can we load Power capicitors on DG sets?
Answers were Sorted based on User's Feedback
Answer / martin
No we need not connect the Capacitor to the DG as the DG
will have the AVR by which the constant voltage is
maintained even in case the load increase or decrease. When
the capacitors are connected they act as a load on the
sytem there by increasing the system load rather than
helping us.
| Is This Answer Correct ? | 26 Yes | 4 No |
Answer / jigar shah
Capacitor requirement arises to effective utilization of
the generated power (to reduce the losses mainly-cu losses
& line losses) & all switchgear component.In general
practice Capacitors are not connected on DG Set.As per my
understanding following are the main reasons for which it
is not recommendation to run capacitors on DG set :
1. During no load condition capacitor will try to increase
the voltage level of genrated voltage which can damage the
insulation of wdg & wdg may get burnt
2. With increase in PF we will not ge much advantage as the
cable losses are negligle.Load is in nearest proximity of
the Equipment.
3. Capacitors can be installed at load side
| Is This Answer Correct ? | 22 Yes | 0 No |
Answer / sudhir purandare
Yes, self working on DG for last 20 years and never had any
problem because of capacitors. Capacitors will help to
improve the power factor of the system and indirectly
reduce the load on alternator (which is mainly for
delivering the reactive power). only care shall be taken by
not allowing the power factor to go in leading. It is a
normal practise to switch on the capacitors after motor
starts and switch off immediately after motor trips.
Instead of maintaining the PF close to unity, it is better
to maintain it 0.9.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / suneetha
A DG is used to supply power when there is power failure
and not for power factor correction but a Power Capacitor
is mainly used for power factor correction and is usually
kept near unity to avoid penality.
| Is This Answer Correct ? | 15 Yes | 6 No |
Answer / reshi
Not at all ,Since DG sets are already generating the rated
voltage required and the designed power factor. For the
sake of discussion if we agree to install the capacitor on
DG sets it will give rise to the overvoltage and the
nearest downstream equipments are most probably not safe by
this option of having the capacitor on the DG sets.
Capacitors are required when the power factor is required
to improve and the best practice is it shall be installed
as close possible to the load.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / amarnath
YES ! The DG Rating is always defined in KVA @ 0.8 Pf Lag.
Hence for optimum utilization of the DG power, it will be
best to have the PF regulated to 0.8 PF Lag. However, care
must be taken not to let the PF go into LEAD condition as it
can lead to instabilty of the system voltage. Suggest to
conduct a detailed load study and opt for Automatic PF
Improvement Relay panels wherein the DG target PF can be set
@ 0.8 and for EB the target setting can be 0.95 Lag or above
. (definitely not LEAD)
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sachin_pawaskar2001
Yes, but then Supply voltage will be higher than the
generated voltage due to ferrenti effect.
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / t n srivastava kanpur
NOT FEASIBLE WITH DG SO ONLY OPTION TO RUN FACTORY AS IT
IS OTHERWISE SHUT DOWN PLANT.
IF ANY DOUBT PLS CONTACT TO ME.
THANKS
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amit
DG set dis-seined for 0.8 Pf and its capacity also dis-seined according to 0.8 pf so when we increase the pf loading capacity increase but the winding are dis-seined for 0.8 pf.so the winding damsge when the pf is rise.
| Is This Answer Correct ? | 0 Yes | 0 No |
Why derivative controller is not used in control systems?
auto reclosing scheme for radial ehv feeder is to be implemented or not?
Why HRG and LRG used beside transformer, what is the purpose
instead of neutral can we use earth/ground to flow the current in the circuit
what is the name of the oil is used in transformer?
why lightning arrestor are made by 2 stack of insulator but why cvt are fully 1 stack of insulator.
If the Brsh of DC motor is shifted by 90 deg, then MNA will shift by --degree.
If DG runing time neutral is disconnected what will be the effect in Engine and Electricial panel.
why we use MV panels??? what's r all the needs
How to take of Transformer oil Break down voltage test?
I want to put this query to SENIOR & EXPERIENCED ELECTRICAL ENGINEERS. 1)I want to know about the control circuit diagrams for control panels. I found it difficult to understand. Is there ant booklet through which we can learn the circuit diagrams? 2)I want to learn about conduiting, laying cables, preparing cable schedules and various techniques which is the part of building infrastucture(construction field). I don't have any experience in this area. I have experience in control panels only. that's why i am not getting any opening in building infrastucture (construction field).Can I get the job in this field as Trainee Engineer? How to enter this field? I need job in PUNE
why voltage ratings of xmission are in 11, 33,66kv and why not 11.5 ,16,19 or any other
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)