Capacitor panel CT is normally fixed on Y phase of the main
panel.why???
Answers were Sorted based on User's Feedback
no my friend,it depends on APFC relay,
1.in L&T make APFC relay ct is looped in R-phase.
2.in Sentron make APFC relay ct is looped in Y-phase.
3.in Sycon make APFC relay ct is looped in B-phase.
if you have any dout see all above relays wiring diagram.
For measuring PF APFC relay required any two phases & one CT sence on remaining phase from main PCC Phase.
Eg.(R-Y phase & BCT from Main Panel)
From--Rajendra Sawant
Miraj.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / zia
Good day friends
some time some of factory's lode not same in R,Y,B.
Example R=155amp, y=140amp, b=145amp which one we selected
for apfc relay for sense observing p-f . we are selected the
maximum amp flow phase.it can be R or Y or B. for good pf
rating.
so its a CT depends on the flowing amp of the phase
| Is This Answer Correct ? | 3 Yes | 1 No |
Thanks Zia Mam,For Sharing Additional information,but what about the manufacturing relay companys who manufacture the relay which has R,Y,B phase Selection of CT which i have mentioned in above answer,should we select our relay as per our Phase Load.
From-Rajendra Sawant
| Is This Answer Correct ? | 0 Yes | 1 No |
what is the difference between LLL and LLLG fault ?
What will happen when we connect 2 bulbs in series between 2 phases
For overhead protection we use which transformer?
What is sequence network? Discuss all three types of sequence network.
Dear Sir I am living in Jaipur Rajasthan now I did complete my b tech degree in electrical engineering in 2012 Sir how I gate certificate of competency for electrical supervisor
what s a servo motor? how to control the servo motor? and its application, purpose of using?
What is High Frequency Grounding????
After synchronizing the running generator with grid, the avr getting tripped and the generator breaker also oettong tripped, before tripping the avr the pf meter of generator is showing leading pf please kindly give a suggestion to rectify this problem.
How Id and Ires are calculated in siprotech 7ut612 and abb trsfmr differential relay.what is the formula
How to calculate the load loss and no load losses of the power Transformer? i am having the following details : full load ct : in AMP HV :1676 ; LV:31.5 1800 KVA ;33KV/620 V for wind mill applications
how will you determine the short circuit capacity of a network
How to select the different contactors ( starter combination) for different AC motors? what about fuse cappacity 4 different motors too?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)