why nearly all the voltage levels are in the multiples of 11
like 3.3 ,6.6 ,33 ,11 kv.....

Answers were Sorted based on User's Feedback



why nearly all the voltage levels are in the multiples of 11 like 3.3 ,6.6 ,33 ,11 kv.......

Answer / nisarg d. patel

In India we provide an offset of 10% overload on the rated voltage level to easily accomodate the varying overload.So in accordance with this, 10 KV becomes 11, 60 KV as 66 and so on and so forth.But this convention is not followed in EHV above 500 KV where we follow the international transmission voltage levels like 730 KV, 1200 KV and so on.And also because the form factor is 1.11 so it becomes symmetric to have the transmission level as 1.1, 3.3 etc.

Is This Answer Correct ?    5 Yes 0 No

why nearly all the voltage levels are in the multiples of 11 like 3.3 ,6.6 ,33 ,11 kv.......

Answer / kolhe g j

Transformer changes the voltage level. Form factor for
sinusoidal AC 1.1 .

Is This Answer Correct ?    9 Yes 5 No

why nearly all the voltage levels are in the multiples of 11 like 3.3 ,6.6 ,33 ,11 kv.......

Answer / virendra joshi

correct is just because of form factor ,

Form factor = Rms value / Average value

Is This Answer Correct ?    4 Yes 1 No

why nearly all the voltage levels are in the multiples of 11 like 3.3 ,6.6 ,33 ,11 kv.......

Answer / brijesh

Because of form factor that is 1.1

Is This Answer Correct ?    4 Yes 2 No

why nearly all the voltage levels are in the multiples of 11 like 3.3 ,6.6 ,33 ,11 kv.......

Answer / ashi

its due to form factor

Is This Answer Correct ?    3 Yes 2 No

why nearly all the voltage levels are in the multiples of 11 like 3.3 ,6.6 ,33 ,11 kv.......

Answer / e.subash chandrasekar

Because of form factor 1.1

Is This Answer Correct ?    1 Yes 1 No

why nearly all the voltage levels are in the multiples of 11 like 3.3 ,6.6 ,33 ,11 kv.......

Answer / k.sahadevan nair

In India and other commonwealth countries, in the initial stage maximum generation voltage was 11 KV considering maximum available insulation rating. In order to step up this voltage,secondary of transformers should be 33 KV, 66 KV, 110 KV ,132 KV, 220 KV etc. So HT voltage of all step up/down transformers were fixed at multiples of 11. This has become a practice. This has nothing to do with form factor 1.11
When generation voltage is improved due to advancement of technology it has become difficult to change rating of all existing transformers. Naturally rating of transmission voltage of multiples of 11 continued and still going on. This is not applicable to EHT as this is a recent development and limited to certain countries only.

Is This Answer Correct ?    0 Yes 0 No

why nearly all the voltage levels are in the multiples of 11 like 3.3 ,6.6 ,33 ,11 kv.......

Answer / er. akil

at 11 kv level losses should be minimum
so.....

Is This Answer Correct ?    0 Yes 7 No

Post New Answer



More Electrical Engineering Interview Questions

what is function of reactor coil in Power factor correction panel

1 Answers  


what happen "when Dyn11 is parallel operation with Dyn1"?

9 Answers  


1.dg on load alarm/stop alarm... 2.dg on load. piu alarm alarm kaise chek krte hai

0 Answers   GTL,


how make megger test for control cable like 12c x 1.5mm and what it apply voltage and test timing details.

0 Answers  


What happens if we give the supply to the rotor of induction motor and make its terminal shorted?

2 Answers  






the problem faced on star or delta winding connection??

0 Answers  


If any HVDC line is going with positive & negative(the negative usually have return path of current with earthing electrode). Now the question is if this HVDC earthed electrode which is using as return path and earthed any nearby 400kv or 220kv AC substation equipments. which will be the impact of this on AC substation & its equipment, how severe may be this and what should be the minimum distance require between HVDC earthed electrode and AC substation equipments? It's really an high engineering level question...Dare to answer and increase your knowledge.

0 Answers   MEIL,


How can you calculate in detail the VA burden of current transformer used for Restricted earth fault protection? Please understand that the CT required here is Class PX or X. Also please show the calculations for knee point vtg, stabilizing resistor, magnetising current.

3 Answers  


Transformer how to maintaince a check b check c check d check

0 Answers   DIC India,


I need a formula to calculate the size of cable as per load but in the terms of length. Please Reply me as i search lot of sites but i did not get the answer.

0 Answers  


Do you know what is dry-out test in x'mer

0 Answers   First American Corporation, GPSC Gujarat Public Service Commission, Jindal,


without name plate detail of blower how we can find out the HP & Rpm ? the input voltage is 230v single phase

1 Answers  






Categories
  • Civil Engineering Interview Questions Civil Engineering (5076)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4445)
  • Electrical Engineering Interview Questions Electrical Engineering (16606)
  • Electronics Communications Interview Questions Electronics Communications (3915)
  • Chemical Engineering Interview Questions Chemical Engineering (1092)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (214)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (258)
  • Instrumentation Interview Questions Instrumentation (2992)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (123)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (0)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1378)