Answer / guest
removed link from actuator than fix back which condition
you need you will get other wise if you have HART base
change your counter (first read counter ) than increased
from potentio meter you can? i donot have idies about same
your positioner model but you can try
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / shabeerali
1. Reverse the potentiometer wire connection of position
transmitter.
2. Perform calibration. if required adjust zero and span .
then position transmitter gives reverse feed back
For direct feedback brown, red, orange.
for Reverse feedback orange, red, brown.
pls refer the manual
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kiraninst
If there is PLC/ Dcs then simply change the gain for reverse -1/ reverse action
| Is This Answer Correct ? | 0 Yes | 0 No |
what diffrence b/w plc s7200,300,400
Square root calculation for dp flow transmitter?
I am a electronics and instrumentation fresher trying for a job in IT sector. what do need to prepare for the interview?
steam drum level transmitter calibration procedure? with example?
please tell me how to convert double acting ytc positioner yt-1200 into single acting ytc positioner ?
how to change measuring units from mmwc to cubm/h in rosemount air flow transmitter with hart communicator fluke 744
Please any one can explain how to calibrate transmitter (smart) online with out remove from the container suppose it is interface level or static pressure level measurement we dont want to remove transmitter from the container mean it is running plant please give me detail. thankx brothers
please send the drdo exam paper
what is the procedure of belt scale calibration?
In case of Transmitter's(e.g.Ultrasonic Flow meter ) we have an normal practise of selction of upstream and downstream distance such as (20D and 5D ).can anyone please let me know whow to calculate "D" ?? i guess it refers to pipe thickness is t right ?
WHEN BOTH WIRES OF THERMOCOUPLE R SHORTED WHAT IS THE OUTPUT THE TEMP ARE 0,30,250,320
pt range is -45 psi to 45 psi.friends can you give answer with calculation and with linerity scale like 0%,25%,50%,75%& 100%?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)