What is the difference between XLPE & FRLS cables? Is FRLS
cables is a type of XLPE cable or both r different?
Answers were Sorted based on User's Feedback
Answer / ramesh chandra dhing
XLPE-crosslinked polyethylene.
FRLS-fire retardent low smoke.
FRLS: is a property and its add on feature which is
introduced during manufacturing of cable on demand by which
we can use these cables in fire prone areas and in case of
fire these cables dose not catch fire upto prescribed temp.
level however XLPE is a type of insulation of cable which
improves current carrying capecity of conductor by 5~10%.
| Is This Answer Correct ? | 78 Yes | 4 No |
Answer / rahul sharma
XLPE is an INSULATING Material while FRLS is a Property
which we seeks in Outer Sheath Part of the Cable. Hence, we
can not compare the Both.
If we are talking about Normal XLPE Cable v/s FRLS XLPE
Cable, then please NOTE that the FRLS XLPE Cables are used
in the Fire Prone Area like Hospitals, Electrical Shops,
Fire Crackeer's Shop.
FRLS Properties:
1. Oxygen index: 29 min, when tested as per ASTM D 2863.
2. Temp. Index: 250°C min,when tested as per ASTM D 2863.
3. Smoke density rating:60% Max,when tested as per ASTM D
2843.
4. Acid Gas generation: Maximum 20% by weight, when tested
as per IEC 60754-1.
5. Flame retardant test as per IEC 60332-3 Cat C will pass.
Above are the properties for FRLS Cables.
** For More information Call me at
rahul.ravincables@gmail.com **
| Is This Answer Correct ? | 51 Yes | 1 No |
XLPE means Cross Linked Poly ethylene cables which may be
FRLS or ordinary. FRLS are fire resistant cables which are
used at the locations which are more prone to fire.
| Is This Answer Correct ? | 26 Yes | 12 No |
Answer / vinod bisht
actually both are different material where FRLS are used in
fire pron areas and XLPE elsewhere.
XLPE-crosslinked polyethylene.
FRLS-fire retardent low smoke.
| Is This Answer Correct ? | 17 Yes | 9 No |
XLPE means Cross Linked poly Ethylene these cables we are
using in Transmission the AC Supply like 440V
FRLS : Flame Retardent Low Smoke These cables we are using
in Fire panel wiring and smoke detectors wiring and FM 200
wiring and for access contol wiring also
In these cables we transmit DC Supply of 12v to 24V and
size of 0.75 to 1.5Sqmm with steel armoured
| Is This Answer Correct ? | 14 Yes | 15 No |
what should be distance between two electrical earthing pit as per i.e.e
Is a contactor (or master relay) required between incoming lines and a VFD? The question goes to safety. If a contactor were used before the VFD and an e-stop engaged then the motor will coast to a stop (i.e. VFD loses power) instead of stopping much faster if the VFD braking fucntion were used. It would make more sense to keep power on the VFD.
why three phase system is not preferred in aircrafts power cckts if yes than explain reasons?
why ac supply neutral should earth not in dc (-)
25 kva 3 phase dg how many current will take per phase , plssssssss reply me
What is the different between earthing & Neutal
Enlist four components of electrive drives.
how to caculate cable size for given amperes
For small size, high frequency coils, the most common core material is- a. )Air b. )Ferrite c.) Powdered ion d.) Steel
How could i check the earth connection of my home using a multimeter?????? If it is possible plz help me....
How does a star connection and delta connection work? How does the star connection save starting current and how does it change to delta?
What is the reason that the humming sound is coming from the induction furnace panel?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)