Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


1.what to do if ferquency of any power system continue to
decrease ?

Answers were Sorted based on User's Feedback



1.what to do if ferquency of any power system continue to decrease ? ..

Answer / sanju

u can bring the frequency to normal by decreasing the laod
shared by the generators. But i dont think any power system
engineer can afford to loose laod. The frequency can be
brought back to the noraml valsue after the following:-
1.make sure that the governor sets of all generators are
working fine.
2.make sure that that the droop characterstics of all the
governors connected are same.
3.make sure that there is no problem with prime mover side.
i hope this wl solve ur problem

sanjeev

Is This Answer Correct ?    10 Yes 1 No

1.what to do if ferquency of any power system continue to decrease ? ..

Answer / tarun aggarwal ymca

according to power system engineering the decrease in
frequency is because of load (as load increases speed
decrease) so Automatic control in power system detect this
change in speed and increase the steam or hydro flow to
turbine to counter balance it.

Is This Answer Correct ?    10 Yes 3 No

1.what to do if ferquency of any power system continue to decrease ? ..

Answer / nishant

Decrease the load of that system untill the frequency is in
limit

Is This Answer Correct ?    12 Yes 6 No

1.what to do if ferquency of any power system continue to decrease ? ..

Answer / sethar12

The problem is not that the frequency of the generator is
decreasing, but the problem is that when this frequency
decreases upto the underfrequency limit of the turbine (or
generator)(frequency bandwidths as given by manufacturer)
(generally at 48Hz). It must be noted that the turbine (or
generator) can run for some commutative duration in
different frequency bandwidths even below 48Hz, but it is
better to avoid in these bandwidths because turbine blades
may damage due to resonance.
The most effective solution is the load-shedding
(distribution side) (by asking the transmission network
controller).
Otherwise reducing the generator load manually.

Is This Answer Correct ?    2 Yes 0 No

1.what to do if ferquency of any power system continue to decrease ? ..

Answer / balaram mishra

I wii increase the roter speed of the generator, so that
the frequency will increase.

Is This Answer Correct ?    1 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

what is the consuption rating of motor in one day

1 Answers  


why table fans rotate clockwise .while ceiling in anti clockwise?

4 Answers  


Is it reuired to use house service barcket for 31/2 core 300 Sq.mm cable,if the distance between pole & shop is around 2 mtrs only or can I hang the cable with GI support in air? upto what size of cable GI serrvice btacket is necessary?

1 Answers   HAL,


Why grables are put in substation?

1 Answers  


why knee point voltage should be high in Ct for differential protection

1 Answers   NTPC,


How can we find out LT UG cable fault (size,from-4*25mm sqr to 4*300mm sqr)? How mani types UG cable faults?

0 Answers  


how to select the isolation tranformer for siemens 802dsl cnotroller

0 Answers   Siemens,


Why inverter rating in KVA?

3 Answers  


Why HRG and LRG used beside transformer, what is the purpose

3 Answers  


why we used to transmitt the power at higher voltage why not at lower voltage

8 Answers  


why the admittance matrix or y bus matrix of a large network is called sparse matrix?

3 Answers  


why we ht line cable size small rather than lt cable.

4 Answers   Aster Teleservices,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)