Why HT cable have only 3 core ?
Answers were Sorted based on User's Feedback
Basically the HT cable is used for transmission line only
not in distribution line. Because we are using delta
connection (Three phase Three wire system) for transmission
and star connection (Three phase Four four wire system). So
that's why the HT cables have three cores only.
Is This Answer Correct ? | 58 Yes | 5 No |
Basically the HT cable is used for transmission line only(
delta connection only)
not in distribution line(star connection)
(Three phase Three wire system) for transmission
and star connection (Three phase Four four wire system). So
that's why the HT cables have three cores only.
Is This Answer Correct ? | 11 Yes | 1 No |
Answer / sanjay chauhan
Basically the HT cable is used for transmission line only
not in distribution line. Because we are using delta
connection (Three phase Three wire system) for transmission
and star connection (Three phase Four four wire system). So
that's why the HT cables have three cores only.
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / superjyoti
HT cables are rated at 1000v to 11kv.This is the range of
transmission voltage.In normal transmission line three
conductor are required.Electrical power is generated at
power plant(11kv normally),then stepped up by transformers
to transmit power to far substation.The secondary winding
of these transformers are in delta connection.
Whereas LT cables are rated up to 1000kv used for
distribution purpose.they are generally of 3.5 core,4 core
etc.three are for phase one for neutral.In the distribution
transformer secondary winding is generally star
connected.so we get 3 core 4 wire o/p(1 wire for neutral)
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ahmed
beacuse we using delta star connection so the incoming will
be 3 core for delta(3 phse
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / ramanharikrishnan
HT line means contaning of three phase only(R,Y,B). There
is no Neutral.That is what HT cables having only 3 Cores
with armouring for earthing.
Is This Answer Correct ? | 2 Yes | 4 No |
Answer / sameer sane
Its very much economical to transmit power by using delta
connections since for very large distances, neutral need
not be used.
Is This Answer Correct ? | 4 Yes | 7 No |
Answer / prabhukumar
Delta connection is best suitable for the transmission of
power where as the star connections is for the
distribution.to avoid the long laying of cable for neutral,
basicaly 3 core HT cable used after that through trafo they
will change to thier requirement.
It may result in failure of neutral or week in neatral, in
case of damage or break.
Is This Answer Correct ? | 0 Yes | 3 No |
Answer / sai singamala
HT cable is used for high voltage transmission purpose due
to avoid the corrona and losses becose of HT cable 3 core
is used for only transmisson of the voltage without neutral
of the genaretion side or power station.
Is This Answer Correct ? | 7 Yes | 11 No |
as per system contain only three phase thats why requirment
is for three core & in system used three core.
Is This Answer Correct ? | 3 Yes | 23 No |
why and how voltage sharing in transformer, during magnetic balance test ?
how can we charged the battery in DG
why we used servo motor insted of inducation motor?
How to Decide(calculate) Bush bar size for copper and aluminiam ?
how to calculate induction motor rating (HP) if name plate is missing from motor at site condition ?
6 Answers ABB, apatel, Bhel, Spatel, Voltas,
How to design power source say 5KW i/p :415v 3 ph, o/p 5KW constant, variable currnt and variable volatge 10-230v,
How to reduce the static electricity producing in solvent room? By P.D.Patil BioCon
Why is copper a better conductor of electricity than aluminium?
how to calculate the settings for shaft ct protn in hydro generators
How many current ratings of MCB's are in the market? e.g: 1A, 2A, .......upto.
what is ground clearence in transmission system.is it varies wit conductor size,height of poles,span.
minimu size and length of gi earth pipe