10rm cable can got load ---- amp?
Or
Which Size Cable can take the load 100amp capacity SCR; breaker.
Answer / babar bilal
100 Amp load can be beard by a 50mm² cable easily. Its current carrying capacity is 155 Amps. If you go down a bit, then 35mm² cable can carry 94 Amps maximum, but its safe limit as per standards is 75.2 AMps @ 80% load capacity.
| Is This Answer Correct ? | 1 Yes | 0 No |
can anybody tell me that for p.f. Improvment we use capacitor banks but how to decide its capacitance. As we all know how to calculate kvar but what abt capacitance value
What will be the effect of circulating current in HT xlpe cable when both the armour ends are grounded. Will the termination fils after some time in case of 33 kv supply.
what is difference between differential protection and distance protection and how we calculate the sloop?
How to take Vector group test of Transformer?
16 Answers Sunflag Steel, Zuari Cements,
what is the disadvantage if earth is connected to neutral
What is the range of efficiency of thermal or steam power plants? Why it is so low?
3.7 kw motor ,how much sq mm cabel want to bare this motor load
The MCB circuit breaker have a voltage rating of 440VAC it's possible to supply a voltage of 480Vac
please write motor, transformer, Generator setting, fault level calculation of Tr.etc
what gas is present in incandescent and florescent bulbs
what is the difference between Ith & Iu rating in MCCB. Particularly on SACE ABB Circuit Breaker?
What is the use of iron core in a transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)