Answer / benu
kva=kw/pf,with low pf,kva will be high,insulation cost in generator and transformer+cu loss in transmission line will rise and efficiency will come down
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / koti
above answer is partially correct i.e, at low pf the kw output is low and is due to inductance and capacitance elements of ckt but not harmonics
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / ghulammohyhuddin
power factor control mager demand form electrical city
because actual lode between appearance lode is power factor
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / purushottam kumar
for constant power and terminal voltage ,if power factor is low current drawn is more ,so more lose ocour ,regulation is poor, conductor size increased than with high power factor
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / sudhakar g
Power factor is imp bcoz....ex: If we have an panel that
will give the o/p of 300KW but if we dont maintain the
powerfactor by using APFCR it will give the o/p of 240KW
only....by maintain the powerfactor by using the APFCR we
can get (0.98%)....power factor means something lagging and
leading in power due to harmonics...
| Is This Answer Correct ? | 6 Yes | 8 No |
what will happen if i connect or change line with phase terminal
what is polarity in ac system? and how do identified?
2. A current i=(10+10 sin t)amperes is passed through MI type ammeter. its reading will be.........
Difference between split ac and cassete ac?
Please explain open transition and closed transistion system in Star delta Starter?and also the state difference of both?
Why all voltage level are multiples of 11, like 220V, 440V, 1100V instead of 200V, 400V, 1000V?
9 Answers Indian School of Mines,
in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 33v to 430.v.
how netral CT is selected (including its details specification)
8 Answers ABB, ABC, dbpl, Mecon, Shree Engineering, Tapasya Transformers,
Instrument connected to a single phase supply
in transformer input is d.c signal which type of emf is induced
how to find the transformer neutral copper earthing size
Why we use the D-curve MCBs in critical power distrubution.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)