What is the difference between XLPE & FRLS cables? Is FRLS
cables is a type of XLPE cable or both r different?
Answers were Sorted based on User's Feedback
Answer / ramesh chandra dhing
XLPE-crosslinked polyethylene.
FRLS-fire retardent low smoke.
FRLS: is a property and its add on feature which is
introduced during manufacturing of cable on demand by which
we can use these cables in fire prone areas and in case of
fire these cables dose not catch fire upto prescribed temp.
level however XLPE is a type of insulation of cable which
improves current carrying capecity of conductor by 5~10%.
| Is This Answer Correct ? | 78 Yes | 4 No |
Answer / rahul sharma
XLPE is an INSULATING Material while FRLS is a Property
which we seeks in Outer Sheath Part of the Cable. Hence, we
can not compare the Both.
If we are talking about Normal XLPE Cable v/s FRLS XLPE
Cable, then please NOTE that the FRLS XLPE Cables are used
in the Fire Prone Area like Hospitals, Electrical Shops,
Fire Crackeer's Shop.
FRLS Properties:
1. Oxygen index: 29 min, when tested as per ASTM D 2863.
2. Temp. Index: 250°C min,when tested as per ASTM D 2863.
3. Smoke density rating:60% Max,when tested as per ASTM D
2843.
4. Acid Gas generation: Maximum 20% by weight, when tested
as per IEC 60754-1.
5. Flame retardant test as per IEC 60332-3 Cat C will pass.
Above are the properties for FRLS Cables.
** For More information Call me at
rahul.ravincables@gmail.com **
| Is This Answer Correct ? | 51 Yes | 1 No |
XLPE means Cross Linked Poly ethylene cables which may be
FRLS or ordinary. FRLS are fire resistant cables which are
used at the locations which are more prone to fire.
| Is This Answer Correct ? | 26 Yes | 12 No |
Answer / vinod bisht
actually both are different material where FRLS are used in
fire pron areas and XLPE elsewhere.
XLPE-crosslinked polyethylene.
FRLS-fire retardent low smoke.
| Is This Answer Correct ? | 17 Yes | 9 No |
XLPE means Cross Linked poly Ethylene these cables we are
using in Transmission the AC Supply like 440V
FRLS : Flame Retardent Low Smoke These cables we are using
in Fire panel wiring and smoke detectors wiring and FM 200
wiring and for access contol wiring also
In these cables we transmit DC Supply of 12v to 24V and
size of 0.75 to 1.5Sqmm with steel armoured
| Is This Answer Correct ? | 14 Yes | 15 No |
Which type of control system is expensive — closed loop or open loop?
Which type of alternator used in power station?
what are the differenc between vcb and sf6 breakers
why core is useful for a transformer ?and also in its operation ?
Define what is the function of anti-pumping in circuit breaker?
What is the difference between circuit breaker and isolator
If genrator not build up voltage , How u can Manually Excite ?
What will happen if we give the 3 phase supply to the rotor of slipring induction motor?
What is drain current of static relay?
what reason of line current and phase current in star connection and line current and phase current not equal in delta connection?
how to calculate power factor rating according to load? please give the answer in simple language, i'm not electrical side
what are the effects of variations in frequency when you are connected to national grid??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)