Can HT cable(11kv cable) be used for 415V, 700A requirement.
Answers were Sorted based on User's Feedback
Answer / ashish baluni
Cable used for HT is designed for High Voltage and low
current carrying capacity. But for Low voltage rating
current requirment is very high which would cause Excess
heating in cable and will result in Puncturing of cable at
weak point.
For Ex- HT side Power=HT Vol* HT Current,if this cable
would be used for Low voltage then Power will be same. Thus
LT Power= HT Power
> 415*700 = 11000* I (Power factor is assumed to be unity)
> I= 26.5 Amp (For HT cable)
Thus,HT cable cant be used for Low voltage at High Current.
| Is This Answer Correct ? | 16 Yes | 1 No |
Answer / v.senthilkumar
We can use HT cable for 415V, 700A. But you have not
mentioned any HT cable rating. If you mention HT cable
rating then we can analise whether it can be use or not.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / ranjit
Actually we cant use HT cables on 415 V LV side because of
without neutral cable. we can use HT cable with neutral
additionally. Neutral cable based on copper size which is
inside on HT cable. Because normally HT cable insulation
more less copper. because HT side High voltage less
current. But economic wise this is not good idea also.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mehul
we can't use h.t. cabel as l.t. cable.
because the cost of your h.t. cable is much higher han same
rating h.t. cable.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / mathew
normally, for HT we are using 240Sqmm cable in ring circuit. this 240sqmm cable is not sufficient for 700A, 2x240sqmm is sufficient for 700A. but we can use this 240 for both 11KV and 415V, thats not a problem.
| Is This Answer Correct ? | 2 Yes | 5 No |
in a distribution board,if we have a load and we have selected a cable after making all calcs (Deratings and V.D , ect...) the cable we have selected was 10mm.sq. now, shall the internal cable inside the switchboard should be 10 mm.sq Like the external or it can be Less???? if somebody have an specs or information he can help D:
What is the kiosk parts, about them and their functions ? If anybody have some PDFs files or details about this plz send it on tawhidfaisal@Yahoo.com
The specific heats of the gas at constant pressure and constant volume are respectively 1.0 kJ/kg K and 0.72 kJ/kg K; the value of R for the gas is
how capacitance is neglected in short transmission lines ?
What is a soft start?
HOW TO CHECK THE VECTOR GROUP OF A TRANSFORMER YD11?
What is difference between unity power factor wattmeter and upper power factor wattmeter? In short circuit test of transformer the wattmeter used is unity power factor type or upper power factor type wattmeter?
0 Answers Jindal Steel and Power,
how much GROUND & NEUTRAL VOLT maintain in data center.
why Lightning arrestor are made by 2 seperate stack of inslutor but why cvt are in single stack of insulator.
Why star pointed terminal have no current? how?
low frequency protection why recomend?
Why the tank of transformer is made rectangular not circular??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)