We operate a 10 Mw facility and we have been experiencing
several trips due to fluctuations on the MVAR? We have
checked all issues related to the AVR and we have found all
OK? Can anyone help us? The grid voltage, internal voltage,
all regular parameters look ok. MVAR fluctuate and there it
goes the unit? What could be happening? Thanks!
Answers were Sorted based on User's Feedback
Answer / chaitanya
this may happen due to the variation of reactance produced
by the capacitors connected to that line/....isolate one by
one under observation...and this can be sorted out on
timely basis,,,,
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / raj
I agree with chaitanya this may happen due to the variation
of reactance produced
by the capacitors connected to that line it will be better
to maintain the Power Factor 0.90 only every where and the
next and only cause is that AVR problem may be some loose
connection in power as well as control side because AVR has
to take care of that MVAR.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / naresh
this could be because of the interturn winding losses that
takes place in the lines.this factor may increase the MVAR
rating of the system,which infuence the performance of thea
system.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / manish
Generator AVR have got two setting either to fix MVAR or
according to load if u set them to fix MWAR generation
probably it will solve ur problem to a extent also look at
load pattern first.its really helpfull when you have synch
operation with grid.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.j.pailwan
Please check CT connections, CT Specifications and
saturation of particularly B phase as this CT feed back is
used in AVR during PF control mode while pareller with grid.
Is This Answer Correct ? | 0 Yes | 0 No |
Whay you want to change your job.
if i am in front of transmission line how to know that current direction without any equipment
What is hipot test procedure?
What are the essential parts of a transformer?
how to calculate Amp, 2 different Amp of batteries? Example: No. of Batteries = 2 Battery voltage = 12V 1st Battery rating = 17AH 2nd battery rating = 30AH between parallel connection then output volt 12v Amp?
why autotransformers are not safe for supplying low voltage from a high voltage source?
How the Transformer oil testing is done & Why oil dielectric goes LOW & what is solution for that ??
how to calculate the capacitor to maintain power factor?
. Draw the vector diagram and condition for the following: 1) Dyn1 2) Ynd0 3) YnYn0
Up to how much limit of HP of electric motor the Star- Delta Starter can be used ?
What is the safety protection? Name the protections of Transformer?
A 50Hz,4-pole,3-phase,star-connected synchronous motor has a synchronous reactance of 12ohmsper phase and negligible armature resistances.the excitation is such as to give an open-circuit voltage of 13.2kilovolt.the motor is connected to 115kilovolt, 50hertz supplying. what maximum load can be the motor torque,line current and power factor?