what is back trip and re-trip in protection schemes? why
these two? define me the exact function of these two?
Answer / santosh kawade
Backup trip and re-trip are functions use for high voltage
overhead transmission line feeders.
In this system normally fault occurs are very short
durations like fault due to birds or due to fall of some
objects on transmission lines. In this case transmission
line trips due to fault but again breaker auto close after
certain duration (approx. 500 to 1000 milliseconds). But if
fault persist it again trips and will not close
automatically at second time.
Santosh kawade
9224 69 3116
Is This Answer Correct ? | 2 Yes | 9 No |
how to convert 1 phase power to 3phase power by using induction motor. . . .
what is the purpose of checking IR and Megger values in motor windings?
What are methods to avoid the inrush current at the time of starting of power transformer ?
Why we check only first column of root locus..?
why a pilot exciter is used in combination with the main exciter? why not only a main exciter is used for excitation to an alternator?
if we put a energy meter in 500 kvar capacitor bank ,then how much units show in energy meter per day.
How to find the maximum load, that can be supplied by a transformer.....
would the same effect be achieved by reversing the connection to one winding of the induction motor 3-phase?
How to reduce current flowing in neutral due to unbalanced load conditions in a three phase system.
WHY NOT CONSIDER PROTONS IN ELECTRICITY LIKE ELECTRIC CURRENT?
Can the efficiency of transformer be measured with the help of wattmeter readings taken at primary and secondary side? Support the answer.
how the arcing is made in ac electric arc furnace? ( between the three electrodes in any sequences or between the electrode & the charge(steel))