What are the testing to be done before the installation of
1000 KVA Transformer?
Answers were Sorted based on User's Feedback
Answer / jyotirmaya
Normally test are done before installation and commissioning
of the transformer. The following test are done;
1. Visual Inspection
2. Insulation Resistance Test
3. Ratio Test
4. Vector Group Test
5. Magnetizing Current Test
6. Core Balance Test
7. Winding Resistance Test
Is This Answer Correct ? | 38 Yes | 3 No |
Polarity Test also an important before loading
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rajan singh tanwar(j.k. cement
For Power
Transformers the
following Pre
Commisioning tests
are done:-
1.Visual Inspection
2.Measurement of IR
Value
3.Measurement of P
I Value
4.Measurement of
Winding
Resistance
5.Short Circuit Test
6.Oprn Circuit Test
7.Magnetic Core
balance Test
8.Voltage Radio Test
9.Oil BDV & Acidity
Test
10.Checking the
function of
OTI, WTI, OSR, MOG,
PRV
Relays
Last one for the
relay's testing but
it also comes under
transformer testing.
Thanks
Is This Answer Correct ? | 3 Yes | 0 No |
what sq.mm copper pvc wire need for ac load current 25amps for 230v ?
what is difference between power & distrubution transformer ?
what is the difference between RCCB and ELCB?
Why capacitor bank ratting Kvar?
if there is nutral in phase why we use earthing wire and grounding? even at fault condition the fault current flows to neutral (it is a lower path)
What is relation between mu(nought) and epsilon(nought)?
There are Two questions about Steam Turbine Generator... What is HRSG bypass of LP, HP used for in power generation? In particualar, in the event that fault of HP bypass, there would be STG TRIP in operation but none on the LP bypass fault...what's the reason ?
What is LMU and LMDU. in PLCC communication of 132 kv transmission line. is it possible to use only one LMU with out LMDU ?
Differnce between earthing and nuetral
in gen traf what is ONAN , ONAF , OFAF and DYN
What is oil temprature with A/T contacts in Transformer ?
why we can use 1 to 5V dc