Can HT cable(11kv cable) be used for 415V, 700A requirement.
Answers were Sorted based on User's Feedback
Answer / ashish baluni
Cable used for HT is designed for High Voltage and low
current carrying capacity. But for Low voltage rating
current requirment is very high which would cause Excess
heating in cable and will result in Puncturing of cable at
weak point.
For Ex- HT side Power=HT Vol* HT Current,if this cable
would be used for Low voltage then Power will be same. Thus
LT Power= HT Power
> 415*700 = 11000* I (Power factor is assumed to be unity)
> I= 26.5 Amp (For HT cable)
Thus,HT cable cant be used for Low voltage at High Current.
| Is This Answer Correct ? | 16 Yes | 1 No |
Answer / v.senthilkumar
We can use HT cable for 415V, 700A. But you have not
mentioned any HT cable rating. If you mention HT cable
rating then we can analise whether it can be use or not.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / ranjit
Actually we cant use HT cables on 415 V LV side because of
without neutral cable. we can use HT cable with neutral
additionally. Neutral cable based on copper size which is
inside on HT cable. Because normally HT cable insulation
more less copper. because HT side High voltage less
current. But economic wise this is not good idea also.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mehul
we can't use h.t. cabel as l.t. cable.
because the cost of your h.t. cable is much higher han same
rating h.t. cable.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / mathew
normally, for HT we are using 240Sqmm cable in ring circuit. this 240sqmm cable is not sufficient for 700A, 2x240sqmm is sufficient for 700A. but we can use this 240 for both 11KV and 415V, thats not a problem.
| Is This Answer Correct ? | 2 Yes | 5 No |
A 100 MVA transformer may be cooled with?
Which one hurts more AC or DC Current ?
why transmission lines traveled in high voltage?
in a distribution board,if we have a load and we have selected a cable after making all calcs (Deratings and V.D , ect...) the cable we have selected was 10mm.sq. now, shall the internal cable inside the switchboard should be 10 mm.sq Like the external or it can be Less???? if somebody have an specs or information he can help D:
what is the voltage regulation for unity and zero power factor?
Why earthing is necessary for any equipment?
WHAT SHOULD BE THE MINIMUM IR VALUE FOR LV (380V) CABLES ACCORDING TO IEC/IEEE.
Write the force balance equation of ideal spring element.
10rm cable can got load ---- amp? Or Which Size Cable can take the load 100amp capacity SCR; breaker.
1 Answers B-Con Trade Associates,
if HT side voltage is high current is low . and LT side voltage is low current is high please explian.
1kva = kw ?
what efficiency at 70% loaded transformer
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)