why are using bus ducts ? why not using cables
Answers were Sorted based on User's Feedback
Answer / anand kumar shukla
as we know very well .we are use the busbar in busduct
because the current bearing rating of busbar is too much
high in compare to the cable.
we use the 150 x12 mm
150 x10 etc.
so the busbar mechanical strenth is too much strong than
cable. and busduct life is too long in compare to cable.
| Is This Answer Correct ? | 65 Yes | 9 No |
Normally busducts are used in between secondary side of the
transformer to panel where the distance will be short and
current carrying capacity will be high the busbars used are
generally of greater cross sectional area than the cables,
and also once they are fixed it hardly requires any
maintenance except for tightness in cables you need to do
period check of IR.
| Is This Answer Correct ? | 47 Yes | 2 No |
Normally we wlli use this BUSDUCTS in LV side of the
transformer BcoZ the Current flowing in the LV side is more
than the HV side.
If we use cable we need Large Sq .mm for which cost is more
than to replace a cable. so, it is used. and another thing
is it has high mechanical strength.
| Is This Answer Correct ? | 23 Yes | 4 No |
Answer / anand
The great advantage of Busduct are compact ( Sandwich type) and easy terminations at trf & panels. When we go for the high rise building with 20 floor, busducts ( one circuit)with floor tapping work out cheaper with less space and reduced distribution boxes. If cables to be laid then 20 circuits to be travelled from Ground floor.
Also busducts are very useful in industrial floor distibutions in a very economical way with more number of tapping.
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / chirag mistry
Busbar SC level is high in comperision of cable.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / m.sridhar
above 1000 Amps ,busbar is mandatory as per IE rules,as there is no protection between transformer secondary and it breaker,probability of busbar failure is very less compared to cable.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / lekha
On LT side, we can use insulated bus bars insted of cables.
Advantage is that we can take tap from busbar at many
places. Such bus bars of Schnieder, L&T are available in
market.
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / neet
Normally busducts are used in between secondary side of the
transformer to panel where the distance will be short and
current carrying capacity will be high the busbars used are
generally of greater cross sectional area than the cables,
and also once they are fixed it hardly requires any
maintenance except for tightness in cables you need to do
period check of IR
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sachin gopi
The transformer rating is more than 1000 KVA,Then current rating will be high so cables should not used.by using bus ducts
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / muhammad irfan ali
Bus Way Good as Compare to cable ,because it has high current rating
and you take supply different location
but it is not good for Medium voltage because it has no high current and also cost is higher then cable
| Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate percentage impedence at 75 deg C at normal tap
Why there are some equipment(i.e:TV) that using 2-pin plug instead of three? What happen if there is current leakage? Are we going to get electric shock??
0 Answers College School Exams Tests,
when motor taking high amp what happen.
what is the maximum current carrying capacity of a 95 sqmm cupper under ground cable laid partialy in land and partialy in ground?
FLP zone Types and Details
What are protections for dty type transformers
what is lrs tank water resistance.
What should be the overcurrent, instantaneous overcurrent, short cicuit current settings (i.e. how many times of motor full load and what is the time duration) for a motor?
What is voltage in two phase?
Why the transformers are rated in KVA. ? in new view.
why use only sf6 circuit breker in 400 kv sub station
how does PLCC work?...
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)