after parallaing two generators current is shooting up in
both the generators.for ex: load is 400 kw..after paralling
and load sharing current in running gen is approx 900 amps
and incoming is 750 amps which is too high when trying
toshift the load current in incoming gen is coming more
than 1300 amps and both getting tripped and making
blackout..
Answers were Sorted based on User's Feedback
Answer / raj
Is both generator parallel to GRID means Your generator
AVR is not working properly, these requrired kvar sharing
must is there available or not If availabel AVR settings to
shoule be change then is not solved the problem it is
required winding test required.
| Is This Answer Correct ? | 1 Yes | 0 No |
it looks like one of the genset is having a big difference in voltage or
the droop kit if fitted something wrong with it or
check after paralling do you have balanced three phase voltage and current or one of the phase is open circuit or
the gen is running the other as motor
if you know the actual reasons later please let us know also
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / yuvi
This means that the phase angle of the existing generator
and the new incomming generator are not matching. You can
try the bright lamp or the dark lamp method to synk them.
There is no way in which you can directly plug in a
alternator to an active AC system.
| Is This Answer Correct ? | 1 Yes | 1 No |
What is the electrical difference between Earthing Switch (ES) and Maintenance Earthing Switch (MES)?
what is the meaning of pi value?
Can anybody please refer the best and simple book for about Protection relays and in detail of all its protection ?
Explain why the Voltage drop will happen in 3 Phase line?
which type of oil is used as a transformer oil?
i have ht transformer of 142 kva with air cooled facility,having secondary voltage 7850volt, and secondary connected full way bridge rectifier .i faced the problem repeatedly that transformer one coil and rectifier diode of two phase was burnt two times. i checked all the secondary ckt. no any short ckt found,then what will be the cause side
2 Answers Modern Terry Towels,
what is through fault?
why the the phase transformer's nuetral has been grounded
When lag/lead/lag-lead compensation is employed?
if the diameter of a conductor is 'R' then what is the distance between two bundle conductor in a phase?
What is difference between Earthing, Ground and Neutral?
1 Answers ABB, ABC, Indo Asian,
What is the advantangeous over SFU (switch fuse Unit) & FsU (Fuse Switch unit) which one is better & application of Both?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)