i am BSEE student, my project study is to synchronize the
generator of an hospital, it have a one 313KVA standby-power
diesel gen.,and three 100kva transformer.The generator
system is operated manually and no ATS or UPS. one more new
building is being build so the transformer will be upgrade
to a higher vale.
1)how i can connect the new gen. to the old gen. and to the
synchronize panel?
2)what is the new gen. to be buy?(rating, etc.)
These is my title: To synchronize the generator system of
the ____ Hospital.
Anyone have a good title?
Thanks.
Answer / kpd
What are you synchronising to? Are you synching to another
generator for load sharing or synching to the mains?
If mains are you synching for export or are you back
synching for bumpless (or no break) return to mains on
restoration? Arew your site transformers fed from the same
ring? If not you'll have all kinds of issues.
Either way the big thing to get in there is your very
expensive G59 testing and approvals before any DNO will
allow any synchronisation. Also the protections in your
generator control to prevent any out of parallel closing to
mains (makes a BIG mess) check syncs etc etc
| Is This Answer Correct ? | 1 Yes | 2 No |
diff.between servo motor and ac motor
What is the implications when 600 hp motor is started when the unit is running with Transformer of capacity 1500 KVA and DG set of 1000kva
What is the height of DA, DAL, DB, DC & DDE tower?
Which test will be more severe for VCB?
active elements are those which are capable of
how to find out capacitor range?
Why the symbol of register is "zig zag"
What is derating?, Why it is necessary, it is same for all means for drives, motors,and cables.
a bulb of 100W and anather bulb of 200W , rated supply voltage 230v.when supply voltage is reduced to 100v,which bulb will give more light? and why with calculation?
why we are using2 wave trap in a feeder?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
1)how to reduce the value of tan delta of trasformer and CB,bushing,CT&PT,CVT ? 2)how to reduce the resistance of CB contact and its operating time? 3)plz.....send me the project report on conditioning and monitoring of substation equipment on my email id (gusaiyogendra03@gmail.com)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)