why are using bus ducts ? why not using cables
Answers were Sorted based on User's Feedback
Answer / ramesh kumar
busbar is Cu or Al conductor without insulator..in market
current Rating available for busbar is high compare with
armored insulated cable. cost also high for cable. but in
safety aspect cable is good.we can use N no of cable to
attain current rate by connecting parallel. busbar need
protection from water. so using dusts shaped structure to
protect busbar.
Is This Answer Correct ? | 3 Yes | 26 No |
Answer / suresh
Also busbars are made in Stainless steels. Once the high
current pass through the steel become hot more than copper.
If we use the sheathed insulation or cable it's become
melted. So, we use busducts to the busbar's was the correct
choice.
Is This Answer Correct ? | 6 Yes | 45 No |
to operate air conditioner of 1.5ton what power of generator is required
What are insulation classes? Tell examples of each of them.
What is the meaning of high reputuring in HRC fuse.?
Tell me how you are ready to comply with the employment rules and regulations if your CV is considered for employment?
how can you size an automatic voltage regulator?
why we use end termination xlpe cable on ht kit
Can you explain about Restricited earth fault protection scheme
Recently we had experienced following problem All RCCB breakers (connected to the load as well as spares) connected to various UPS systems at various floors at a high rise building tripped during a power break down and upon starting up of generator.This Generator is recently inducted into the installation. Can any one explain the reason behind this tripping. Regards Viswanathan
what are the components of a start and stop motor control?
1.what is the difference between transformer differential and busbar differential.2)why we are using 2 slope for trafo diif and 1 slope for busbar diff.3)what is the purpose of metrosil and stabilizing resistor in high impedance relay circuit.4)how metrosil reduce the peak volage.5)what is the funtion of stabilizing resistor
Why wind turbines wheels rotate constantly
What should do when induction motor take more load in single phase ?