10rm cable can got load ---- amp?
Or
Which Size Cable can take the load 100amp capacity SCR; breaker.
Answer / babar bilal
100 Amp load can be beard by a 50mm² cable easily. Its current carrying capacity is 155 Amps. If you go down a bit, then 35mm² cable can carry 94 Amps maximum, but its safe limit as per standards is 75.2 AMps @ 80% load capacity.
Is This Answer Correct ? | 1 Yes | 0 No |
what is the maximum genarating in india?
what is the difference between "ampere trip and ampere frame"
how calculate external illumintion in a compound area. for e.g. there is one open park having 600m2 area and i have to put 40w flouresent tube fitting with pole. how shall i calculate the numbers of fitting.
What is RMU, and what it's function?
I need a formula to calculate the size of cable as per load but in the terms of length. Please Reply me as i search lot of sites but i did not get the answer.
DISCUSS THE SHAFT MOUNTED D.C. GENERATOR ,BASED ON EXCITATION SYSTEM IN ELECTRICAL SYSTRM
what is the effect of leading power factor on Power transformers in existing in major power utility
when meggering a 3ph,480v oil reservoir heater on a regen gas compressor, why do I get a reading to ground when meggering phase to ground? shouldn't it read opened or is there something that makes it read closed? on the same heater, when ohming, it reads open. thanx
AC SUPPLY HAVING 230 V FREQUENCY REDUCED ZERO IF MEN TACUCHES THE SUPPLY WEATHER HE GETS SHOCK OR NOT?
is it possible to export & import power in a same transformer.how
What kind of Neutral CT can be placed in 11/0.433KV transformer to be used and what are its specification?
What is mean demand of the Plant?