If the damper winding on the rotor of a synchronous motor is
removed after starting what will happen?

Answers were Sorted based on User's Feedback



If the damper winding on the rotor of a synchronous motor is removed after starting what will happe..

Answer / meenakshi

damper windings are mainly used to provide startn torque
for sync motors.though under the normal running
condition,the damper does not carry any current since the
rotor runs at a synchronous speed, it cannot b removed.its
another purpose is to prevent hunting(i.e,momentary speed
fluctuation) n helps the motor to run @ sync speed by
preventing oscillations.

Is This Answer Correct ?    31 Yes 2 No

If the damper winding on the rotor of a synchronous motor is removed after starting what will happe..

Answer / deepak tyagi

When synchronous motor get started than it run at
synchronous speed. at this time damper has not current. the
second purpose is it provied synchronzing power in case of
disturbance.this power pull the machine in the synchronizm
again. so if we remove the after starting than machine will
work in synchronizm but as load incresed machine will not
work as synchronous motor.

Is This Answer Correct ?    4 Yes 1 No

If the damper winding on the rotor of a synchronous motor is removed after starting what will happe..

Answer / shailendra

in synchronous motor Damper winding mainly used to damp out the oscillation, which may occur due to any sudden load change, that's why its called DAMPER WINDING ( not a starting winding). but at the time of starting it is used as a starting winding also ( but this is not a primary use of it).

Is This Answer Correct ?    3 Yes 0 No

If the damper winding on the rotor of a synchronous motor is removed after starting what will happe..

Answer / sara ashfaq

1- Damper windings helps the synchronous motor to start
on its own (self starting machine) by providing starting torque
2- By providing damper windings in the rotor of
synchronous motor "Hunting of machine"can be suppressed.When
there is change in load, excitation or change in other
conditions of the systems rotor of the synchronous motor
will oscillate to and fro about an equilibrium position. At
times these oscillations becomes more violent and resulting
in loss of synchronism of the motor and comes to halt

Is This Answer Correct ?    2 Yes 0 No

If the damper winding on the rotor of a synchronous motor is removed after starting what will happe..

Answer / mehmed

damper windings are mainly used to provide startn torque
for sync motors.though under the normal running
condition,the damper still carry little current even the
rotor runs at a synchronous speed, it still can be removed.
i already done the lab experiment.

its another purpose is to prevent hunting(i.e,momentary speed
fluctuation) n helps the motor to run @ sync speed by
preventing oscillations.

Is This Answer Correct ?    0 Yes 1 No

If the damper winding on the rotor of a synchronous motor is removed after starting what will happe..

Answer / ashish negi

damper winding is connected to stator winding togive
starting torque to synchronous machine.once the motor is
started it can be removed but it is not practically
possible.

Is This Answer Correct ?    1 Yes 2 No

If the damper winding on the rotor of a synchronous motor is removed after starting what will happe..

Answer / p.senthil kumar

Damper windings in synchrous motor only for the purpose of
starting(Sychronous motors are not self started type).after
motor get started damper winding can be removed.

Is This Answer Correct ?    7 Yes 14 No

Post New Answer

More Electrical Engineering Interview Questions

WHY CAPACITOR IS NOT USED FOR THREE PHASE MOTORS DURING STARTING

1 Answers   Quest,


ouestion for the post of section engineer

1 Answers   BSNL, RRB,


How can i check a relay good or not?

2 Answers  


If Earthing is poor in a DB of of Residential Building, will residents feel a leakage voltage in a Electrical Ssytem? is this statement true?

1 Answers   Dolphin International,


Whether power factor should be high or low? Why?

0 Answers  






Why we use Delta connection in the secondary side of a High Voltage transformer?

1 Answers  


If ct ratio is 250/1 and mtr is of 5 amp, what will be mf?

1 Answers  


A 230V, 60W bulb when connected to 230v supply what current and power will consume, if same bulb is connected to 200v what purrent and power will consume?

3 Answers  


Why does the rotor rotate?

1 Answers   Machino Polymers, OPTCL,


there is a power transformer 66/11kV in delta-delta connection has 5 feeder coming out from the secondary side. One of the feeder in it normally loaded (loaded than other feeder)and this feeder usually trips with double OCR causing the bank transformer to trip. Now if the load of this feeder is put on other transformer then that no problems occurs on that transformer or the load. However normally all the test(IR, PI, short ckt, open ckt,grounding test and other ) has been conducted for this but evertything transformer..... I am not geting what is the actual problem...

2 Answers  


what is doid

0 Answers  


difference between diode and scr?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)