Capacitor panel CT is normally fixed on Y phase of the main
panel.why???
Answers were Sorted based on User's Feedback
no my friend,it depends on APFC relay,
1.in L&T make APFC relay ct is looped in R-phase.
2.in Sentron make APFC relay ct is looped in Y-phase.
3.in Sycon make APFC relay ct is looped in B-phase.
if you have any dout see all above relays wiring diagram.
For measuring PF APFC relay required any two phases & one CT sence on remaining phase from main PCC Phase.
Eg.(R-Y phase & BCT from Main Panel)
From--Rajendra Sawant
Miraj.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / zia
Good day friends
some time some of factory's lode not same in R,Y,B.
Example R=155amp, y=140amp, b=145amp which one we selected
for apfc relay for sense observing p-f . we are selected the
maximum amp flow phase.it can be R or Y or B. for good pf
rating.
so its a CT depends on the flowing amp of the phase
| Is This Answer Correct ? | 3 Yes | 1 No |
Thanks Zia Mam,For Sharing Additional information,but what about the manufacturing relay companys who manufacture the relay which has R,Y,B phase Selection of CT which i have mentioned in above answer,should we select our relay as per our Phase Load.
From-Rajendra Sawant
| Is This Answer Correct ? | 0 Yes | 1 No |
How to calculate the electrical load for a standard telecom BTS shelter and choose the DG set capacity for the same load?
What is ZCT? it operating principle and how is work with RCCB (residual current circuit breaker)?
Is it necessary to seperate the DG earth grid with Electricity Board earth grid for protecting the DG set. if yes why?
why we cannot protect 100% winding of an alternator by using differential protection?
the power loss in an overloaded line is mainly due to? a. resistance b. capacitance d. inductance d. none
What are the function of different components of servo motor?
Advantages of Induction Motors
how to select the surge suppresor for the 33 KV supply and what will be the rating, selection guide
which oil is used in transformer?
how terminal voltage increases when load is capacitive (leading pf load)? (explain practically what is happening, not using phasor diagram
How can we estimate Gen rotor current?
In CDG type IDMTL realy O/L , E/F, O/C which are used for out going feedrs,on R-phase o/c element, Y-phase , e/f elecment and on b -phase o/c element will be connected . Why the earth fault on center phase only, why not on other two phases?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)