Single acting ON-OFF valve. it is air to open. when sov energized , valve will be open, so during that if air fail then what will be the condition of valve ( open or close ) ???
Answers were Sorted based on User's Feedback
Answer / ahmed
the valve will close because air is fail then only one force is available the spring force the valve will follow spring power even if sov still energized
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / prem
Since SOV is energized theoretically valve will not close. To depressurize the actuator/valve SOV must de energize to open the vent port.
In Other whand,if pneumatic source become empty and no back up supply, Valve will close gradually due to loss of instrument air supply even though SOV is energized.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / kausar
If it has airlock then it will be remain same because at the time of pneumatic failure it locks the air automatically.generally now with control valve airlock,booster ,sov and air filter regulator are arranged in order to make the line safe
| Is This Answer Correct ? | 1 Yes | 1 No |
It will be remain in same condition if there is no air leakage and the valve is not spring loaded.
| Is This Answer Correct ? | 1 Yes | 1 No |
How to connect PLC to DCS ?
Can we measure pressure using differential pressure transmitter? If yes then how?
protection relay watchdog contact operation?
Why boiler chimney area oxyden sensor fixing?
What properties or parameters to be taken into consideration for protection while selection of Dcs controller.
what is diff between the centrifugal and reciprocating
What is force balance principle? State some of its’ advantages.
where the use of direct action control valve?
what is the path to communicate from profi to ofc.what is the means of communication.what is multi cire cable in ofc.
What is micromotion transmitter? What is the porpose of using this transmitter?
one rtd sensor which is connected at middle of distillation column where actual temp. is 100deg but when we tight this sensor at thermowell end it goes down to 90 deg & when remove from the thermowell(but sensor end dipped in well) showing actual reading, what is reason?
what is the Instrumentation?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)