if the t/c o/p is 4-20mv then how plc recognize it
because we are dealing with the 4-20ma in the
plc ????????????????
Answers were Sorted based on User's Feedback
Answer / arindam
why we require a 4-20 mamp for transmission? the main reason
behind it because of electro magnetic interference the
voltage can get interfered very easily and we can't get our
desired o/p value.when we are using 4-20 mamp this problem
is solved but since, PLC is a digital device it can
understand mainly High=5V or low so we design the sink to
have a resistance as high to get the desired voltage, the 4
mamp is also helpful to power the electronics at the
transmitter end. to have a 4-20 mv instead can firstly :
cause em interference and secondly we need to have a
continuous level monitoring for different voltages...which
can increase the size of PLC . Also because of change of
impedance at the transmission line the voltage can drop
below 4 volt ocassionaly then loop powering of field
instrument will not be possible.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / biswarup das
There is different module in a PLC . Out of which one is T/C
module if you connect the o/p of T/C directly to this module
of PLC , then the PLC will recognise it.
T/C module is not inbuilt we have to select it seperately.
There are many modules like this such as RTD module, 0-10
volt module etc.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / guest
we will convert mV in to the ma....by connecting resistance
in parallel
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / sreekanth
standard thermocouple output is 0 to 10 mV. There will be 4-
20MA converter either in DCS in the field(Transmitter)as
the modules will accept only 4-20 MA output.
| Is This Answer Correct ? | 1 Yes | 5 No |
What is Alpha & Beta fctors related to Orifice Plate & its relation with flow?
A pressure differential gauge type of instrument has a manifold with 2 isolation valves (hp and lp),2 vents(1 each for hp and lp) and 1 equalizing valve. Determine the position of each valve(either fully closed or fully open) when troboulshooting to: 1. zero the transmitter. 2. determine if there is a block in the impulse line. 3. determine if the gauge is functioning properly. The process fluid is water.
what is different between modbus and serial link? please could anybody give right answer.
what is hot loop check and cold loop check.
3 Answers Bapco Bahrain Petroleum Company,
need to calculate flow rate with the help of dp range and orifice bore dia and size. range is 0 to 400 inwc and orifice size is 12 inch 150 # rf and bore dia is 7.180 inch. need to calculation for flow rate
What are the different types of temperature sensors and the principle they work on?
Boolean algebra
Control valve Flow characteristic. How the equal percentege curve form?
warning lamp does not light, but it does light when the wire from the lamp going to the sending unit is grounded (the part that plugs into the sending unit) what does this indicate)?
How to O2 analyzer works?
why we use 250 ohms across HART CALIBRATOR DURING CALIBRATION OF TRANSMITTER
what is the difference between SMART and tipical transmeter ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)