Answer / bhavesh chauhan
First of all let us know what is Tan Delta......?
Tan Delta Testing of a transformer or a CT or a PT determines integrity of insulation of the equipment which determines the remaining life of the equipment. Tan Delta is also called as loss angle or Dissipation Factor Testing.
In a perfect capacitor the curve of voltage vs current are phase shifted by 90..in case if any impurities are present the phase shift wont be 90 degree any more which means it will be less than 90. Thus by measuring new angle developed less than 90 we can calculate the loss angle or the level of insulation.
Measuring of Tan Delta is very simple..We have a Tan Delta Kit which has two terminals coming out of it. Applying the two terminals on top and bottom of the equipment and injecting the current through kit we can get the values of the test..
Tan delta Point is nothing but a point covered by a nut bolt on the bottom side of Bushing of transformer and CT..............
| Is This Answer Correct ? | 34 Yes | 14 No |
Tan Delta point in the CT is located at the bottom of the CT. It is provided specifically for TanD testing so that we can find the capacitance and TanD between CT primary and its structure.
It is It is usually connected to ground. But at the time of test, it should be separated from ground and should be connected to LV lead from the TanDelta test set.
| Is This Answer Correct ? | 3 Yes | 0 No |
How can we select suitable capacity generator for three phase load (inductive load) and how to take study analysis in 3 three phase load system ?
What is the equivalent circuit of a transformer and its vector diagram?
campared to ac, in dc corona loss is
Hello, im taking an introduction to PLC..and i'm having a hard time on creating a program for 2 lamps blinking alternately with this button characteristics: 1.) One push button (starts upon pressing) 2.) Same push button (when pressed again, will pause the system) 3.) Same push button (when pressed again, will continue the paused system) 4.) Same push button (when pressed within 2 seconds, will shut off the system) Pls..i know this is just a simple problem for you guys..
Why CT secondary is grounded?
why the carbon brushes are broken in srim while the motor runningtime
What is A check, B check, C Check & D check for a diesel Generat
0 Answers Jtekt Koyo Bearings,
how many percent setting of motor over load relay of its full load current
what is the thumb rule to know current carrying capacity of copper conductors of different size.
can u light up bulb with out useing neutral
Why high Voltages come in multiple of 11, like 11 KV, 33KV, 66 KV, 132 KV etc.
what is over frequency protection
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)