how to calculate generator capacity?(kva)
Answers were Sorted based on User's Feedback
Answer / aamod tripathi
first the total load to be catered is taken in kw
the load factor
diversity factor
efficiency of the generator
power factor is to be known
then calculate the kva rating of the generator by
kva= (kw*load factor)/(power factor* efficiency* diversity
factor)
AFTER THIS CALCULATION A CONTINGENCY FACTOR OF 10-20%
Is This Answer Correct ? | 28 Yes | 5 No |
Answer / farrukhwaheed
kw*load factor)/(power factor* efficiency* diversity
factor)
Is This Answer Correct ? | 9 Yes | 7 No |
do any one help me to get "C" license,, i have doubts ,,, if mediators ter pls call me,, my no is 8056640042
How to find the maximum load, that can be supplied by a transformer.....
Can we use BS 6651 and BS EN 62305 standards for computer room lightning ptotection in substation?
how the arcing is made in ac electric arc furnace? ( between the three electrodes in any sequences or between the electrode & the charge(steel))
current cyring capacity of .75sqmm copper cable
In Plumbing services What are accessories we consider for a bathroom?
Electricty is generated at around 16kV, then step up to 220kV for transmission then steped down to power transformers then DTs and then through the LT n/w it reaches the consumer end. At the consumer end 230V supply is required. So, why is electricity not generated directly at 230V and transmitted?
Is it possible to measure the voltage of a battery from a single terminal?
What is the difference between rated and per unit in transformer?
in science exhibition how lamp can blink when you clap near the lamp ? thank you
what is effect of reverse c.t connection on metering.
please send me latest & previous years question papers for IOCL Technical level questions