as the rated current is coming around 6 amperes you can select a CB of 20A DP or SP. A 4sqmm cable will be std for the 1 hp pump.. you will have to verify with your supply company rules for the size of cable to be used for the designed value of circuit breaker.
| Is This Answer Correct ? | 3 Yes | 2 No |
What are the procedures followed for underground cable laying.....???
How to calculate amount of copper used in a motor (AC&DC), generator and transformer? Datasheet provides power rating and mass of the equipment....can we somehow use this available info.
why stone used in Transformer yard.
how does a tube light starter works?
In 3.5X150 Sq.mm cable what does 150 stand for outer dia or inner dia?
how to identified power tranfer line is how much KV????
Interchange 7 and 6 ,÷and× 36×7+4-7×3
difference between dol and rdol startors?
I have 2 Nos of 2500kVA 33/0.415V cast resin transformers. How to decide on ampere rating of HT Panel? Also advise me how many panel RMG i have to consider whether 4 panel ok?
Refernce currents are to be generated using refernce cueernts how can this be done??
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?
1.what to do if ferquency of any power system continue to decrease ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)