why 1 to 5 vdc is used for output measurment
Answers were Sorted based on User's Feedback
Answer / kandan
since we use 4 to 20ma transmission signal,the voltage drop
at the o/p is 1 to 5V.
In the O/P 250 ohm resistance is used.So when the signal is
4ma then 4*250=1V
when the signal is 20ma,then the O/P is 20*250=5V.
| Is This Answer Correct ? | 46 Yes | 4 No |
Answer / ranjit mallick
Because upto 1 volt and 4ma the signal can be trigered due
to some earth leakage, bias malfunction, noise signal,
small magnetic interferance etc.Hence it is used as lower
tolerance to avoid unwanted triggering of the instrument
and can be termed as floating output.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / abdul hakkem
for analog arithmetic calculation can be done only by Voltage, thats way 4-20 mA is converted & taken as a voltage output
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajesh
Because of the Burden resistance of the Instruments/Load of
PLC are normally 250ohms
So Its Corresponding we will get 1 to 5V
| Is This Answer Correct ? | 6 Yes | 12 No |
who's take first position in process in the timing of new installation flow transmitter and control vavle. give the answer with logical trick.
Questions on flow meters,few questions on HART protocol,
what does the ratio 800-400-300-200/1-1-1-1-1 in the specification of current transformer indicates?
why 4ma show higher zero ? i have transmiter flow renge 0-1000 m3/h but 4 ma show in monitoring 200 m3/h and 20 ma show 1000 m3/h i want when 4ma show 0 m3/h and 20ma 1000m3/h
what should be minimum length and size of impulse line for steam flow orifice and feed water orifice? asked by sanjay parihar
Range 8 Kg/cm2, alarm to be set at 2Kg/cm2, at wat pressure reciever switch to be calibrated? justify the ans?
What is difference between scada and virtual instrumentation?
what is the difference between SCADA and DCS?
what is function of DCS , and how is it work , explain with difination
1 Answers Bapco Bahrain Petroleum Company,
Please explain for RS 485 & RS 232 communication
Which type of diaphragm use in costic line, dm water line, natural gas line, oil line?
the pump holds on run indication into the dcs and filed local control panel remote push button condition operaton wrong like when the push button pushing conditions the pump is off and the push button release condition the pump is on totally opposite condition . And control room inside give the stop command into dcs just 1secon relay engage and again normal condition. How can I slove
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)