Answer / hemachandra.m
main reason to parralel operation of the transformers are
for the load sharing purpose means if we have more load
than the excisting t/f then wecan do the parralel operation
of the two transformers that two transformers must be same
voltage ratio,vector group,and turns ratio.
| Is This Answer Correct ? | 10 Yes | 1 No |
after parallisation of trafo.,we can give a stable voltage
to the load, also if there is any probelem in any trafo. ,
than we can transfer all the the load to the another .
| Is This Answer Correct ? | 8 Yes | 7 No |
Answer / akshay khadse
when load current increases above the capacity of one x"mer , we can connect one more i parallel instead of replacing the existing with bigger one.
it is possible to repair or maintain the x"mer in parallel connect one by one without shutting off the plant.
if a 1 large x"mer used its failure will shut off the installation .the parallel x"mer solve this problem
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / prasad
I would like add a point to reena:
Generally we choose transformers with same capacity and impedance for redudandancy in Process plants to avoid power interruption to process.. and we do paralleling of trfs to carryout load shiftings without interruption especially critical loads.. (this is not in the case of lighting etc. where interruption really doesn't matter.)
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / reena
Main reason for parrallal operation of trasformer is to work without failure because we need power for 24 hours.
If failure occur or in cse of maitanace we can provide power to the consumer.
Also, one reason is that in parralal operation transformer share the total load.So, instead of one transformer if we have two it save total cost as well as the mainance cost coz we can manage with one if other has fualt so, we can atleat give power to the critical load.
| Is This Answer Correct ? | 7 Yes | 9 No |
Answer / mahendra
Becoze when connecting Xmer in parallel frequency ,Voltage
and phase Sequence should be same.
| Is This Answer Correct ? | 1 Yes | 3 No |
why the rotor is outside in case of ceiling fan?
WHY SECONDARY OF CT SHOULD NEVER BE KEPT OPEN CIRCUITED?
what is the difference between torque induced and torque load?compare them with respect to dc motor?
IF % IMPEDANCE OF A TRANSFORMER IS INCREASED FROM 5.8% TO 8% HOW MUCH THE EFFICIENCY OF THE TRANSFORMER WILL COME DOWN?
I HAVE A 1 MVA TRANSFORMER, I WANT TO KNOW THE FAULT LEVEL OF THE SYSTEM ( WHAT IS FAULT LEVEL PLEASE EXPLAIN WITH EXAMPLE)
what happens when a power transformer neutral earthing broken???
Define coil span?
if its possible for step up or step down DC volage directly ? possible means how we can do it ?
HOW TO CALCULATE THE WIRE SIZE FOR THE GIVEN LOAD?
what is amf panel & how it is working
Why 11kv to be generated in generation station
0 Answers TNEB Tamil Nadu Electricity Board,
What does a permanent magnet generator do?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)