Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


We use ungrounded DC system (220V/110V) for control and
protection system in substations etc. Suppose we have long
2 core DC cables running from our DCDB in control room to
the load (length of around 2 to 3 km). Do we need to
protect these long DC cables from earth leakages or not? If
yes how?

Answers were Sorted based on User's Feedback



We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / krishna

Usage of differential relay for 220V/110V is not an
economical idea. Differential protection is the costlier
protection. DC Cables should be protected from earthleakage
bacause of which voltage differences occurs and trips the
circuits due to large variations. I suggest to go for
MCCB/MCB of required rating which trips the circuit when
earth leakage occurs.

Is This Answer Correct ?    5 Yes 1 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / ch.shankar

use dc differential relay or poles insulation monitor which
will help u to measure leakage

Is This Answer Correct ?    5 Yes 3 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / k.prakashchandra

Normally dc earth fault locater is employed. If one polarity
shows earth fault there is nothing to panic.Heavy fault
current occurs if the other polarity also develops fault. If
tripping is provided ,the protection may get lost.

Is This Answer Correct ?    1 Yes 0 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / sanjay choubey aditya electron

You can use online Insulation Monitor Bender Germany make
products for above requirement you can also see website for
more details: www.bender.org many Steel Plant, Substation
are using Bender products same applicaton.

Is This Answer Correct ?    1 Yes 0 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / sanjay

You can use online Insulation Monitor Bender Germany make
products for above requirement you can also see website for
more details: www.bender.org many Steel Plant, Substation
are using Bender products same applicaton.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Which types of following motors are most efficient?

0 Answers  


you are a electrical student, why are you coming for software job.

4 Answers   TCS,


what is the difference between Resin Cast CT and Oil cooled CT?

1 Answers  


I am in last year of Engineering.I want to apply for ONGC on GATE based score.They require Certificate of Competency as Electrical Supervisor.How can i get this certificate so I can apply for AEE(ELECTRICAL) in 2016

1 Answers   ONGC,


In power transformer YnD0 Vector Group is possible or not? if possible, what will be the vector diagram and what are the conditions?

2 Answers  


what's the activities of reactor in Buchholz relay?

1 Answers   Yahoo,


differentiate between remote backup relay and local backup relay?

1 Answers  


Hi everyone. Some Generators uses 3-Pole breakers with extra contactors for Neutral. Some uses 4-Pole. Why so? What is the idea behind this? Thanks in advance for the solution. Kr.

0 Answers  


what is the control circuit for operating the clean room air shower

0 Answers   L&T,


What is the technical difference between On delay timer and a Star delta timer?

0 Answers   Roche,


3 shows a 415 V, 3-phase generator supplying a 3-phase 415/110 V transformer. Draw the individual and combined impedance diagrams to a base of 10 kVA. Determine the system fault kVA and the fault currents at the 415 V and 110 V busbars for short circuit faults on the transformer input or output terminals. Work in p.u. values of impedances.

0 Answers  


Why winding temperature ct placed in B-Phase of the transformers?? 

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)