in a distribution board,if we have a load and we have
selected a cable after making all calcs (Deratings and
V.D , ect...) the cable we have selected was 10mm.sq.
now, shall the internal cable inside the switchboard should
be 10 mm.sq Like the external or it can be Less????
if somebody have an specs or information he can help D:
Answer / saadsms
Hi
the in side cond,s will be less in size than the main cable
(out feeder) because they are branches to feed several loads.
their sizes may be ( 6,4,2.5,1.5 ) mm2.
and must be stranded isolated s.c wire to be flixible.
saad
| Is This Answer Correct ? | 2 Yes | 1 No |
how to calculate cooling requirement of datacentre from electrical load?
It is observed that AVR of an Alternator is more likely to fail if the Generator and Mains Neutral are directly connected to each other. Why should this be so?
Why is remote backup preferred to local backup?
What is power focter ?
diff. between star, delta connection?
1 HP = how many Kva
AIR GAP IS TERMED AS USEFUL. WHY?
difference between ground,neutral and earth?..
is this the formula of building wiring to get the main breaker.Watts/volts*.8%+higher motor*(25%)=ampere. yes or no or send the correct formula for building wiring.
why transformer fuse wire is very thin as compared to home fuse wire while voltage lavel is low
For 132 KV line, PT or CVT which is prefered for measuring & protection? is there any IS or IEE standard available?
what is the formula for AH?HOW CAN IT CALCULATE
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)