Answer / guest
removed link from actuator than fix back which condition
you need you will get other wise if you have HART base
change your counter (first read counter ) than increased
from potentio meter you can? i donot have idies about same
your positioner model but you can try
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / shabeerali
1. Reverse the potentiometer wire connection of position
transmitter.
2. Perform calibration. if required adjust zero and span .
then position transmitter gives reverse feed back
For direct feedback brown, red, orange.
for Reverse feedback orange, red, brown.
pls refer the manual
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kiraninst
If there is PLC/ Dcs then simply change the gain for reverse -1/ reverse action
| Is This Answer Correct ? | 0 Yes | 0 No |
How can you differentiate Instrumentation to Electrical?
what is function of vibration, and how is it work, explain with difination
1 Answers Bapco Bahrain Petroleum Company,
We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.
what is the daily job of an instrument commissioning supervisor
while i check zero check for dp flow transmitter some fluctuating came (0 to 458 kg/h) what is the reason?
WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD
whyvibration probe (bently nevada ) is set -10 volt for zero reference?
you are on site,the plant trips,you are approached by operations,what do you do?
Single acting ON-OFF valve. it is air to open. when sov energized , valve will be open, so during that if air fail then what will be the condition of valve ( open or close ) ???
why gray colour is choosing to all instrument panel.why not choosing other colour?
IF PLC POWER FAILURE THEN WHAT HAPPEN?
Whatis the reset ofset and control system in instrumentation
1 Answers Asyad International Company, CAE, Sugar Factory,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)