why are using bus ducts ? why not using cables
Answers were Sorted based on User's Feedback
Answer / anand kumar shukla
as we know very well .we are use the busbar in busduct
because the current bearing rating of busbar is too much
high in compare to the cable.
we use the 150 x12 mm
150 x10 etc.
so the busbar mechanical strenth is too much strong than
cable. and busduct life is too long in compare to cable.
| Is This Answer Correct ? | 65 Yes | 9 No |
Normally busducts are used in between secondary side of the
transformer to panel where the distance will be short and
current carrying capacity will be high the busbars used are
generally of greater cross sectional area than the cables,
and also once they are fixed it hardly requires any
maintenance except for tightness in cables you need to do
period check of IR.
| Is This Answer Correct ? | 47 Yes | 2 No |
Normally we wlli use this BUSDUCTS in LV side of the
transformer BcoZ the Current flowing in the LV side is more
than the HV side.
If we use cable we need Large Sq .mm for which cost is more
than to replace a cable. so, it is used. and another thing
is it has high mechanical strength.
| Is This Answer Correct ? | 23 Yes | 4 No |
Answer / anand
The great advantage of Busduct are compact ( Sandwich type) and easy terminations at trf & panels. When we go for the high rise building with 20 floor, busducts ( one circuit)with floor tapping work out cheaper with less space and reduced distribution boxes. If cables to be laid then 20 circuits to be travelled from Ground floor.
Also busducts are very useful in industrial floor distibutions in a very economical way with more number of tapping.
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / chirag mistry
Busbar SC level is high in comperision of cable.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / m.sridhar
above 1000 Amps ,busbar is mandatory as per IE rules,as there is no protection between transformer secondary and it breaker,probability of busbar failure is very less compared to cable.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / lekha
On LT side, we can use insulated bus bars insted of cables.
Advantage is that we can take tap from busbar at many
places. Such bus bars of Schnieder, L&T are available in
market.
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / neet
Normally busducts are used in between secondary side of the
transformer to panel where the distance will be short and
current carrying capacity will be high the busbars used are
generally of greater cross sectional area than the cables,
and also once they are fixed it hardly requires any
maintenance except for tightness in cables you need to do
period check of IR
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sachin gopi
The transformer rating is more than 1000 KVA,Then current rating will be high so cables should not used.by using bus ducts
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / muhammad irfan ali
Bus Way Good as Compare to cable ,because it has high current rating
and you take supply different location
but it is not good for Medium voltage because it has no high current and also cost is higher then cable
| Is This Answer Correct ? | 0 Yes | 0 No |
CAN A CD/CLOCK RADIO WITH 110V 60HZ WORK ON A 110V 50HZ FEED.
How does frequency affect KVA rating of a transformer? If a 500 kva, 400 v, 60 hz t/f is to be operated on 50 hz frequency then how will its KVA rating change? a-increase b-decrease c-remains same Also explain why do u think like that.
What happened when a three phase induction motor work on two phase supply.9
why we use crushed stone in switch yard?
If a motor of 8.5 KW with same load and using in both Star & Delta one by one,then which will take more current in star connected or in delta connected
HOW TO CALCULATE BATTERY BACKUP TIME & AH CAPACITY AGAINST UPS KVA RATING?
In a running D.G set engine and Alternator is revolving at 1500RPM but no output in the terminal>>>>what to do?? someone told excitation problem ....please advice
why we use post insulators in no ofstacks at substation for supporting equipment ? why we not use single post insulator
Which type of questions well asked. ?
I have a transformer 3phase 11kv/410v and its name plate missing. now how can I judge its rated kva?
i have 2 motor of same rating. on no load condition one motor take 1.6A but other motor is taking 4.8A. what is the reason of this. please explain with proof.
what is per unit calculation?looking for simple and strong explanation thk u
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)