what is back trip and re-trip in protection schemes? why
these two? define me the exact function of these two?

Answer Posted / santosh kawade

Backup trip and re-trip are functions use for high voltage
overhead transmission line feeders.

In this system normally fault occurs are very short
durations like fault due to birds or due to fall of some
objects on transmission lines. In this case transmission
line trips due to fault but again breaker auto close after
certain duration (approx. 500 to 1000 milliseconds). But if
fault persist it again trips and will not close
automatically at second time.

Santosh kawade
9224 69 3116

Is This Answer Correct ?    2 Yes 9 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Why are the laminations insulated from each other?

638


How much weight an electrical engine can pull??

1614


can you any one give exact mathematical relation between AC current and DC current?

1384


During FEED, you will have all the information with regards to cable. How will you calculate the MTO for MV and LV Cables? what are your considerations?

2020


kVA rating of ordinary transformer is increased when connected as an auto transformer because A transformation ratio increased B secondary voltage increased C energy is transferred both inductively and conductively D secondary current increased

2141






Define average demand?

894


if an insulated power and control cables of a running gas diesel gensets laid direct in an open trench i.e, trench bed is not rcc of a power house in which rain water, spillage water alwas exists and all power control cables remains submerged even when gas gensets of 480 kw each runningin on load. These power &control cables runs from power house to switchgear room through these trenches in which water remains most of the time. pl explain its merit & de-merit

1401


What should be the magnetic balance test values for a 3 phase delta/star connected single primary dual secondary winding transformer (90 MVA / 2 X 45 MVA TRANSFORMER)

1405


how dia of wire and angles are calculated for overhead shielding wire to protect substation equipment from lightening strokes???

1564


HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT SWITCH BOARD,MLDB,ACB,BUSBAR,ETC...?

3477


Write the force balance equation of ideal dashpot element.

835


In india, according to trade theory above 5 HP motor reqired star delta starter. But we R connect 11 KV motor with 14MW in Direct to line ( With VCB starter combination) Can U Guess, How it is possible ?????

1595


How to know any size of cable if there are not written on cable? Answer must be theurical not by experience.

1668


What is Load sharing of Transformer ?

1540


how we select ac fuse rating of an power inverter???

1382