if the t/c o/p is 4-20mv then how plc recognize it
because we are dealing with the 4-20ma in the
plc ????????????????

Answer Posted / biswarup das

There is different module in a PLC . Out of which one is T/C
module if you connect the o/p of T/C directly to this module
of PLC , then the PLC will recognise it.

T/C module is not inbuilt we have to select it seperately.
There are many modules like this such as RTD module, 0-10
volt module etc.

Is This Answer Correct ?    5 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Please can anybody help for control valve sizing step by step procedure?

1647


what is span value and zero ? and how set ?

1073


how to calibrate electro pneumatic positioner 8013 mil controls ltd ?gsr

7460


Area classification, Equipments, Gas groups, temperature classification, Ingress protection, Fire Extinguishers.

1505


How flow can be measured with dp?

677






What is difference of fanuc alpha series 16i and 18i controller.also what is differnce betn TC and MC controller

1885


what is exact time to study dcs and plc cources

1566


Calculate the maximum pressure drop that can be allowed to occur across a control valve, so that we can prevent cavitation / flashing from occurring. Use the following formula: Δ P allow = Km (P1 – PvapourA) where, Δ P allow - the maximum allowable differential pressure for sizing purposes, or terminal pressure drop; Km- the valve recovery coefficient from the manufacturer’s catalogue; P1 - absolute inlet fluid pressure; PvapourA - absolute fluid vapour pressure at the inlet temperature; Use Atmospheric pressure = 101.3 kPa, P1 = 1200 kPa(g), PvapourA = 4 kPa, KM = 0.72

1656


how to calculate orifice sizing? and tell me if pipe size bet 50mm t0 200mm then we can use pipe flange??? and above 250mm pipe size should i use D & D/2 Flange? is it right or wrong?

1500


what is easiest way to read STL language in PLC?

2664


What denotes the 5/8mm in the 3300XL 5/8mm proximitor probe?

991


Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer

4178


I want to know the questions asked in ONGC interview(after being selected in the written exam) for Instrumentation branch.Kindly help.

1767


Who to difference between analog in & analog out in dcs?

1032


What is difference between differential pressure & delta pressure?

619