We use ungrounded DC system (220V/110V) for control and
protection system in substations etc. Suppose we have long
2 core DC cables running from our DCDB in control room to
the load (length of around 2 to 3 km). Do we need to
protect these long DC cables from earth leakages or not? If
yes how?
Answers were Sorted based on User's Feedback
Answer / krishna
Usage of differential relay for 220V/110V is not an
economical idea. Differential protection is the costlier
protection. DC Cables should be protected from earthleakage
bacause of which voltage differences occurs and trips the
circuits due to large variations. I suggest to go for
MCCB/MCB of required rating which trips the circuit when
earth leakage occurs.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / ch.shankar
use dc differential relay or poles insulation monitor which
will help u to measure leakage
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / k.prakashchandra
Normally dc earth fault locater is employed. If one polarity
shows earth fault there is nothing to panic.Heavy fault
current occurs if the other polarity also develops fault. If
tripping is provided ,the protection may get lost.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sanjay choubey aditya electron
You can use online Insulation Monitor Bender Germany make
products for above requirement you can also see website for
more details: www.bender.org many Steel Plant, Substation
are using Bender products same applicaton.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sanjay
You can use online Insulation Monitor Bender Germany make
products for above requirement you can also see website for
more details: www.bender.org many Steel Plant, Substation
are using Bender products same applicaton.
| Is This Answer Correct ? | 0 Yes | 0 No |
Which types of following motors are most efficient?
you are a electrical student, why are you coming for software job.
what is the difference between Resin Cast CT and Oil cooled CT?
I am in last year of Engineering.I want to apply for ONGC on GATE based score.They require Certificate of Competency as Electrical Supervisor.How can i get this certificate so I can apply for AEE(ELECTRICAL) in 2016
In power transformer YnD0 Vector Group is possible or not? if possible, what will be the vector diagram and what are the conditions?
what's the activities of reactor in Buchholz relay?
differentiate between remote backup relay and local backup relay?
Hi everyone. Some Generators uses 3-Pole breakers with extra contactors for Neutral. Some uses 4-Pole. Why so? What is the idea behind this? Thanks in advance for the solution. Kr.
what is the control circuit for operating the clean room air shower
What is the technical difference between On delay timer and a Star delta timer?
3 shows a 415 V, 3-phase generator supplying a 3-phase 415/110 V transformer. Draw the individual and combined impedance diagrams to a base of 10 kVA. Determine the system fault kVA and the fault currents at the 415 V and 110 V busbars for short circuit faults on the transformer input or output terminals. Work in p.u. values of impedances.
Why winding temperature ct placed in B-Phase of the transformers??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)