in a distribution board,if we have a load and we have
selected a cable after making all calcs (Deratings and
V.D , ect...) the cable we have selected was 10mm.sq.
now, shall the internal cable inside the switchboard should
be 10 mm.sq Like the external or it can be Less????
if somebody have an specs or information he can help D:
Answer / saadsms
Hi
the in side cond,s will be less in size than the main cable
(out feeder) because they are branches to feed several loads.
their sizes may be ( 6,4,2.5,1.5 ) mm2.
and must be stranded isolated s.c wire to be flixible.
saad
| Is This Answer Correct ? | 2 Yes | 1 No |
cany anyone suggest electrical wesites for providing study materials?
Tan delta point in transformer to be earth or not?
If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calculation formula. what extra load have to consider. in what efficiency it will work.
How to derive detailed design of Suitable bus Bar for 100A for 6.6KV?
How to Calculate IKW(input kilowatt)of a Chiller plant
State ohm’s law?
Why consumers are charged based on Kwh basis why not on Kvah basis.
what is the working principle of DC generator ?
Why one side of secondary of transformer is earthed, to supply single conductor of electric traction system?
how to select the surge suppresor for the 33 KV supply and what will be the rating, selection guide
whats the formula for convert KVAR to FARADS
What are the disadvantges of leading power factor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)