Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


We use ungrounded DC system (220V/110V) for control and
protection system in substations etc. Suppose we have long
2 core DC cables running from our DCDB in control room to
the load (length of around 2 to 3 km). Do we need to
protect these long DC cables from earth leakages or not? If
yes how?

Answers were Sorted based on User's Feedback



We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / krishna

Usage of differential relay for 220V/110V is not an
economical idea. Differential protection is the costlier
protection. DC Cables should be protected from earthleakage
bacause of which voltage differences occurs and trips the
circuits due to large variations. I suggest to go for
MCCB/MCB of required rating which trips the circuit when
earth leakage occurs.

Is This Answer Correct ?    5 Yes 1 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / ch.shankar

use dc differential relay or poles insulation monitor which
will help u to measure leakage

Is This Answer Correct ?    5 Yes 3 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / k.prakashchandra

Normally dc earth fault locater is employed. If one polarity
shows earth fault there is nothing to panic.Heavy fault
current occurs if the other polarity also develops fault. If
tripping is provided ,the protection may get lost.

Is This Answer Correct ?    1 Yes 0 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / sanjay choubey aditya electron

You can use online Insulation Monitor Bender Germany make
products for above requirement you can also see website for
more details: www.bender.org many Steel Plant, Substation
are using Bender products same applicaton.

Is This Answer Correct ?    1 Yes 0 No

We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Supp..

Answer / sanjay

You can use online Insulation Monitor Bender Germany make
products for above requirement you can also see website for
more details: www.bender.org many Steel Plant, Substation
are using Bender products same applicaton.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Is it legal of using 3 phase motors in 2 phase in Tamilnadu?

2 Answers  


what is sinwave ups

1 Answers   Exide,


why chock were used in old tubelights but are not newest tubelights?

0 Answers  


How to prepare electrical preventive maintenance plan & shedule of machine tools.

2 Answers  


why two fuses are used in battery charging room?one in positive line and the other in negative line?do any DC system require two fuses?

1 Answers   HPCL,


what is diffrence between neutral and earth wire

23 Answers   Bhel, Esab, MTNL,


bit confused - am i correct in thinking that to determine line to line voltage in a star config 110v 3 phase 4 wire distribution system i would use a voltmeter? I have a circuit configured as an unbalanced load, consisting of three incandescent lamps (1x40w, 1x60w, 1x100w - all 110v rated)connected in a star configuration to a 110v 3 phase 4 wire distribution system. I want to find out what types of meters i would use to obtain: a) each line to line voltage b) the line to neutral voltage across each load c) current flowing in each line and load d) current flowing in the neutral conductor e) power supplied to the loads im assuming i would be using ammeters in series along each line and voltmeters in parallel across each line to neutral? Also how could i predict these meter readings before taking them and with which formulae? Any help would be greatly appreciated A.

1 Answers  


Why is negative feedback invariably preferred in closed loop system?

0 Answers  


KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these transformer has big size? Give reason

4 Answers   Suzlon,


how can we calculate air compressure capacity

1 Answers  


in 3 phase induction motor resistance value is how much

1 Answers  


What is mean by sinewave.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)