We operate a 10 Mw facility and we have been experiencing
several trips due to fluctuations on the MVAR? We have
checked all issues related to the AVR and we have found all
OK? Can anyone help us? The grid voltage, internal voltage,
all regular parameters look ok. MVAR fluctuate and there it
goes the unit? What could be happening? Thanks!
Answers were Sorted based on User's Feedback
Answer / chaitanya
this may happen due to the variation of reactance produced
by the capacitors connected to that line/....isolate one by
one under observation...and this can be sorted out on
timely basis,,,,
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / raj
I agree with chaitanya this may happen due to the variation
of reactance produced
by the capacitors connected to that line it will be better
to maintain the Power Factor 0.90 only every where and the
next and only cause is that AVR problem may be some loose
connection in power as well as control side because AVR has
to take care of that MVAR.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / naresh
this could be because of the interturn winding losses that
takes place in the lines.this factor may increase the MVAR
rating of the system,which infuence the performance of thea
system.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / manish
Generator AVR have got two setting either to fix MVAR or
according to load if u set them to fix MWAR generation
probably it will solve ur problem to a extent also look at
load pattern first.its really helpfull when you have synch
operation with grid.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.j.pailwan
Please check CT connections, CT Specifications and
saturation of particularly B phase as this CT feed back is
used in AVR during PF control mode while pareller with grid.
| Is This Answer Correct ? | 0 Yes | 0 No |
Give me clear explanation.What is the Different Between Load break switch and Vacuum circuit breaker
what is differnt between metering CTs an protection CTs
1.difference between sts & ats? 2.what is fm200 system brefly explain?
What does the term power factor shows?
How to select a D.G set for calculated load of 110kW..?
7 Answers Shakthi Power Systems,
why aggregate is placed all around substation ground.
why do you give the dc supply to field of alternator
What is basic difference between Soft Starters And VFD drives?
my b-tech percentage is 50%. what answer will satisfy the hr ?
if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will happen?
In our homes we place the 5Amps fuse...now in our house only takes 5Amps for all normal conditions ha???
why dc moter are not earthed ????
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)