What is the difference between XLPE & FRLS cables? Is FRLS
cables is a type of XLPE cable or both r different?
Answers were Sorted based on User's Feedback
Answer / ramesh chandra dhing
XLPE-crosslinked polyethylene.
FRLS-fire retardent low smoke.
FRLS: is a property and its add on feature which is
introduced during manufacturing of cable on demand by which
we can use these cables in fire prone areas and in case of
fire these cables dose not catch fire upto prescribed temp.
level however XLPE is a type of insulation of cable which
improves current carrying capecity of conductor by 5~10%.
| Is This Answer Correct ? | 78 Yes | 4 No |
Answer / rahul sharma
XLPE is an INSULATING Material while FRLS is a Property
which we seeks in Outer Sheath Part of the Cable. Hence, we
can not compare the Both.
If we are talking about Normal XLPE Cable v/s FRLS XLPE
Cable, then please NOTE that the FRLS XLPE Cables are used
in the Fire Prone Area like Hospitals, Electrical Shops,
Fire Crackeer's Shop.
FRLS Properties:
1. Oxygen index: 29 min, when tested as per ASTM D 2863.
2. Temp. Index: 250°C min,when tested as per ASTM D 2863.
3. Smoke density rating:60% Max,when tested as per ASTM D
2843.
4. Acid Gas generation: Maximum 20% by weight, when tested
as per IEC 60754-1.
5. Flame retardant test as per IEC 60332-3 Cat C will pass.
Above are the properties for FRLS Cables.
** For More information Call me at
rahul.ravincables@gmail.com **
| Is This Answer Correct ? | 51 Yes | 1 No |
XLPE means Cross Linked Poly ethylene cables which may be
FRLS or ordinary. FRLS are fire resistant cables which are
used at the locations which are more prone to fire.
| Is This Answer Correct ? | 26 Yes | 12 No |
Answer / vinod bisht
actually both are different material where FRLS are used in
fire pron areas and XLPE elsewhere.
XLPE-crosslinked polyethylene.
FRLS-fire retardent low smoke.
| Is This Answer Correct ? | 17 Yes | 9 No |
XLPE means Cross Linked poly Ethylene these cables we are
using in Transmission the AC Supply like 440V
FRLS : Flame Retardent Low Smoke These cables we are using
in Fire panel wiring and smoke detectors wiring and FM 200
wiring and for access contol wiring also
In these cables we transmit DC Supply of 12v to 24V and
size of 0.75 to 1.5Sqmm with steel armoured
| Is This Answer Correct ? | 14 Yes | 15 No |
what is the need of capacitor in transmission lines?and how it works.
Which type of Oil is used in transformers, & what is its strength?
A 12.5 hp slip ring motor taking high initial current and its MPCB is getting open.what may be the reason?
why we +ve load distribution in 24v and -ve load distribution in 48volt in the telecom sector.?
How to take vector group test for Ynd11 transformer.
Will u plz give me simple diagram for tube light connection & also function of chock?
8 Answers Bhushan Power Steel, Dalmia Group, Jindal, Practical Viva Questions, TCS, Windmoller,
why using eleven's multiple for substations?
1. A 380 / 220 V r.m.s. 3-phase 4-wire circuit carries loads of 8 + j8.1 ohm; 4 + j4.1 ohm; and 2 +j2.1 ohmin the three phases respectively. The length of the circuit is 100 m, and the resistivity of the phase conductors is 0.0005 Ω/m. The neutral conductor is of the same size as the phase conductors. a) Select a reference angle 0for the first phase. Then write down the three phase voltages in both polar format and complex number format. b) Make appropriate assumptions, and take temperature effects on resistance is insignificant. Calculate the currents in the three phases. (Note: Determine conductor resistance, and apply Kirchhoff’s Voltage Law) Based on the result, suggest a main switch rating for the circuit. c) Show your preferred direction of neutral current in a diagram, and then determine its value. (Note: Apply superposition principle, and Kirchhoff’s Current Law) Use its magnitude to show that in this circuit, the unbalanced load may increase the voltage drop in some of the phases. (Note: Also observe the common volt drip in neutral) State your assumptions, if there are any. d) Suddenly the neutral wire of the circuit is broken. Estimate the new currents in the first phase, i.e. Phase L1. State your assumptions, if there are any.
What is the difference bet ween EDO Type & MDO type ACBs, and what is the advantage EDO Type over than MDO type ACBs.
WHAT IS MVA RATING OF KOTHAGUDAM THERMAL STATION POWER TRANSFORMER?
what is negative phase sequence
Define what is power quality meter ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)