We operate a 10 Mw facility and we have been experiencing
several trips due to fluctuations on the MVAR? We have
checked all issues related to the AVR and we have found all
OK? Can anyone help us? The grid voltage, internal voltage,
all regular parameters look ok. MVAR fluctuate and there it
goes the unit? What could be happening? Thanks!
Answers were Sorted based on User's Feedback
Answer / chaitanya
this may happen due to the variation of reactance produced
by the capacitors connected to that line/....isolate one by
one under observation...and this can be sorted out on
timely basis,,,,
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / raj
I agree with chaitanya this may happen due to the variation
of reactance produced
by the capacitors connected to that line it will be better
to maintain the Power Factor 0.90 only every where and the
next and only cause is that AVR problem may be some loose
connection in power as well as control side because AVR has
to take care of that MVAR.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / naresh
this could be because of the interturn winding losses that
takes place in the lines.this factor may increase the MVAR
rating of the system,which infuence the performance of thea
system.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / manish
Generator AVR have got two setting either to fix MVAR or
according to load if u set them to fix MWAR generation
probably it will solve ur problem to a extent also look at
load pattern first.its really helpfull when you have synch
operation with grid.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.j.pailwan
Please check CT connections, CT Specifications and
saturation of particularly B phase as this CT feed back is
used in AVR during PF control mode while pareller with grid.
| Is This Answer Correct ? | 0 Yes | 0 No |
What does ampere turns shows?
how to determine the cable size...pls explain me with the formula taking particular load....does the factors like impedance & short circuit rating influence the cable size, if so how....
How to calculate the Airconditioner capacity for a standard telecom BTS shelter?
Why derivative controller is not used in control systems?
There is any especial requirement for motor to drive through with VFD?
Three way plug point is there ,in that plug why we need earth pin is bigger than compare with phase and nutral pins?
why do we have 230v a.c. as general voltage for domestic supply rather than others?
How much current can carry the 1 sq inch super enamelled copper wire?
In LRS how much water PH value maintain for good operation of motor?
In chillers & freezers which gas will be use?
why a tester wont shock while testing the power in house
50 electric bulbs are connected across supply of 220 volts. After one bulb is fused remaining 49 bulbs are again connected to same supply. which case will have more illumination & WHY????????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)