Answer / thowsif_emerson
An isolation transformer is a transformer, often with
symmetrical windings, which is used to decouple two
circuits. An isolation transformer allows an AC signal or
power to be taken from one device and fed into another
without electrically connecting the two circuits. Isolation
transformers block transmission of DC signals from one
circuit to the other, but allow AC signals to pass. They
also block interference caused by ground loops. Isolation
transformers with electrostatic shields are used for power
supplies for sensitive equipment such as computers or
laboratory instruments.
In electronics testing, troubleshooting and servicing, an
isolation transformer is a 1:1 power transformer which is
used as a safety precaution. Grounded objects near the
device under test (desk, lamp, concrete floor, oscilloscope
ground lead, etc.) may be at a hazardous potential
difference with respect to that device. By using an
isolation transformer, the bonding is eliminated, and the
shock hazard is entirely contained within the device.
Isolation transformers are also used for the power supply
of devices not on ground potential. A well-known example is
the Austin transformer for the power supply of air-traffic
obstacle lamps on mast radiators insulated against ground.
Isolation transformers are commonly designed with careful
attention to capacitive coupling between the two windings.
This is necessary because excessive capacitance could also
couple AC current from the primary to the secondary. A
grounded shield is commonly interposed between the primary
and the secondary. This greatly reduces the coupling of
common-mode noise present on supply conductors.
Differential noise can magnetically couple from the primary
to the secondary of an isolation transformer. This requires
other measures, such as a filter, to block differential
noise from the secondary of an isolation transformer.
| Is This Answer Correct ? | 13 Yes | 1 No |
How to calculate main incomer rating of APFC Panel ? Let's say i want to find main incomer for 11kV, 1000kVAR Panel.
Please tell me what is the difference between online UPS & OFF line UPS?
why the excitation is necessary to produce the reactive power
which mm cable should be used for 1.hp immersible pump motor for the distance of 330 metres?
Why lightning arrester blast in rainy day?
1 Answers Eco Cement, Mahaveer, MBDL,
is it necessarry to charge the battery of ups always??
WHAT SHOULD BE THE BEST CURRENT RATINGS (PRIMARY / SECONDARY)FOR A CT INSTALLED AT THE INCOMING 11KV PANE? WILL IT BE CALCULATED ON THE BASES OF MAXIMUM DEMANT VALUE OR ON SUM OF ALL TRANSFORMER'S KVA? NOMALLY MAX DEMAND REPRESENT THE MAXIMUM OPERATING LOAD OF THE PLANT AND TOTAL KVA OF (SAY 5 NUMBERS TRANSFORMERS) REPRESENT THE CONNECTED LOAD. WHICH i.e. MAX DEMAND KVA OR CONNECTED KVA ARE BETTER TO USE FOR CT CURRENT CALCULATION? PLEASE ANSWER.
List examples of voltage source?
hi engineers,if suppose distribution is going to two diff village mistakenly they r interchange the neutral of twowhat happen?
what do you mean by PF correction. A motor is rated at 15 kw,415 volts, 0.7 pf and eff of 0.92. The powerfactor is improved to 0.98 by adding capacitors at the bus. calculate the current drawn by motor under full load condition before and after pf correction
in alternator permanent magnet generator is also connected on the alternator shaft,then y that PMG voltage is very low as compared to alternator?
Define delay time.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)