if HT side voltage is high current is low . and LT side
voltage is low current is high please explian.
Answers were Sorted based on User's Feedback
Answer / asutosh
for a perticular design the incoming power is same.
we know P = VI so when voltage is high current is low &
viceversa.
| Is This Answer Correct ? | 21 Yes | 0 No |
Answer / jital
Voltage & Current are the inverse propotion ( Voltage is
High, Current is less & Voltage is low, Current is More )
for the Same load when considered on different voltages.
its following P = VI
I.E> For the Same Load in 11 KV Current will be very less
For the same load in 415 V Current will be high compare to
11 Kv
| Is This Answer Correct ? | 17 Yes | 0 No |
Answer / bapi
AS kVA RATING OF A TRAFO IS CONSTANT.
SO FOR HT SIDE MEANS HIGH VOLTAGE SIDE CURRENT IS LESS &
FOR LT SIDE MEANS LOW VOLTAGE SIDE CURRENT IS MORE.
HIGH VOLTAGE X LOW CURRENT = LOW VOLTAGE X HIGH CURRENT
(HT SIDE) (LT SIDE)
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / bhavesh chauhan
Voltage and Current are inversely proportional to each other in Transformers.. As the value of voltage increases current decreases, and as the value of voltage decreases the current value increases.... I Will make you count..
Practically i work in a 220/66/11 kv power station.
I have a 100 MVA Transformer which is a Step Down X'mer. The H.V Side of the X'mer gets 220KV input and L.V of the X'mer gives 66KV output...Now to calculate ............
The Current for H.V Side according to P=VI
we have P=100 MVA
V=220 KV
I=?
I= 100 10^6 /1.732 X 220 X 10^3 = 262.24 Amps
Similarly for L.V
I= 100 10^6 /1.732 X 66 X 10^3 = 874.79 Amps
These are the Actual H.V and L.V Current reading of a working transformer... Which proves that when Voltage decreases current increases..........Thank you
| Is This Answer Correct ? | 6 Yes | 1 No |
What happened when a three phase induction motor work on two phase supply.9
What is the maximum No. of out going mccbs permitted from an LV distribution paqnel? What is the ampere relation between incomer and out going switch gears/mccbs?
Two CTs 1600/1 and 35/1 are in series. while checking the ratio test of a CT(1600/1),same 1600A will also pass through the CT having ratio 35/1. Will it be harmfull to the ct(35/1),if yes , what will happen.CT secondary is shorted
What will be the fault current of any system when its generation is 10% of BASE generation( FUll Load )?Will is 10% or the same as full base calculation?
how can we determine size of a cable by knowing the kw or current rating of a load?how can we calculate the resistance box of a slip ring motor?
Technical specification of a wind farm
What is In (current rating) shown on the MCCB? Is this full load which can withstand by the circuit breaker
What is double throw isolator and single throw Isolator.
Wy transformer ratings are in multiple of 11 always?
How to Calculate KA Rating of Main LT Panel
why is used for starters for staring motors?
Why synchorised generators are used for the production of electricity?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)