Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


When i went to a interview the interviewer ask me a
question for that i cant able to answer him if anyone knows
answer me
How will you design a capacitor bank for a plant? if my p.f
is 0.6 i have to improve it to 0.9 or 1 what kind of steps i
have to do? and is there any formula for calculating this?

Answers were Sorted based on User's Feedback



When i went to a interview the interviewer ask me a question for that i cant able to answer him if..

Answer / joel q.

You must add a capacitor bank. you can determine the size
of the capacitor to be added using the following formula.

KVAR = KW*Tan((arccos0.6) -(Arccos0.9))

Is This Answer Correct ?    7 Yes 0 No

When i went to a interview the interviewer ask me a question for that i cant able to answer him if..

Answer / raju

to improve powerfactor only capacitor banks should be used
but not inductor as capacitor having leading pf which wil
reduces reactive power and improves pf

Is This Answer Correct ?    3 Yes 3 No

When i went to a interview the interviewer ask me a question for that i cant able to answer him if..

Answer / kaushik

if we are talking for 0.6 pf laging to 1 pf then we require
a capacitor bank.
the rating of the bank will be=v*i*sin(angle) in vars
angle=cosinverse(0.6).
if we are talking for 0.6 pf leading to 1 pf then we require
a inductor bank.
the rating of the bank will be=v*i*sin(angle) in vars
angle=cosinverse(0.6).
v=supply line voltage.
i=line current.

Is This Answer Correct ?    0 Yes 0 No

When i went to a interview the interviewer ask me a question for that i cant able to answer him if..

Answer / amrish sharma

just calculate total load of plant,,, then use capacitor 30
percent rating of total load,,, example if you have hunderd
ampere load then use 30Kvar capacitor,,,

Is This Answer Correct ?    1 Yes 2 No

When i went to a interview the interviewer ask me a question for that i cant able to answer him if..

Answer / jothi

If power factor must be improved from lower value to higher
value then capacitor or inductor banks must be added....

Is This Answer Correct ?    4 Yes 7 No

When i went to a interview the interviewer ask me a question for that i cant able to answer him if..

Answer / saravanakumar

If you want improve your power factor, you should provide a
capacitor bank.The rating of the bank is 1/3 rd of the
transformer ratings.

Is This Answer Correct ?    1 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

why high speed tripping relay will be used in tripping circuit why not normal relay

0 Answers  


cleat wiring system is used at

2 Answers  


If we says that current is flow only when there is closed path & neutral work as a return path for the same. Then how circuit is closed in three phase as no neutral available ??

1 Answers   Nimbus Harbor Facilities Management,


How to calculate flow of water delivered by pump when pressure & size of pipe line is given

0 Answers   Knight Frank,


if we give connection of 100watts bulb through a single phase energy meter ,the disc of a meter rotates why it happens?

1 Answers  


Where the excitation is given either stator or rotor in actually in power plants?

13 Answers  


to hook up ten 50 amp rv pedastels at a lenth of 600 feet from the service what size will my service need to be and the size of wire will I have to run to each pedastel in series??????

0 Answers  


what is vector surge & vector shift? we have 25.3 MW(11kv) generator & 11kv/132kv transformer, connected with with 132 kv grid.vector surge relay is tripping frequentaly.what is permissible maximum limit for this.

3 Answers  


how the testing of CT OF 400/200/100 done in33/11 kv s/s

1 Answers   Reliance,


expalanation for 5p10 class.

6 Answers  


what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks

0 Answers   ABC,


Is any AC drive(VFD) had a feature of DC injection braking? if available please mention the detail. i.e drive can supply braking torque when the motor in idle state.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)