WHY TRANSFORMER IS MEASURED IN KVA?
Answers were Sorted based on User's Feedback
Answer / vamsi kaushik
the losses in the transformer viz., core and copper losses
depend upon voltage and current respectively. as a
machine's rating is framed depending upon the heating
inturn on the losses, the transformer rating is always
specified in terms of voltage and current i.e., in terms of
kva rating.
moreover a transformer has to take any kind of load
irrespective of the power factor. it is not economical to
design a transformer to carry only one kind of load.
hence due to tje above two reasons the rating of a
transformer is given in terms of its kva rating.
| Is This Answer Correct ? | 45 Yes | 4 No |
Answer / bhupinder
KVA mean Voltage x Current
and
KW mean Voltage x Current x Power factor
The only difference is power factor
Power factor depends upon load and its value varies from
0.5 to 1
As kw is depend upon the power factor , but kva does not
depends upon the power factor mean kva of any transformer
or generator does not change with power factor . SO to know
the correct power of transformer ,we use kva as it nothing
to do with load type or power factor value
| Is This Answer Correct ? | 28 Yes | 3 No |
Answer / mahesh-lanco
The Losees in the transformer are mainly 1.Core Losses
2.Copper Losses.
As we are well aware,the core losses depends on Volage and
Copper Losses on Current.
KVA means Product of Volatge & Current.
Thts what The rating of Transformer in KVA but not in KW.
| Is This Answer Correct ? | 16 Yes | 2 No |
Answer / naresh
Because power factor of the load is unknown that's why transformer measure in kva
| Is This Answer Correct ? | 1 Yes | 1 No |
Any AC electrical equipment that has conductors have to be rated in voltage and amps, so it is KVA if more than thousand. WHY.
SIMPLE . If more than the designed amps flows through the equipment it will over heat and burn.(destroyed)
IF a 500 kw transformer is loaded at 415 v at unity pf to the max it will carry 500000/415x1.732 = 695 amps
if the same transformer is loaded at 500kw at 415 v but at 0.5 pf it will carry 500000/415x1.732x0.5 = 1391 amps
can the transformer winding take this amount of current.You see on both occasions the load was 500 kw but the pf was different and the amps was double.What will happen if the transformer is loaded at a further lower pf. should the transformer be still rated as 500kw
| Is This Answer Correct ? | 4 Yes | 9 No |
Answer / shanmugam.k
In transmission line the voltage value measured as volt and
current value measured as amphere and also the indicated
in kilo only .then only we measure in KVA
| Is This Answer Correct ? | 4 Yes | 11 No |
Answer / bhushan naik
Because Power factor is depand upon the consumer.
| Is This Answer Correct ? | 10 Yes | 21 No |
Answer / vinod kumar.g
Transformers are generally measured in KVA because it has
got nothing to do with the power-phase voltage. Its
measured against the angle between Voltage-current. And
hence KVA.
| Is This Answer Correct ? | 15 Yes | 33 No |
types of transformers?
what is meaning of bus raiser???
Car battery + terminal allways biger than - terminal! Why?
can you show me the components inside a air circuit breaker with connection diagram?
extremely urgent please, why a fuse is used before voltmeter but not with a ammeter connected to a CT(current transformer),thanks in anticipation.
induction 3 phase motor terminal connection
How to Calculate 11 KV Side Cable size of a 250 KVA Oil cooled transformer
how to select proper cable for ct wiring so that drop within the limit.
140 is load amps for a equipments and what ratio of CT requied for installimg ammeter to amps montering purpose?
I have 11KV/415V power distribution transformer. I have found unbalance current in LT (415V) side. Also observed that unbalance voltage (3V) at LV side due to HV side unbalance voltage. What should I check for this? Also, the same LV side load can run in balance on captive power.
why distribution transformer is uesd in Delta/Star formation?is there any significance in doing this?If yes then breif?
What is the exact formula for one weber of magnetic flux?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)