Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


We use ungrounded DC system (220V/110V) for control and
protection system in substations etc. Suppose we have long
2 core DC cables running from our DCDB in control room to
the load (length of around 2 to 3 km). Do we need to
protect these long DC cables from earth leakages or not? If
yes how?

Answers were Sorted based on User's Feedback



We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / krishna

Usage of differential relay for 220V/110V is not an
economical idea. Differential protection is the costlier
protection. DC Cables should be protected from earthleakage
bacause of which voltage differences occurs and trips the
circuits due to large variations. I suggest to go for
MCCB/MCB of required rating which trips the circuit when
earth leakage occurs.

Is This Answer Correct ?    5 Yes 1 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / ch.shankar

use dc differential relay or poles insulation monitor which
will help u to measure leakage

Is This Answer Correct ?    5 Yes 3 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / k.prakashchandra

Normally dc earth fault locater is employed. If one polarity
shows earth fault there is nothing to panic.Heavy fault
current occurs if the other polarity also develops fault. If
tripping is provided ,the protection may get lost.

Is This Answer Correct ?    1 Yes 0 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / sanjay choubey aditya electron

You can use online Insulation Monitor Bender Germany make
products for above requirement you can also see website for
more details: www.bender.org many Steel Plant, Substation
are using Bender products same applicaton.

Is This Answer Correct ?    1 Yes 0 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / sanjay

You can use online Insulation Monitor Bender Germany make
products for above requirement you can also see website for
more details: www.bender.org many Steel Plant, Substation
are using Bender products same applicaton.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Which motor has high starting torque

2 Answers   Greenko,


In Delta connected capcitor bank, One bank failed due to some problem. Can we connect Open delta capacitor bank to 3 phase motor. The motor voltage rating is 6.6KV. IF yes what changes will happen?

1 Answers  


i need project topics along with circuit diagram in the electrical and electronics engg and also some websites regarding projets.

0 Answers  


if you asked to choose a ckt breaker from MCB & MCCB for 32A which one will be best and why??

7 Answers  


how to calculate the breaking capacity of different breakers.

0 Answers   UltraTech,


what is static frequency converter?what is the function...of sfc...?

0 Answers   L&T,


Is the force acting between two parallel conductors of infinte length carrying AC of frequency 50Hz remians constant with respect of time? If not then what would be the frequency of the force acting?

1 Answers  


how to select a circuit breaker?

24 Answers   ABB, BARC, TCS,


what is the role of energy meter in distribution system ?

0 Answers  


why and how voltage sharing in transformer, during magnetic balance test ?

0 Answers   ME,


TO operate transformers in parallel, vector symbol of the both should be same.If one transformer name plate is not there, how can we conclude that whether the transformer is having the same vector symbol or not?

4 Answers  


What are safety features considered for Lifts during emergency?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)