if HT side voltage is high current is low . and LT side
voltage is low current is high please explian.
Answers were Sorted based on User's Feedback
Answer / asutosh
for a perticular design the incoming power is same.
we know P = VI so when voltage is high current is low &
viceversa.
Is This Answer Correct ? | 21 Yes | 0 No |
Answer / jital
Voltage & Current are the inverse propotion ( Voltage is
High, Current is less & Voltage is low, Current is More )
for the Same load when considered on different voltages.
its following P = VI
I.E> For the Same Load in 11 KV Current will be very less
For the same load in 415 V Current will be high compare to
11 Kv
Is This Answer Correct ? | 17 Yes | 0 No |
Answer / bapi
AS kVA RATING OF A TRAFO IS CONSTANT.
SO FOR HT SIDE MEANS HIGH VOLTAGE SIDE CURRENT IS LESS &
FOR LT SIDE MEANS LOW VOLTAGE SIDE CURRENT IS MORE.
HIGH VOLTAGE X LOW CURRENT = LOW VOLTAGE X HIGH CURRENT
(HT SIDE) (LT SIDE)
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / bhavesh chauhan
Voltage and Current are inversely proportional to each other in Transformers.. As the value of voltage increases current decreases, and as the value of voltage decreases the current value increases.... I Will make you count..
Practically i work in a 220/66/11 kv power station.
I have a 100 MVA Transformer which is a Step Down X'mer. The H.V Side of the X'mer gets 220KV input and L.V of the X'mer gives 66KV output...Now to calculate ............
The Current for H.V Side according to P=VI
we have P=100 MVA
V=220 KV
I=?
I= 100 10^6 /1.732 X 220 X 10^3 = 262.24 Amps
Similarly for L.V
I= 100 10^6 /1.732 X 66 X 10^3 = 874.79 Amps
These are the Actual H.V and L.V Current reading of a working transformer... Which proves that when Voltage decreases current increases..........Thank you
Is This Answer Correct ? | 6 Yes | 1 No |
why hv winding is not placed near to transformer core
Why Indian Electricity frequency desined 50 Cycles as developed countrys are using high frequency with low voltage
What is the function of automatic Transfer Switch(ATS) in details
what is the knee point voltage in current transformer
what is the formula for converting KW into KWH ?
i Have 1000kva 11/.4 kv voltemp make t/f Its a 2 year old. i wants to known how much iron losses & copper loses during no load condition.
what is the function of CRGO in a Transformer?
HOW many type of Circut Breaker in the world used in 400 kv substation?
how to determine kilowatts (real power) is used in energy meter? is it apparent power effect the disk rotation?
What does bode plots shows?
Pls explan the OLR setting in VCB at HT yard
i have 400/230v transformer and didnt done the neutral eatrhing. i connected one lamp to one phase and neutral to the earth. but the lamp is not glowing. again i connected neutral to earth and repeated the same. then the lamp is glowing. in the first condition i tested with a line tester also, at that time the tesrer is glowing what is happening i dont know can any one help me?